Ground flow formula (Water Overlay): Difference between revisions
(121 intermediate revisions by 2 users not shown)
Underground flow is different from surface flow, since it has to account for the slowdown and porousness of the medium. In general, horizontal underground flow is calculated using formulas described in Harbaugh 2005<ref name="Harbaugh"/><ref name="Modflow"/>. However, when an [[Aquifer (Water_Overlay)|aquifer]] is present, the aquifer variant is applied.
Ground flow is different from surface flow, since it has to account for the slowdown and porousness of the medium. In general, horizontal ground flow is calculated using formulas described in Harbaugh 2005{{ref|Harbaugh}}{{ref|Modflow}}. However, when an [[Aquifer (Water_Overlay)|aquifer]] is present, the [[ground flow formula (Water Overlay)#Aquifer formula|Aquifer formula]] is applied.
===Default horizontal flow===
The Hydraulic Conductivity formula used depends on the value of the [[Hydraulic conductivity with thickness (Water Overlay)|HYDRAULIC_CONDUCTIVITY_WITH_THICKNESS]] attribute in the [[Water Overlay]]:
[[File:Undergroundflow2.png|right|400px|thumb|Two adjacent cells, where underground water level of cell 1 is larger than cell 2.]]
* A value <math><= 0</math> means [[Ground flow formula (Water Overlay)#Hydraulic Conductivity without Thickness|Hydraulic Conductivity without Thickness]] formula will be used.
* A value <math>> 0</math> means [[Ground flow formula (Water Overlay)#Hydraulic Conductivity with Thickness|Hydraulic Conductivity with Thickness]] formula will be used.
===Hydraulic Conductivity without Thickness===
[[File:Undergroundflow2.png|right|400px|thumb|Two adjacent cells, where ground water level of cell 1 is larger than cell 2.]]
The flow between the two cells is calculated as:
: Δw = w<sub>1</sub> - w<sub>2</sub>
: B<sub>ex</sub> = max ( B<sub>1</sub> , B<sub>2</sub> ) - D<sub>ground</sub>
<math>\Delta w_t = w_{1,t} - w_{2,t}</math>
: A<sub>c</sub> = Δx * ( w<sub>avg</sub> - B<sub>ex</sub> )
: C = min(C<sub>1</sub> , C<sub>2</sub> )
<math>B_{bb} = max ( B_{1}- d_{b,1} , B_{2}- d_{b,2} ) </math>
: q = Δw * C * A<sub>c</sub> / Δx * Δt
<math>A_{c,t} = \Delta x \cdot ( \bar{w_{t}} - B_{bb} )</math>
<math>K = min(K_{1} , K_{2} )</math>
<math>V_{K,t} = \frac{\Delta w \cdot K \cdot A_{c,t}}{ \Delta x} \cdot \Delta t</math>
: w<sub>n</sub> = The [[Groundwater level formula (Water Overlay)|underground water level]] of cell n.
: <math>w_{n,t}</math> = The [[Groundwater level formula (Water Overlay)|ground water level]] of cell <math>n</math> at time <math>t</math>.
: B<sub>n</sub> = The [[terrain height (Water Overlay)|surface height]] of cell n.
: <math>B_c</math> = the datum height of the surface of cell c, set by the [[Elevation model (Water Overlay)|elevation]] or a [[Terrain elevation prequel (Water Overlay)|Terrain elevation prequel]].
: C<sub>n</sub> = The ground conductance of cell, defined in [[Terrain ground infiltration md (Water Overlay)|GROUND_INFILTRATION_MD]] of the underground terrain.
: <math>d_{b,c}</math> = The ground bottom distance of the cell c, defined by a [[Bottom distance prequel (Water Overlay)|Bottom distance prequel]] or a general [[Ground_bottom_distance_m_(Water_Overlay)|GROUND_BOTTOM_DISTANCE_M]] of the Water Overlay.
: D<sub>ground</sub> = The configured ground bottom distance, defined in [[Ground_bottom_distance_m_(Water_Overlay)|GROUND_BOTTOM_DISTANCE_M]] of the Water Overlay.
: <math>B_{bb}</math> = the datum height of the bottom boundary at the edge of interaction between the two cells.
: A<sub>c</sub> = Area of conductance.
: <math>K_n</math> = The hydraulic conductivity of the cell, defined in [[Terrain hydraulic conductivity md (Water Overlay)|HYDRAULIC_CONDUCTIVITY_MD]] of the ground terrain.
: Δw = Underground water level difference.
: <math>A_{c,t}</math> = Area of conductance at time <math>t</math>.
: Δt = Computational timestep.
: <math>\Delta w</math> = Ground water level difference at time <math>t</math>.
: Δx = Size of grid cell.
