Breach flow formula (Water Overlay): Difference between revisions
mNo edit summary
(81 intermediate revisions by 4 users not shown)
Flow through breaches is calculated based on the [[Weir_formula_(Water_Overlay)|Weir formula]], including the consideration between free flow and submerged flow situations.
Flow through [[Breach (Water Overlay)|breach]]es is calculated based on the [[Weir formula (Water Overlay)|weir formula]], including the consideration between free flow and submerged flow situations.
The weir formula is supplied with Breach width, which is always calculated with the [[Breach_growth_formula_(Water_Overlay)|Breach growth formula]] before calculating the weir flow.
The weir formula is supplied with the breach width (as stand-in for the weir width), which is always calculated with the [[Breach growth formula (Water Overlay)|breach growth formula]] before calculating the weir flow. The downstream water level can be measured using a configured [[Breach level area_(Water Overlay)|Breach Level Area]], or one automatically placed based on the [[Breach measurement distance m (Water Overlay)|configured measurement distance]] and breach [[Breach angle (Water Overlay)|orientation]].
For the entry area, the area where the water originates from, the following also applies:<br>
The water level used is defined by either an [[Breach_input_area_(Water_Overlay)|input area]] or the [[External water level (Water Overlay)|external water level]].
In case of an external area, the surface height used is defined by [[External surface level (Water Overlay)|external surface level]]. This height limits how far the water level can be lowered.
* The water level used is defined by either an [[Breach input area (Water Overlay)|input area]] or the [[External water level (Water Overlay)|external water level]].
In case of an input area, the average water level is determined based on the individual grid cells of the input area.
* In case of an external area, the surface height used is defined by [[External surface level (Water Overlay)|external surface level]]. This height limits how far the water level can be lowered.
* Optionally a second value can be supplied for the [[External area (Water Overlay)|external area]]. In that case, the second value represents the area of the bottom.
* In case of an [[Breach input area (Water Overlay)|input area]], the average water level is based on the [[Surface water level formula (Water Overlay)|water level]] on the individual grid cells of the input area.
Each timestep, the external water level is changed based on the amount of water flowing in or out.
:<math>h_e = w_{e,t} - z_b</math>
| t=0
|''w<sub>e,t</sub> = w<sub>e,0</sub>
:<math>\Delta V = min(h_e \cdot A_s , Q_{w,t} \cdot \Delta t)</math>
| otherwise
In case <math>A_s = A_b</math>:
|''w<sub>e,t</sub> = w<sub>e,t-1</sub> - ( (Δw * cell) / A<sub>e</sub> )''
:<math>w_{e,t+1} = w_{e,t} - \frac{\Delta V}{A_b}</math>
Where:
Where:
* Δw = The water flow which takes place (out of the virtual external water source)
: <math>z_{b}</math> = Datum height of the bottom of the area water flows from.
* cell = Cell size
: <math>w_{e,t}</math> = The [[Surface water level formula (Water Overlay)|water level]] of the entry area at time <math>t</math>; In case of an external area: [[External water level (Water Overlay)|EXTERNAL_WATER_LEVEL]] of the [[Breach (Water Overlay)|breach]].
* w<sub>e,t</sub> = The water level of the entry area at time t.
: <math>h_e</math> = Relative water height in the external area.
* w<sub>e,0</sub> = The water level of the entry area; In case of an external area: [[External water level (Water Overlay)|EXTERNAL_WATER_LEVEL]] attribute of the breach.
: <math>Q_{w,t}</math> =  The calculated water flow which takes place at time <math>t</math>, based on the [[Weir formula (Water Overlay)|weir formula]].
* A<sub>e</sub> = The size of in the entry area; In case of an external area: [[External area (Water Overlay)|EXTERNAL_AREA]] attribute of the breach.
: <math>\Delta t</math> = The [[Timestep formula (Water Overlay)|timestep]] in seconds.
: <math>\Delta V</math> = The limited volume of water transported, based on the remaining water.
: <math>A_{s}</math> = The size of the entry area; In case of an external area: [[External area (Water Overlay)|EXTERNAL_AREA]] of the breach.
