Flow across [[Weir (Water Overlay)|weir]]s is calculated differently for free flow and submerged flow. | Flow across [[Weir (Water Overlay)|weir]]s is calculated differently for free flow and submerged flow. The weir height may vary based on provided values or automatic adjustment; therefore, it is determined first. | ||
First the upstream water level is calculated as follows: | |||
:<math>w_{u,t} = max( w_{l,t}, w_{r,t})</math> | :<math>w_{u,t} = max( w_{l,t}, w_{r,t})</math> | ||
:<math> | |||
Next, the adjusted weir height is determined. It either originates from the supplied weir height(s) <math>z_{w,t}</math> or it is adjusted according to the weir threshold level. Once adjusted, a lockout period is set during which the height cannot change again. | |||
:<math>z^{*}_{w,t} = | |||
\begin{cases} | \begin{cases} | ||
z^*_{w,t}, & \text{if} & \ | z_{th}, & \text{if} & \|{w_{u,t} - \tau_w}\| > \mu \text{ and } \tau_w > -10000 \\ | ||
z_{w,t-1}, & \text{otherwise} | z^{*}_{w,t-1}, & \text{if} & T_{wm} > T \\ | ||
z_{w,t}, & \text{otherwise} | |||
\end{cases} | |||
</math> | |||
The height adjustment range values, defined by the min and max, are determined next: | |||
:<math>z_{min,w} = max ( z_{w,t} - \rho, min (z_{b,l}, z_{b,r} ) )</math> | |||
:<math>z_{max,w} = | |||
\begin{cases} | |||
z_{w,t}, & \text{if} & w_{u,t} < z^{*}_{w,t-1} \\ | |||
z_{w,t} + \rho, & \text{otherwise} | |||
\end{cases} | |||
</math> | |||
Finally, the adjusted weir height is calculated and stored, as well as the moment in time at which the weir can be adjusted again. | |||
:<math>z_{th} = | |||
\begin{cases} | |||
min(z_{max,w}, max( z_{min,w}, z^{*}_{w,t-1} + \mu )), & \text{if} & w_{u,t} < \tau_w \\ | |||
min(z_{max,w}, max( z_{min,w}, z^{*}_{w,t-1} - \mu )), & \text{otherwise} | |||
\end{cases} | \end{cases} | ||
</math> | </math> | ||
:<math> T_{wm} = T + t_{wm}</math> | |||
:<math>z_{w,t} = z^{*}_{w,t}</math> | |||
With the weir height known, the relative water heights at both ends are calculated: | |||
: <math>h_s = max(0, max( w_{l,t}, w_{r,t} ) - z_{w,t})</math> | |||
: <math>h_d = max(0, min( w_{l,t}, w_{r,t} ) - z_{w,t})</math> | |||
The weir uses either a submerged flow <math>Q_s</math> or a free flow <math>Q_f</math> formula, determined by the following ratio: | |||
: <math>r_h = \frac{h_d}{h_s}</math> | : <math>r_h = \frac{h_d}{h_s}</math> | ||
:<math> | :<math> | ||
| Line 30: | Line 53: | ||
For free flow, it is calculated directly: | For free flow, it is calculated directly: | ||
: <math>Q_f = f_{ | : <math>Q_f = f_{dw} \cdot C_w \cdot b \cdot ( h_s - h_d )^{N_w}</math> | ||
For submerged flow, the following calculation is used: | For submerged flow, the following calculation is used: | ||
: <math>Q_s = | : <math>Q_s = f_{loss} \cdot A \cdot \sqrt{ 2 \cdot g \cdot ( h_s - h_d ) }</math> | ||
Finally the actual amount of water | with: | ||
: <math>\Delta w = \frac{\Delta t \cdot Q}{\Delta x}</math> | : <math>A = b \cdot (h_s-h_d)</math> | ||
Finally the actual amount of water level change is calculated: | |||
: <math>\Delta w = \frac{\Delta t \cdot Q}{\Delta x \cdot \Delta x}</math> | |||
Where: | Where: | ||
* <math>w_{l,t}</math> = The water level on the left side of the weir, relative to {{datum}}, at time <math>t</math>. | * <math>w_{l,t}</math> = The water level on the left side of the weir, relative to {{datum}}, at time <math>t</math>. | ||
* <math>w_{r,t}</math> = The water level on the right side of the weir, relative to {{datum}}, at time <math>t</math>. | * <math>w_{r,t}</math> = The water level on the right side of the weir, relative to {{datum}}, at time <math>t</math>. | ||
* <math>w_{u,t}</math> = The calculated upstream water level, relative to {{datum}}, at time <math>t</math>. | |||
* <math>z_{th}</math> = The height of the weir at time t, according to the height adjustment mechanism. | |||
* <math>\tau_w</math> = The [[Weir target level (Water Overlay)|WEIR_TARGET_LEVEL]] of the weir. | |||
* <math>T_{wm}</math> = Moment in time in seconds after which the weir can adjust its height again. | |||
* <math>z_{w,t}</math> = The [[Weir height (Water Overlay)|WEIR_HEIGHT]] of the weir, at time <math>t</math>. | * <math>z_{w,t}</math> = The [[Weir height (Water Overlay)|WEIR_HEIGHT]] of the weir, at time <math>t</math>. | ||
* <math>z^{*}_{w,t}</math> = The optionally adjusted height of the weir at time t, depending on the weir height adjustment mechanism. | |||
