Flow through [[culvert (Water Overlay)|culvert]]s is based on an open channel flow calculation. | Flow through [[culvert (Water Overlay)|culvert]]s is based on an open channel flow calculation. | ||
The actual height of the culvert is at least the height of the terrain on either end of the culvert and the provided threshold height: | The actual datum height of the culvert is at least the height of the terrain on either end of the culvert and the provided threshold height: | ||
: <math>B_c = \max( T_c , B_l , B_r )</math> | : <math>B_c = \max( T_c , B_l , B_r )</math> | ||
For circular culverts, the flow height <math>h_f</math> is: | |||
: <math>h_f = \max(0,\min(D,\max (w_{l}, w_{r})-B_c)))</math> | |||
For rectangular culverts, the flow depth h is: | |||
: <math>h_f = \max(0,\min(H,\max (w_{l}, w_{r})-B_c)))</math> | |||
: <math> | |||
: <math> | |||
The loss coefficient for the culvert is calculated: | The loss coefficient for the culvert is calculated: | ||
: <math>U = \sqrt{ \frac{1}{ 1 + \frac{2g \cdot n^2 \cdot length }{ R_{h}^{\frac{4}{3}}} }}</math> | : <math>U = \sqrt{ \frac{1}{ 1 + \frac{2g \cdot n^2 \cdot length }{ R_{h}^{\frac{4}{3}}} }}</math> | ||
The hydraulic radius R_h is calculated using the formula's in the image | The hydraulic radius <math>R_h</math> is calculated as: | ||
: <math>R_h = \frac{A}{P_w}</math> | |||
For circular culverts, the flow area <math>A</math> and the wetted perimeter <math>P_w</math> is calculated using the formula's in the image below. | |||
[[File:Hydraulic_radius.png|left]]{{clear}} | |||
Where the radius of the culvert: | |||
: <math>r = \frac{D}{2}</math> | |||
For rectangular culverts, the flow area and wetted perimeter is calculated as followed: | |||
: <math>A = h_f \cdot D</math> | |||
<math> | |||
P_w = | |||
\begin{cases} | |||
D + 2h_f, & \text{if } h_f < H \\ | |||
2D + 2H, & \text{if } h_f \ge H | |||
\end{cases} | |||
</math> | |||
The potential flow through the culvert is then calculated: | The potential flow through the culvert is then calculated: | ||
: <math> | : <math>Q = U \cdot K \cdot \sqrt{ 2g \cdot \Vert w_{l} - w_{r} \Vert }</math> | ||
Finally the actual amount of water flow is calculated: | Finally the actual amount of water flow is calculated: | ||
: <math>\Delta f = \frac{\Delta t \cdot | : <math>\Delta f = \frac{\Delta t \cdot Q} { \Delta x}</math> | ||
Where: | Where: | ||
* <math>D</math> = The [[Culvert diameter (Water Overlay)|CULVERT_DIAMETER]] attribute of the culvert. | * <math>D</math> = The [[Culvert diameter (Water Overlay)|CULVERT_DIAMETER]] attribute of the culvert, representing either the inside diameter of a circular culvert or the inside width of a rectangular culvert. | ||
* <math>H</math> = The [[Culvert diameter (Water Overlay)|CULVERT_RECTANGULAR_HEIGHT]] attribute of the culvert, representing the inside height of a rectangular culvert. | |||
* <math>h_f</math> = The (flow) height of the water inside the culvert. | |||
* <math>T_c</math> = The [[Culvert threshold (Water Overlay)|CULVERT_THRESHOLD]] attribute of the culvert. | * <math>T_c</math> = The [[Culvert threshold (Water Overlay)|CULVERT_THRESHOLD]] attribute of the culvert. | ||
* <math>B_c</math> = The [[Terrain height (Water Overlay)| | * <math>B_c</math> = The [[Terrain height (Water Overlay)|datum height]] of the base of the culvert. | ||
* <math>w_{l}</math> = The [[Surface water level formula (Water Overlay)|water level]] on the left end of the culvert, relative to {{datum}}. | * <math>w_{l}</math> = The [[Surface water level formula (Water Overlay)|water level]] on the left end of the culvert, relative to {{datum}}. | ||
* <math>w_{r}</math> = The [[Surface water level formula (Water Overlay)|water level]] on the right end of the culvert, relative to {{datum}}. | * <math>w_{r}</math> = The [[Surface water level formula (Water Overlay)|water level]] on the right end of the culvert, relative to {{datum}}. | ||
* <math>R_h</math> = The hydraulic radius in the culvert<ref name="hydradius"/>. | * <math>R_h</math> = The hydraulic radius in the culvert<ref name="hydradius"/>. | ||
* <math>K</math> = | * <math>R_w</math> = The wetted perimeter. | ||
* <math>g</math> = | * <math>A</math> = The flow area. | ||
* <math>K</math> = Circular flow area, based on the height of the water in the (circular) culvert. | |||
* <math>g</math> = {{gravity}}. | |||
* <math>L</math> = The length of the culvert, calculated as the distance between the culvert's endpoints. | * <math>L</math> = The length of the culvert, calculated as the distance between the culvert's endpoints. | ||
* <math>U</math> = Loss coefficient for culverts. | * <math>U</math> = Loss coefficient for culverts. | ||
* <math>n</math> = The [[Culvert n (Water Overlay)|CULVERT_N]] attribute of the culvert. | * <math>n</math> = The [[Culvert n (Water Overlay)|CULVERT_N]] attribute of the culvert. | ||
