A Water Overlay is a [[Grid Overlay|grid overlay]] for which results are calculated by the [[Water Module]]. The [[Water_Module_Basics|Basic theory of the Water Module]] in the {{software}} is an implementation of a 2D grid based shallow water model based on the 2D Saint Venant equations. The module is further enhanced with infiltration, evaporation, groundwater flow and hydraulic structures. Depending on the use case, the simulated period can be set to few seconds and up to a few months. The [[Water_Module_Theory|theory]] section describes in detail how calculations are performed.
__NOTOC__
To perform the calculations, the project area is divided into a [[Grid overlay|grid of cells]]. Each cell has a specific quantity of water and specific hydrological parameters based on the data in the project. The total time which should be simulated is divided into discrete [[Timestep formula (Water Overlay)|timesteps]]. Per timestep, each cell communicates with its adjacent cells to exchange water, based on its water level, surface height, current flow direction and other factors. Accuracy and reliability is obtained by dividing the project area and simulation time into sufficiently small cells and steps, at the cost of more computation time.
==What are the Water Overlays==
The final results of the calculation can be inspected, as well as intermediate snapshots of the hydrological situation during the simulation, known as [[Timeframes (Water Overlay)|timeframes]].
* [[Rainfall_(Overlay)|Rainfall Overlay]]
* [[Flooding_(Overlay)|Flooding Overlay]]
* [[Groundwater_(Overlay)|Groundwater Overlay]]
==Tips on creating a new project when working with the Water Overlays==
When creating a new project in the [[Wizard|new project wizard]], take into account the [[Terrain_height#Terrain_height_in_the_Tygron_Platform|Advanced options]]. In this menu for example the [[GEO_Data|AHN3]] dataset can be selected, which, if available for your project area, provides the most recent heightdata available as Open Data. Also, the [[GEO_Data|IMWA]] dataset is already checked, this means that if available in your project area, Water Level areas and/or Culverts are already imported.
==Configuration==
{{Editor ribbon|header=Current situation|bar=Overlays|left panel=The water overlay|right panel=Configuration wizard}}
===Configuration wizard===
The Configuration Wizard can be found in the General tab of the overlay. <br> <br>
[[File:Config_wizard.JPG|900px]] <br><br>
For the [[Flooding_(Overlay)|Flooding Overlay]] the wizard has an extra step, the [[Rainfall_(Overlay)|Rainfall]] and [[Groundwater_(Overlay)|Groundwater Overlay]] wizard are basically the same.
<br>'''Step 1'''
<br>'''Step 2'''
In the second step the elements of the water system can be imported. In some sub-steps the there are four options: to do nothing and proceed, to import the data with the [[Geo_Data_Wizard|Geo data wizard]], or when you already have the data imported to select it based on an attribute of the data or to let the {{software}} automatically generate some data.
* the breach areas (only for the [[Flooding_(Overlay)|Flooding overlay]])
* water level areas; when automatically generating data one water level area covering the whole project area is created. The water level can be adjusted afterwards.
* ground water data
* sewer areas; can also be automatically generated based on the urbanization of the project area
* inundated areas; these are areas that are already inundated at the start of the flooding
* constructions; for the constructions keep in mind that when the data is point data, it has to overlap two water level areas. Therefore make sure the point data is on the border of two water level areas
** Weirs
** Culverts
** Pumps
** Sewer overflows; if chosen to automatically generate the sewer areas, the sewer overflows can also be automatically generated
<br>'''Step 3'''
Adjust, if needed, the hydrological coefficents used for the calculations for the [[Terrain#Surface|surface terrain]], the [[Terrain#Underground|underground terrain]] and the [[Functions#Function_values|function values]] (for example the amount of water storage for a certain type of building).
<br>'''Step 4'''
<br>'''Step 5'''
Also you can set the number of timeframes in the slider. The timeframes are the intermediate results of the calculation and are not the same as the timesteps. Each timeframe contains numerous timesteps, based on the grid cell size and the speed of the flooding (see for more information the [[Flooding_(Overlay)#Flooding_Model|Courant number]]). The more timeframes you choose, the more insight you will get into the calculation. Each of the timeframe results can be exported.