: <math>A_{b}</math> = The (optional) size of the bottom of the entry area; In case of an external area: the second value provided for the [[External area (Water Overlay)|EXTERNAL_AREA]] of the breach. In case only one value is provided, <math>A_{b} = A_{s}</math>
==Trapezoidal prism==
[[File:external_water_body_trapezoid.png|right|External water body as a trapezoid]]
The [[External area (Water Overlay)|external water area]] can also be represented as a trapezoidal prism. The new water level then has to be calculated differently.
The length and width of the surface area are currently considered equal. Therefore:
:<math>L = \sqrt{A_s}</math>
:<math>W_s = L</math>
The width of the bottom area is then calculated as:
:<math>W_b = \frac{A_b}{L}</math>
Next, we will calculate the new water level based on <math>\Delta V</math>:
:<math> h_{e,0} = w_{e,0} - z_b</math>
:<math>a = \frac{W_s-W_b}{4 \cdot h_{e,0}}</math>
:<math>A_{t,t} = 2 \cdot (a \cdot h_{e_t}^2 + 0.5 \cdot W_b \cdot h_{e_t})</math>
:<math>\Delta A = \frac{\Delta V}{L}</math>
:<math>c = \frac{-\Delta A * A_{t,t}}{2}</math>
:<math>D = (\frac{W_b}{2})^2 - 4 \cdot a \cdot c</math>
==Notes==
if <math> D < 0</math>, determine the new water level based on a box shape:
*The water level w<sub>e</sub> cannot become lower than the surface height s<sub>e</sub>, defined by [[External_surface_level_(Water_Overlay)|EXTERNAL_SURFACE_LEVEL]] in case of an external entry area. In case of an input area within the project, the surface height is determined per grid cell.
otherwise, determine the new water level based on the determinant and flow direction:
:<math>w_{-} = \frac{-\frac{W_b}{2} - \sqrt{D}}{2 \cdot a} + z_b</math>
:<math>w_{+} = \frac{-\frac{W_b}{2} + \sqrt{D}}{2 \cdot a} + z_b</math>
:<math>w_{e,t+1} =
\begin{cases}
w_{+} & \mbox{ if } \Delta V < 0 & \mbox{ and } w_{+} \le w_{e,t}\\
w_{-} & \mbox{ if } \Delta V < 0 & \mbox{ and } w_{+} > w_{e,t}\\
w_{+} & \mbox{ if } \Delta V \ge 0 & \mbox{ and } w_{-} < w_{e,t}\\
w_{-} & \mbox{ if } \Delta V \ge 0 & \mbox{ and } w_{-} \ge w_{e,t}\\
\end{cases}
</math>
Where:
: <math>L</math> = Length of the trapezoidal prism
: <math>A_{s}</math> = The size of the entry area; for external areas, this is the [[External area (Water Overlay)|EXTERNAL_AREA]] of the breach.
: <math>W_s</math> = Width of the original top (surface at <math>t = 0</math>) of the trapezoid
: <math>A_{b}</math> = The optional size of the entry area bottom; for external areas, this is the second [[External area (Water Overlay)|EXTERNAL_AREA]] value. If only one value is provided, <math>A_{b} = A_{s}</math>.
: <math>z_{b}</math> = Datum height of the bottom of the entry area.
: <math>W_b</math> = Width of the bottom of the trapezoid
: <math>h_{e,0}</math> = The initial relative water height in the external area.
: <math>h_{e,t}</math> = The relative water height in the external area at time <math>t</math> .
: <math>a</math> = Slope of the trapezoid
: <math>A_{t,t}</math> = Area of the trapezoidal side of the trapezoid prism at time <math>t</math>
: <math>c</math> = Constant based on new area of the trapezoid <math>A_{t,t+1}</math>
: <math>D</math> = Polynomial discriminant
==See also==
* [[Breach (Water Overlay)|Breach]]
|notes=
*The water level w<sub>e</sub> cannot become lower than the surface height s<sub>e</sub>, defined by [[External surface level (Water Overlay)|EXTERNAL_SURFACE_LEVEL]] in case of an external entry area. In case of an input area within the project, the [[Elevation model (Water Overlay)|surface height]] is determined per grid cell.