* <math>z_{b,l}</math> = The water bottom elevation at the left side of the weir. | |||
* <math>z_{b,r}</math> = The water bottom elevation at the right side of the weir. | |||
* <math>z_{min,w}</math> = The minimum allowed height for weir w. | |||
* <math>z_{max,w}</math> = The maximum allowed height for weir w. | |||
* <math>\mu</math> = The [[Weir move step m (Water Overlay)|WEIR_MOVE_STEP_M]] of the water overlay, applicable to all weirs. | |||
* <math>\rho</math> = The [[Weir move range m (Water Overlay)|WEIR_MOVE_RANGE_M]] of the water overlay, applicable to all weirs. | |||
* <math>T</math> = Current simulated time in seconds. | |||
* <math>t_{wm}</math> = The [[Weir move interval s (Water Overlay)|WEIR_MOVE_INTERVAL_S]] of the water overlay, applicable to all weirs. | |||
* <math>h_s</math> = The height of the water column relative to the top of the weir, on the side with the highest [[Surface water level formula (Water Overlay)|water level]], at time <math>t</math>. | * <math>h_s</math> = The height of the water column relative to the top of the weir, on the side with the highest [[Surface water level formula (Water Overlay)|water level]], at time <math>t</math>. | ||
* <math>h_d</math> = The height of the water column relative to the top of the weir, on the side with the lowest [[Surface water level formula (Water Overlay)|water level]], at time <math>t</math>. | * <math>h_d</math> = The height of the water column relative to the top of the weir, on the side with the lowest [[Surface water level formula (Water Overlay)|water level]], at time <math>t</math>. | ||
* <math> | * <math>r_h</math> = The ratio of water heights on either side of the weir. | ||
* <math>Q</math> = The potential rate of water flow across the weir. | |||
* <math> | * <math>Q_f</math> = The potential rate of water flow across the weir, based on a free flow calculation. | ||
* <math> | * <math>Q_s</math> = The potential rate of water flow across the weir, based on a submerged calculation. | ||
* <math> | * <math>f_{dw}</math> = Dutch weir factor, set to 1.7. | ||
* <math>f_{ | |||
* <math>C_w</math> = The [[Weir coefficient (Water Overlay)|WEIR_COEFFICIENT]] of the weir. | * <math>C_w</math> = The [[Weir coefficient (Water Overlay)|WEIR_COEFFICIENT]] of the weir. | ||
* <math> | * <math>N_w</math> = The [[Weir n (Water Overlay)|WEIR_N]] of the weir. | ||
* <math>b</math> = The breadth of weir crest, adjustable using the [[Weir width (Water Overlay)|WEIR_WIDTH]]. | * <math>b</math> = The breadth of weir crest, adjustable using the [[Weir width (Water Overlay)|WEIR_WIDTH]]. | ||
* <math> | * <math>f_{loss}</math> = Loss coefficient for submerged weirs, set to 0.9. | ||
* <math>A</math> = Flow area, based on the highest water column height relative to the top of the weir, and [[Weir width (Water Overlay)|WEIR_WIDTH]] of the weir. | * <math>A</math> = Flow area, based on the highest water column height relative to the top of the weir, and [[Weir width (Water Overlay)|WEIR_WIDTH]] of the weir. | ||
* <math>g</math> = | * <math>g</math> = {{gravity}}. | ||
* <math>\Delta w</math> = The water | * <math>\Delta w</math> = The water level change in meters, which takes place. | ||
* <math>\Delta t</math> = Computational timestep. | * <math>\Delta t</math> = Computational [[Timestep formula (Water Overlay)|timestep]] in seconds. | ||
* <math>\Delta x</math> = Cell size. | * <math>\Delta x</math> = Cell size in meters. | ||
===Free flow coefficients=== | ===Free flow coefficients=== | ||
| Line 71: | Line 104: | ||
When <math>h \approx 0.01</math> meters, the following holds. | When <math>h \approx 0.01</math> meters, the following holds. | ||
:<math>f_{ | :<math>f_{dw} \cdot C_w \approx C_d \cdot \sqrt{g}</math> | ||
:<math>C_d=0,633 \cdot (1-\frac{0.0003}{h})^ | :<math>C_d=0,633 \cdot (1-\frac{0.0003}{h})^{N_w}</math> | ||
where: | where: | ||
* <math>f_{ | * <math>f_{dw}</math> = Dutch weir factor, set to 1.7. | ||
* <math>C_w</math> = The [[Weir coefficient (Water Overlay)|WEIR_COEFFICIENT]] of the weir, set to a default of 1.1 | * <math>C_w</math> = The [[Weir coefficient (Water Overlay)|WEIR_COEFFICIENT]] of the weir, set to a default of 1.1 | ||
* <math>N_w</math> = The [[Weir n (Water Overlay)|WEIR_N]] of the weir, set to <math>\frac{3}{2}</math> by default. | |||
* <math>C_d</math> = Calculated Coefficient of discharge. | * <math>C_d</math> = Calculated Coefficient of discharge. | ||
* <math>g</math> = acceleration due to gravity. | * <math>g</math> = acceleration due to gravity. | ||