<br>'''Step 6'''
===Manual configuration===
==Data==
===Model connections===
====Terrain height====
{{main|Terrain height}}
Terrain height is modeled in the form of an underlying grid, potentially amended by a [[GeoTIFF]].
Terrain height is a required and automatic connection. Each [[project]] has a terrain height model. By default the terrain height model will be derived from data sources relevant to the geographical location of the project area. However, especially in water bodies the level of detail of the terrain height may be insufficient. For these situations it's possible to load in an additional GeoTIFF of terrain heights.
{{GeoTIFFSpec
|title=Groundwater
|description=The height of the ground water level across the project area.
|nodata=Data is unchanged from the base terrain height.
|value=Groundwater level
|unit={{mdatum}}
====Weather====
Weather in the {{software}} is modeled in the form of a [[weather|weather definition]].
[[Weather]] defines a number of environmental circumstances the hydrological model is subject to. It also defines the (total) {{inlink|simulation time}}.
=====Rain and simulation time=====
'''Linear configuration'''<br>{{RequestImage|description=Graph showing one period of rain, and one dry period. A second line showing the total amount of rain fallen up to that point. The total amount of time marked as simulation time.}}
{| class="wikitable"
! Property
! Unit
! Description
|Rain for
|minutes
|How long rain should last at the start of the simulation.
|Total rainfall
|mm
|How much rain should fall in the specified period.
|Dry after rain (days, hours, minutes)
|How long the simulation continues after the rain has fallen.
'''Custom configuration'''<br>{{RequestImage|description=Graph showing multiple periods of varying duration and varying rain intensities. A second line showing the total amount of rain fallen up to that point. The total amount of time marked as simulation time.}}
If a use-case requires a more complex sequence of rain than a single period of rain followed by a single dry period, it is possible to prepare a [[comma-separated values]] file with a sequence of periods and values.
{{CSVSpec
|title=Rain and simulation
|line=Additional rainfall until specified moment
|criteria=<!--
-->Time should always be greater than or equal to previous time<!--
--><br>Rain should never be negative<!--
|attribute=RAIN_M
|header1=Time|unit1=s
|header2=Rain|unit2=m
|l1e1=Time when first period ends|l1e2=Total rain during first period
|l2e1=Time when second period ends|l2e2=Total rain during second period
=====Evaporation=====
Evaporation is the consistent removal of water from the hydrological model over a specified period of time. As long as evaporation takes places at a certain rate, water both on the surface and underground can be subject to removal from the hydrological model. The evaporation rate defined by the weather is the base amount of evaporation for the {{inlink|Evaporation model|evaporation model}}.
'''Linear configuration'''<br>{{RequestImage|description=Graph showing constant amount of evaporation, and a fictive water amount decreasing consistently over time.}}
! Property
! Unit
! Description
|Surface evaporation
|mm/day
|The speed at which water evaporates during the simulation
'''Custom configuration'''<br>{{RequestImage|description=Graph showing varying amounts of evaporation in multiple periods, and a fictive water amount decreasing consistently over time with the speed of the evaporation.}}
If a use-case requires a more complex pattern of evaporation than a single evaporation rate, it is possible to prepare a [[comma-separated values]] file with a sequence of periods and values.
{{CSVSpec
|title=Evaporation
|line=Rate of evaporation until specified moment
|criteria=<!--
--><br>Evaporation should never be negative<!--
|attribute=RAIN_M
|header2=Evaporation|unit2=m
|l1e1=Time when first period ends|l1e2=Amount of evaporation during first period
|l2e1=Time when second period ends|l2e2=Amount of evaporation during second period
====Ground water====
Ground water in the {{software}} is modeled in the form of a [[GeoTIFF]].