: <math>\Delta t</math> = Computational [[Timestep formula (Water Overlay)|timestep]] in seconds.
: w<sub>avg</sub> = Averaged underground water level, based on water levels in underground, [[Terrain water storage percentage (Water Overlay)|WATER_STORAGE_PERCENTAGE]] and potentially the [[Surface water level formula (Water Overlay)|surface water level]], when the underground is filled to the top.
: <math>\Delta x</math> = Size of grid cell.
: <math>\bar{w_{t}}</math> = Averaged ground water level at time <math>t</math>, based on water levels in ground, [[Terrain water storage percentage (Water Overlay)|WATER_STORAGE_PERCENTAGE]] and potentially the [[Surface water level formula (Water Overlay)|surface water level]], when the ground is filled to the top.
: <math>V_{K,t}</math> = The amount of water to be transported at time <math>t</math> between one cell and the other.
<br clear=both>
===Hydraulic Conductivity with Thickness===
===Aquifer formula===
When an [[Aquifer (Water_Overlay)|aquifer]] is present, its hydraulic diffusivity is used to calculate the water flow.
First, the hydraulic diffusivity dictates the fraction of the water height difference which will flow.
<math>KD = min(KD_{1} , KD_{2} )</math>
: ''F = 2 * sqrt( KD / WSP<sub>source</sub> ) * sqrt( Δt ) * ( 1 / cell )''
Based on this fraction, the actual amount of water flow is calculated.
<math>V_{KD,t} = \Delta w \cdot KD \cdot \Delta t</math>
: ''Δw = ( (WL<sub>source</sub>/WSP<sub>source</sub>) - (WL<sub>target</sub>/WSP<sub>source</sub>) ) * F''
Where:
* Δw = The underground flow which takes place.
* Δt = Computational timestep.
: <math>KD_n</math> = The hydraulic conductivity of the cell, multiplied with the thickness of the layer, defined in [[Terrain hydraulic conductivity with thickness md (Water Overlay)|HYDRAULIC_CONDUCTIVITY_WITH_THICKNESS_MD]] of the ground terrain.
* cell = Cell size.
: <math>V_{KD,t}</math> = The amount of water to be transported at time <math>t</math> between one cell and the other.
* F = Fraction of water which flows between cells
When an [[Aquifer (Water_Overlay)|aquifer]] is present, its [[Aquifer kd (Water Overlay)|hydraulic diffusivity]] is used to calculate the water flow.
* KD = The [[Aquifer kd (Water Overlay)|AQUIFER_KD]] attribute of aquifer.
The volume of water transported through the aquifer is calculated as follows:
* WSP<sub>source</sub> = The [[Terrain water storage percentage (Water Overlay)|WATER_STORAGE_PERCENTAGE]] attribute of the underground terrain type of the origin cell.
: <math>V_{a,t} =
* WSP<sub>target</sub> = The [[Terrain water storage percentage (Water Overlay)|WATER_STORAGE_PERCENTAGE]] attribute of the underground terrain type of the target cell.
\begin{cases}
* WL<sub>source</sub> = The amount of water in the saturated zone of the source cell. The height of the water column if the equivalent amount of water was placed on the surface.
\Delta w_{t} \cdot {KD}_a \cdot \Delta t & \text{if } w_{n,t} > z_a  \text{ and } KD_a > 0 \\
* WL<sub>target</sub> = The amount of water in the saturated zone of the target cell. The height of the water column if the equivalent amount of water was placed on the surface.
V_{K(D),t}  & \text{otherwise}
\end{cases}
</math>
==See also==
Where:
*[[Underground model (Water Overlay)#Horizontal flow and aquifers| Underground horizontal flow]]
: <math>\Delta w_{t}</math> = Ground water level difference between the two adjacent cells at time <math>t</math>;
: <math>{KD}_a</math> = The [[Aquifer kd (Water Overlay)|AQUIFER_KD]] attribute of aquifer.
: <math>w_{n,t}</math> = Ground water level in the respective cell at time <math>t</math>;
: <math>z_a</math> = [[Aquifer datum (Water Overlay)|the datum height of the aquifer]] at the cell.
: <math>V_{K(D),t}</math> = The calculated amount of water to be transported at time <math>t</math> between one cell and the other.
: <math>V_{a,t}</math> = Volume in <math>m^{3}</math> that flows between the two adjacent cells due to the aquifer at time <math>t</math>.