| Line 87: | Line 121: | ||
The following topics are related to this formula. | The following topics are related to this formula. | ||
; Structures | ; Structures | ||
: [[ | : [[Weir (Water Overlay)|Weir]] | ||
: [[Breach (Water Overlay)|Breach]] | |||
; Models | ; Models | ||
: [[Surface model (Water Overlay)|Surface model]] | : [[Surface model (Water Overlay)|Surface model]] | ||
; Formulas | |||
: [[Breach flow formula (Water Overlay)|Breach flow formula]] | |||
; Test cases | |||
: [[Weir height test case (Water Module)|Weir height test case]] | |||
{{Article end | {{Article end | ||
| Line 102: | Line 142: | ||
|api=*[[Api session event editor building set attribute]] | |||
{{WaterOverlay formula nav}} | {{WaterOverlay formula nav}} | ||
Latest revision as of 12:41, 13 October 2026
Flow across weirs is calculated differently for free flow and submerged flow. The weir height may vary based on provided values or automatic adjustment; therefore, it is determined first.
Next, the adjusted weir height is determined. It either originates from the supplied weir height(s) or it is adjusted according to the weir threshold level. Once adjusted, a lockout period is set during which the height cannot change again.
The weir uses either a submerged flow or a free flow formula, determined by the following ratio:
with:
Where:
- = The water level on the left side of the weir, relative to datum, at time .
- = The water level on the right side of the weir, relative to datum, at time .
- = The calculated upstream water level, relative to datum, at time .
- = The height of the weir at time t, according to the height adjustment mechanism.
- = The WEIR_TARGET_LEVEL of the weir.
- = Moment in time in seconds after which the weir can adjust its height again.
- = The WEIR_HEIGHT of the weir, at time .
- = The optionally adjusted height of the weir at time t, depending on the weir height adjustment mechanism.
- = The water bottom elevation at the left side of the weir.
- = The water bottom elevation at the right side of the weir.
- = The minimum allowed height for weir w.
- = The maximum allowed height for weir w.
- = The WEIR_MOVE_STEP_M of the water overlay, applicable to all weirs.
- = The WEIR_MOVE_RANGE_M of the water overlay, applicable to all weirs.
- = Current simulated time in seconds.
- = The WEIR_MOVE_INTERVAL_S of the water overlay, applicable to all weirs.
- = The height of the water column relative to the top of the weir, on the side with the highest water level, at time .
- = The height of the water column relative to the top of the weir, on the side with the lowest water level, at time .
- = The ratio of water heights on either side of the weir.
- = The potential rate of water flow across the weir.
- = The potential rate of water flow across the weir, based on a free flow calculation.
- = The potential rate of water flow across the weir, based on a submerged calculation.
- = Dutch weir factor, set to 1.7.
- = The WEIR_COEFFICIENT of the weir.
- = The WEIR_N of the weir.
- = The breadth of weir crest, adjustable using the WEIR_WIDTH.
- = Loss coefficient for submerged weirs, set to 0.9.
- = Flow area, based on the highest water column height relative to the top of the weir, and WEIR_WIDTH of the weir.
- = the acceleration due to gravity, set to 9.80665.
- = The water level change in meters, which takes place.
- = Computational timestep in seconds.
- = Cell size in meters.
To clarify the free flow formula in comparison with the ISO[1] standard definitions: When meters, the following holds.
- = The WEIR_COEFFICIENT of the weir, set to a default of 1.1
- = The WEIR_N of the weir, set to by default.
- = Calculated Coefficient of discharge.
- = acceleration due to gravity.
- = Weir head; the height of the water column relative to the top of the weir.
For generally larger than that, the flow can be calculated up to 5.5% smaller than expected when using the second pair of coefficients. However, this can be corrected with the weir coefficient if necessary.
Related
- Structures
- Weir
- Breach
- Models
- Surface model
- Formulas
- Breach flow formula
- Test cases
- Weir height test case
API Endpoints
- ↑ ISO FDIS 4360, 2020 Edition, March 3, 2020 - HYDROMETRY - OPEN CHANNEL FLOW MEASUREMENT USING TRIANGULAR PROFILE WEIRS ∙ Technical Committee: ISO/TC 113/SC 2 Flow measurement structures ∙ Found at: https://www.iso.org/standard/70915.html ∙ (last visited: 28-11-2022)