The hydrological model can simulate the {{inlink|underground model|underground}} environment as well. To enhance the level of detail of the underground environment, it is possible to connect a groundwater [[GeoTIFF]] to the water model. The ground water GeoTIFF will dictate the underground water levels relative to {{datum}} at the start of the simulation, influencing how much more water can be stored underground and how much water can flow from the underground.
Ground water is only a relevant connection when the {{inlink|underground model}} is active. If the ground water model is not active, a connection with a ground water model is not relevant, regardless of whether it's present or not.
Ground water is an optional connection. If no ground water is connected to the water model, the ground water level relative to {{datum}} is equal to the water level as defined by the {{inlink|water level areas}}.
{{GeoTIFFSpec
|title=Groundwater
|unit={{mdatum}}
====Subsidence====
Subsidence in the {{software}} is modeled in the form of a [[Subsidence_(Overlay)|subsidence overlay]].
The hydrological model is greatly influenced by the [[terrain height|height of the terrain]]. In virtually all cases water flows from higher places to lower places. The water model can be connected to a [[Subsidence_(Overlay)|subsidence]] calculation which affects the terrain height. This allows the model to take into account a period of subsidence which changes the terrain, and calculate the impact, effects, and flow in the future.
Subsidence is an optional connection. If no subsidence model is connected to the water model, no subsidence is applied to the model prior to the calculations. Other effects on the terrain height, such as {{inlink|breach}}es, still apply.
===Hydrological features===
The water system can be enhanced with a number of hydrological features, which can be loaded in as [[area]]s. These hydrological features form special properties or modifications on the hydrological system.
====Water level area====
A water level area represents real-world water level areas. Within a water level area, the heights of all water [[terrain]]s are set to a specified level. {{RequestImage|description=An image (before)showing a terrain with part of it marked as water terrain. A second image (after) showing the same terrain, with the water terrain no longer specially marked but with a quantity of water on top. Both images have one valley marked as water terrain and another one which is regular terrain.}}
! Attribute
! Unit
! Description
! Default (when attribute is not present)
|{{anchor|WATER_LEVEL|WATER_LEVEL}}
|{{mdatum}}
|The water level for all water terrains in this water level area
|n/a
====Sewer area====
A sewer area is part of the definition of a system of sewers in the specified area. Sewer storage is present in the hydrological model wherever the sewer area intersects with a {{inlink|Sewered constructions|sewered construction}}.
! Attribute
! Unit
! Description
|{{anchor|SEWER_STORAGE|SEWER_STORAGE}}
|m
|The maximum height the water can reach in this sewer. This value, multiplied by the surface area of the sewered constructions the sewer area intersects with, forms the total amount of water this sewer can store.
|n/a
|{{anchor|SEWER_PUMP_SPEED|SEWER_PUMP_SPEED}}
|m3/s
|The amount of water removed from the sewer by removing it from the hydrological model entirely.
|0
Sewers don't have default storage amount, but when generating them automatically in the {{inlink|configuration wizard}}, suggested values are 0,007m for older sewers and 0,04 for newer sewers.
====Breach====
A breach is a modification to the [[terrain height]], with an optional in- or outflow of water for the hydrological model. This can be used to represent calamitous situations, such as a breach in a levee. Breaches can also be used to easily simulate a terrain height increase, effectively creating a levee.
A breach can either be defined solely as a terrain height modification using its {{inlink|SURFACE_OVERRIDE}} attribute, or as an in- or outlet by adding an {{inlink|INLET_Q}} attribute as well. If the breach is only defined as a terrain height change, only water that is already created or defined in some other way in the hydrological model can flow through and from it. If the breach is also given an inlet speed, water will automatically be created or removed uniformly on the breach.