==Related==
|related=
; Features
; Features
: [[Aquifer (Water Overlay)|Aquifer]]
: [[Aquifer (Water Overlay)]]
; Formulas
; Formulas
: [[Groundwater level formula (Water Overlay)|Groundwater level formula]]
: [[Groundwater level formula (Water Overlay)]]
: [[Underground infiltration formula (Water Overlay)|Underground infiltration formula]]
: [[Ground infiltration formula (Water Overlay)]]
; Models
; Models
: [[Underground model (Water Overlay)|Underground model]]
: [[Infiltration model (Water Overlay)|Infiltration model]]
: [[Infiltration model (Water Overlay)]]
: [[Substance flow model (Water Overlay)|Substance flow model]]
: [[Tracer flow model (Water Overlay)]]
==References==
* [[Ground model (Water Overlay)#Horizontal flow and aquifers| Ground model]]
|references=
<references>
<references>
<ref name="Modflow">Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods, book 6, chap. A55 ∙ p 31 ∙ found at:  https://doi.org/10.3133/tm6A55 (last visited 2019-02-04)</ref>
{{ref|Modflow
<ref name="Harbaugh">Harbaugh, A.W., 2005, MODFLOW-2005, the U.S. Geological Survey modular ground-water model-the Ground-Water Flow Process: U.S. Geological Survey Techniques and Methods 6-A16, variously paginated.</ref>
  |name=Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods
  |author=Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017)
  |page=31, of book 6, chapter A55
  |source=
  |link=https://pubs.usgs.gov/publication/tm6A55
  |lastvisit=04-02-2025
{{ref|Harbaugh
  |name=MODFLOW-2005, the U.S. Geological Survey modular ground-water model-the Ground-Water Flow Process: U.S. Geological Survey Techniques and Methods 6-A16
  |author=>Harbaugh, A.W., 2005
  |page=various
  |source=
  |link=
  |lastvisit=
</references>
</references>
{{Template:WaterOverlay_nav}}
{{WaterOverlay formula nav}}
Latest revision as of 07:36, 10 July 2026
Ground flow is different from surface flow, since it has to account for the slowdown and porousness of the medium. In general, horizontal ground flow is calculated using formulas described in Harbaugh 2005[1][2]. However, when an aquifer is present, the Aquifer formula is applied.
The Hydraulic Conductivity formula used depends on the value of the HYDRAULIC_CONDUCTIVITY_WITH_THICKNESS attribute in the Water Overlay:
Δwt=w1,t−w2,t
Bbb=max(B1−db,1,B2−db,2)
Ac,t=Δx⋅(wt¯−Bbb)
K=min(K1,K2)
VK,t=Δw⋅K⋅Ac,tΔx⋅Δt
wn,t = The ground water level of cell n at time t.
Bc = the datum height of the surface of cell c, set by the elevation or a Terrain elevation prequel.
db,c = The ground bottom distance of the cell c, defined by a Bottom distance prequel or a general GROUND_BOTTOM_DISTANCE_M of the Water Overlay.
Bbb = the datum height of the bottom boundary at the edge of interaction between the two cells.
Kn = The hydraulic conductivity of the cell, defined in HYDRAULIC_CONDUCTIVITY_MD of the ground terrain.
Ac,t = Area of conductance at time t.
Δw = Ground water level difference at time t.
wt¯ = Averaged ground water level at time t, based on water levels in ground, WATER_STORAGE_PERCENTAGE and potentially the surface water level, when the ground is filled to the top.
VK,t = The amount of water to be transported at time t between one cell and the other.
Δwt=w1,t−w2,t
KD=min(KD1,KD2)
VKD,t=Δw⋅KD⋅Δt
KDn = The hydraulic conductivity of the cell, multiplied with the thickness of the layer, defined in HYDRAULIC_CONDUCTIVITY_WITH_THICKNESS_MD of the ground terrain.
VKD,t = The amount of water to be transported at time t between one cell and the other.
Aquifer formula
When an aquifer is present, its hydraulic diffusivity is used to calculate the water flow.
Va,t={Δwt⋅KDa⋅Δtif wn,t>za and KDa>0VK(D),totherwise
Where:
Δwt = Ground water level difference between the two adjacent cells at time t;
KDa = The AQUIFER_KD attribute of aquifer.
wn,t = Ground water level in the respective cell at time t;
za = the datum height of the aquifer at the cell.
VK(D),t = The calculated amount of water to be transported at time t between one cell and the other.
Va,t = Volume in m3 that flows between the two adjacent cells due to the aquifer at time t.
Features
Models
  1. ↑ MODFLOW-2005, the U.S. Geological Survey modular ground-water model-the Ground-Water Flow Process: U.S. Geological Survey Techniques and Methods 6-A16 ∙ >Harbaugh, A.W., 2005 ∙ Page(s): various
  2. ↑ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods ∙ Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Page(s): 31, of book 6, chapter A55 ∙ Found at: https://pubs.usgs.gov/publication/tm6A55 ∙ (last visited: 04-02-2025)