*When water is flowing from the project area to an external area, the slope of the external area remains the same, even when the water level rises above the original water level. In the case of a trapezoidal prism, it is extrapolated upwards.
|api=*[[Api session event editor overlay set attribute]]
==Related==
; Features
: [[Breach (Water Overlay)|Breach]]
; Formulas
: [[Weir formula (Water Overlay)|Weir formula]]
: [[Breach growth formula (Water Overlay)|Breach growth formula]]
; Models
: [[Surface model (Water Overlay)|Surface model]]
{{Template:WaterOverlay_nav}}
{{WaterOverlay formula nav}}
Latest revision as of 14:55, 12 October 2026
Flow through breaches is calculated based on the weir formula, including the consideration between free flow and submerged flow situations. The weir formula is supplied with the breach width (as stand-in for the weir width), which is always calculated with the breach growth formula before calculating the weir flow. The downstream water level can be measured using a configured Breach Level Area, or one automatically placed based on the configured measurement distance and breach orientation.
  • The water level used is defined by either an input area or the external water level.
  • In case of an external area, the surface height used is defined by external surface level. This height limits how far the water level can be lowered.
  • Optionally a second value can be supplied for the external area. In that case, the second value represents the area of the bottom.
  • In case of an input area, the average water level is based on the water level on the individual grid cells of the input area.
he=we,t−zb
ΔV=min(he⋅As,Qw,t⋅Δt)
In case As=Ab:
we,t+1=we,t−ΔVAb
Where:
zb = Datum height of the bottom of the area water flows from.
we,t = The water level of the entry area at time t; In case of an external area: EXTERNAL_WATER_LEVEL of the breach.
he = Relative water height in the external area.
Qw,t = The calculated water flow which takes place at time t, based on the weir formula.
Δt = The timestep in seconds.
ΔV = The limited volume of water transported, based on the remaining water.
As = The size of the entry area; In case of an external area: EXTERNAL_AREA of the breach.
Ab = The (optional) size of the bottom of the entry area; In case of an external area: the second value provided for the EXTERNAL_AREA of the breach. In case only one value is provided, Ab=As
Trapezoidal prism
The external water area can also be represented as a trapezoidal prism. The new water level then has to be calculated differently.
L=As
Ws=L
Wb=AbL
Next, we will calculate the new water level based on ΔV:
he,0=we,0−zb
a=Ws−Wb4⋅he,0
At,t=2⋅(a⋅het2+0.5⋅Wb⋅het)
ΔA=ΔVL
c=−ΔA*At,t2
D=(Wb2)2−4⋅a⋅c
if D<0, determine the new water level based on a box shape:
we,t+1=we,t−ΔVAb
w−=−Wb2−D2⋅a+zb
w+=−Wb2+D2⋅a+zb
we,t+1={w+ if ΔV<0 and w+≤we,tw− if ΔV<0 and w+>we,tw+ if ΔV≥0 and w−<we,tw− if ΔV≥0 and w−≥we,t
Where:
L = Length of the trapezoidal prism
As = The size of the entry area; for external areas, this is the EXTERNAL_AREA of the breach.
Ws = Width of the original top (surface at t=0) of the trapezoid
Ab = The optional size of the entry area bottom; for external areas, this is the second EXTERNAL_AREA value. If only one value is provided, Ab=As.
zb = Datum height of the bottom of the entry area.
Wb = Width of the bottom of the trapezoid
he,0 = The initial relative water height in the external area.
he,t = The relative water height in the external area at time t .
a = Slope of the trapezoid
At,t = Area of the trapezoidal side of the trapezoid prism at time t
c = Constant based on new area of the trapezoid At,t+1
D = Polynomial discriminant
  • The water level we cannot become lower than the surface height se, defined by EXTERNAL_SURFACE_LEVEL in case of an external entry area. In case of an input area within the project, the surface height is determined per grid cell.
  • When water is flowing from the project area to an external area, the slope of the external area remains the same, even when the water level rises above the original water level. In the case of a trapezoidal prism, it is extrapolated upwards.
API Endpoints