! Attribute
! Unit
! Description
|{{anchor|SURFACE_OVERRIDE|SURFACE_OVERRIDE}}
|{{mdatum}}
|The new [[terrain height]] at the location of the breach.
|n/a
|{{anchor|INLET_Q_breach|INLET_Q}}
|m3/sec
|The maximum amount of water flowing into the model through this breach. A negative value means the breach functions as an outlet, and water is removed from the hydrological model.
|0
|{{anchor|INLET_CAPACITY_breach|INLET_CAPACITY}}
|m3
|The maximum, total amount of water which can flow in or out through this breach. Water flowing back in the other direction replenishes the capacity.
|Infinite
|{{anchor|LOWER_THRESHOLD_breach|LOWER_THRESHOLD}}
|{{mdatum}}
|If a lower threshold is set, water will only flow into the model through this breach until the average water level on this breach is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion.
|None
|{{anchor|UPPER_THRESHOLD_breach|UPPER_THRESHOLD}}
|{{mdatum}}
|If an upper threshold is set, water will only flow out the model through this breach until the average water level at the point of this breach is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion.
|None
Also note that a breach shares attribute names with the {{inlink|inlet}}s, and that changing the attribute keys for breaches also affects the keys for inlets.
====Inundation====
An inundation is an initial placement of a quantity of water. This differs from the {{inlink|water level area}}s in that an inundation level allows you to place water anywhere on the surface.{{RequestImage|description=Same image as for water area, but in which the water terrain is already filled and the other valley isn't, but in the second image is filled with water.}}
! Attribute
! Unit
! Description
|{{anchor|INUNDATION_LEVEL|INUNDATION_LEVEL}}
|{{mdatum}}
|The height of the water.
|n/a
===Hydrological constructions===
The water system can be enhanced with a number of hydrological [[construction]]s. These are constructions which effect water flow in specific cells, according to the parameters and rules of the constructions used. The effects of these constructions can be adjusted by setting the appropriate attributes.
* {{Anchor|Line-based constructions}}'''Line-based constructions'''<br>{{RequestImage|description=A simple polygon shape (rectangle), then the visualization of the skeleton lines, then the highlighting of the relevant endpoints.}}Line-based constructions form a direct connection between two exact cells, allowing water to flow from one point to another. The flow is dictated by the construction's formula. The endpoints of a line-based construction, the exact cells which are connected by the construction, are computed based on the orientation and size of their polygon. Essentially, the furthest ends of the polygon are used as end-points. Because the cells are considered adjacent, any calculated flow through line-based hydrological constructions is instantaneous.
* {{Anchor|Point-based constructions}}'''Point-based constructions'''<br>{{RequestImage|description=A simple polygon shape (square), then the visualization of the calculation of the centerpoint, and finally the highlighting of the endpoint.}}Point-based constructions add or remove water in one or more computational layers, based on their formula's. The centerpoint of a point-based construction, the exact cell where the effect takes place, is is the geometric center of the construction's polygon.
Note that the more complex the polygon is, the more difficult it is for the {{software}} to resolve it to a simple line or center point.
====Culvert====
A culvert is a {{inlink|Line-based constructions|line-based construction}}.
! Attribute
! Unit
! Description
! Default
|{{anchor|CULVERT_WIDTH|CULVERT_WIDTH}}
|m
|The diameter of the culvert. For throughput calculations, the culvert is assumed to have a spherical cross-section.
|1
|{{anchor|CULVERT_HEIGHT|CULVERT_HEIGHT}}
|{{mdatum}}
|The height of the culvert. (When set to a level lower than the terrain for either endpoint of it, the culvert's height is equal to the height of the (highest) terrain under either endpoint.)
|0
|{{anchor|CULVERT_N|CULVERT_N}}
|manning value
|The manning value of the culvert's material, which influences the flow speed.
|0,014
====Weir====
A weir is a {{inlink|Line-based constructions|line-based construction}}.
! Attribute
! Unit
! Description
! Default
|{{anchor|WEIR_HEIGHT|WEIR_HEIGHT}}
|{{mdatum}}
|The height of the weir.
|n/a
|{{anchor|WEIR_WIDTH|WEIR_WIDTH}}
|m
|The width of the weir.
|5
|{{anchor|WEIR_COEFFICIENT|WEIR_COEFFICIENT}}
|coefficient
|The flow coefficient related to the shape of the weir
|1,1
====Pump====
A pump is a {{inlink|Line-based constructions|line-based construction}}.