* <math> | * <math>Q</math> = The potential rate of water flow through the culvert in <math>m^3s^{-1}</math>. | ||
* <math>\Delta f</math> = The water flow which takes place. | * <math>\Delta f</math> = The water flow which takes place. | ||
* <math>\Delta t</math> = Computational timestep. | * <math>\Delta t</math> = Computational [[Timestep formula (Water Overlay)|timestep]] in seconds. | ||
* <math>\Delta x</math> = Cell size. | * <math>\Delta x</math> = Cell size in meters. | ||
==Related== | ==Related== | ||
| Line 49: | Line 64: | ||
: [[Surface model (Water Overlay)|Surface model]] | : [[Surface model (Water Overlay)|Surface model]] | ||
{{article end | |||
|references= | |||
<references> | <references> | ||
<ref name="hydradius">Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)</ref> | <ref name="hydradius">Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)</ref> | ||
{{WaterOverlay formula nav}} | {{WaterOverlay formula nav}} | ||
Latest revision as of 13:20, 5 March 2024
Flow through culverts is based on an open channel flow calculation.
For circular culverts, the flow height is:
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle h_f = \max(0,\min(D,\max (w_{l}, w_{r})-B_c)))}
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle h_f = \max(0,\min(H,\max (w_{l}, w_{r})-B_c)))}
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle U = \sqrt{ \frac{1}{ 1 + \frac{2g \cdot n^2 \cdot length }{ R_{h}^{\frac{4}{3}}} }}}
The hydraulic radius Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle R_h} is calculated as:
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle R_h = \frac{A}{P_w}}
For circular culverts, the flow area Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle A} and the wetted perimeter Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle P_w} is calculated using the formula's in the image below.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle r = \frac{D}{2}}
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle A = h_f \cdot D}
Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle P_w = \begin{cases} D + 2h_f, & \text{if } h_f < H \\ 2D + 2H, & \text{if } h_f \ge H \end{cases} }
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle Q = U \cdot K \cdot \sqrt{ 2g \cdot \Vert w_{l} - w_{r} \Vert }}
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle \Delta f = \frac{\Delta t \cdot Q} { \Delta x}}
Where:
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle D} = The CULVERT_DIAMETER attribute of the culvert, representing either the inside diameter of a circular culvert or the inside width of a rectangular culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle H} = The CULVERT_RECTANGULAR_HEIGHT attribute of the culvert, representing the inside height of a rectangular culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle h_f} = The (flow) height of the water inside the culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle T_c} = The CULVERT_THRESHOLD attribute of the culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle B_c} = The datum height of the base of the culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle w_{l}} = The water level on the left end of the culvert, relative to datum.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle w_{r}} = The water level on the right end of the culvert, relative to datum.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle R_h} = The hydraulic radius in the culvert[1].
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle R_w} = The wetted perimeter.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle A} = The flow area.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle K} = Circular flow area, based on the height of the water in the (circular) culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle g} = the acceleration due to gravity, set to 9.80665.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle L} = The length of the culvert, calculated as the distance between the culvert's endpoints.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle U} = Loss coefficient for culverts.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle n} = The CULVERT_N attribute of the culvert.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle Q} = The potential rate of water flow through the culvert in Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle m^3s^{-1}} .
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle \Delta f} = The water flow which takes place.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle \Delta t} = Computational timestep in seconds.
- Failed to parse (MathML with SVG or PNG fallback (recommended for modern browsers and accessibility tools): Invalid response ("Math extension cannot connect to Restbase.") from server "https://wikimedia.org/api/rest_v1/":): {\displaystyle \Delta x} = Cell size in meters.
Related
- Structures
- Culvert
- Models
- Surface model
- ↑ Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)