! Attribute
! Unit
! Description
! Default
|{{anchor|PUMP_SPEED|PUMP_SPEED}}
|m3/s
|The speed at which water is pumped from the lower end-point to the higher end-point.
|n/a
====Sewer overflow====
Sewer overflows are points where water is moved from the sewer area to the above-ground water system. A sewer overflow will allow water to flow through if the water in the sewer exceeds the {{inlink|SEWER_OVERFLOW_THRESHOLD}}, and the water in the connected sewer exceeds the height of the terrain at the location of the sewer overflow. It will then function for all sewers part of that sewer area.
A sewer overflow is a {{inlink|Point-based constructions|point-based construction}}. It must intersect with a {{inlink|Sewer area|sewer area}}, but does not need to intersect with a an actual sewer.
! Attribute
! Unit
! Description
! Default
|{{anchor|SEWER_OVERFLOW|SEWER_OVERFLOW}}
|{{mdatum}}
|The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water level in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out.
|n/a
|{{anchor|SEWER_OVERFLOW_SPEED|SEWER_OVERFLOW_SPEED}}
|m3/s
|The maximum speed at which water can flow out from the sewer through this overflow.
|10
====Inlet====
An inlet is a {{inlink|Point-based constructions|point-based construction}}.
! Attribute
! Unit
! Description
! Default
|{{anchor|INLET_Q_constructions|INLET_Q}}
|m3/sec
|The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model.
|n/a
|{{anchor|INLET_CAPACITY_constructions|INLET_CAPACITY}}
|m3
|The maximum amount of water which can flow in or out through this construction. Water flowing back in the other direction replenishes the capacity.
|Infinite
|{{anchor|LOWER_THRESHOLD_constructions|LOWER_THRESHOLD}}
|{{mdatum}}
|If a lower threshold is set, water will only flow into the model through this inlet until the water level at the point of this inlet is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion.
|None
|{{anchor|UPPER_THRESHOLD_constructions|UPPER_THRESHOLD}}
|{{mdatum}}
|If an upper threshold is set, water will only flow out the model through this outlet until the water level at the point of this inlet is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion.
|None
Also note that an inlet shares attribute names with the {{inlink|Breach|breach}}es, and that changing the attribute keys for inlets also affects the keys for breaches.
===Miscellaneous hydrological properties of constructions===
The effects of these constructions can be adjusted by setting the appropriate attributes. In some cases, these are attributes which relate to [[function value]]s. For these attributes, either can be adjusted to the same effect. Note that attributes which are connected to a function can be redefined, like the attribute names for {{inlink|hydrological constructions}} and {{inlink|hydrological features}} can be redefined.
In contrast with {{inlink|Hydrological constructions|hydrological constructions}} and their properties, all constructions can have any or all of the following miscellaneous effects on the hydrological model.
====Sewered constructions====
Sewered constructions are constructions under which a sewer exists, and through which water can flow into the sewer. When a sewered connection overlaps with a {{inlink|sewer area}}, that overlap forms an actual sewer, with the storage capacity of the {{inlink|SEWER_STORAGE}} attribute of the sewer area. Any surface water entering the cell of a sewered construction is directly moved to the sewer (unless the sewer is filled to capacity).
! Attribute
! Unit
! Function value
! Description
|{{anchor|SEWERED|SEWERED}}
|boolean
|Connected to sewer
|Whether this construction is connected to the sewer.
====Water storage constructions====
! Attribute
! Unit
! Function value
! Description
|{{anchor|WATER_STORAGE|WATER_STORAGE}}
|m³/m²
|Water storage (m³/m²)
|How much water this construction can store.
====Porous constructions====
! Attribute
! Unit
! Function value
! Description
|{{anchor|GROUND_INFILTRATION_MD_constructions|GROUND_INFILTRATION_MD}}
|m/day
|Ground infiltration per day (m)
|The speed at which water can flow vertically from the surface to the underground unsaturated zone.
====Crops and foliage====
! Attribute
! Unit
! Function value
! Description
|{{anchor|ROOT_DEPTH_M_constructions|ROOT_DEPTH_M}}
|m
|Depth of plant roots (m)
|The depth of the roots of this construction, relative to the terrain height at the location of this construction. Water can be drawn from the underground and evaporated if the roots can reach it.
|{{anchor|WATER_EVAPORATION_FACTOR_constructions|WATER_EVAPORATION_FACTOR}}
|factor
|Water evaporation
|How fast this construction can evaporate water from the underground. The {{inlink|weather}}'s evaporation speed is multiplied by this factor to determine the rate of evaporation.
====Critical structures====
Some constructions may be considered critical, meaning the consequences of water stress are greater for these structures than for others. Examples include hospitals and (elementary) schools. Critical constructions will receive additional highlighting by the {{inlink|IMPACTED_BUILDINGS}} result type when the building is impacted by the amount of water defined by {{inlink|IMPACT_FLOOD_THRESHOLD_M}}.
! Attribute
! Unit
! Function value
! Description
|{{anchor|CRITICAL_INFRASTRUCTURE|CRITICAL_INFRASTRUCTURE}}
|nominal integer
|Critical infrastructure
|Whether this construction is deemed a critical construction. 0 means the construction is never deemed impacted.
====Chemical emitters/decomposers====
! Attribute
! Unit
! Description
! Default
|{{anchor|CHLORIDE_constructions|CHLORIDE}}
|x/m²
|The amount of chloride created per second per m² in this location.
|0
|{{anchor|NITROGEN_constructions|NITROGEN}}
|x/m²
|The amount of nitrogen created per second per m² in this location.
|0
|{{anchor|PHOSPHORUS_constructions|PHOSPHORUS}}
|x/m²
|The amount of phosphorus created per second per m² in this location.
|0
Chemical emitters's attributes do not take the form of function values, and must be added manually<!--[[constructions#Adding_attributes]]--> or as part of [[Geo_Data_Wizard|loading in geodata]].
===Hydrological properties of terrain===
[[Terrain]]s in a project have a number of hydrological properties which can influence the flow of water in a project. The following attributes of terrains have effects on the hydrological model:
====Water====
Water terrains are processed by the water model in a specific manner before the simulation is started. For each water terrain in the 3D world, the bottom of the water body is treated as a land surface in the same fashion as dry land. Water is then placed on it on the surface {{inlink|layers|layer}}, up to the level defined by the overlapping {{inlink|Water level area|water area}}'s {{inlink|WATER_LEVEL}} attribute. Terrains not marked as water terrain are not initiated with water.
Terrains marked as water are subject to an additional check for the {{inlink|WATER_STRESS}} {{inlink|Result types|result type}}. If the amount of water on a water terrain has not increased by more than {{inlink|ALLOWED_WATER_INCREASE_M}} relative to the {{inlink|Water level area|water level area}}'s water level, that terrain will not count as stressed for that result type. The amount of water on that location must be at least {{inlink|ALLOWED_WATER_INCREASE_M}} more than the {{inlink|Water level area|water level area}}'s water level.
! Attribute
! Unit
! Terrain type
! Description
|{{anchor|WATER|WATER}}
|boolean
|Surface
|Whether the specified terrain is a water terrain.
====Evaporation{{anchor|Evaporation_terrain}}====
! Attribute
! Unit
! Terrain type
! Description
|{{anchor|ROOT_DEPTH_M_surface|ROOT_DEPTH_M}}
|m
|Surface
|The depth of the roots of this surface terrain, relative to the surface. Water can be drawn from the underground and evaporated if the roots can reach it.
|{{anchor|WATER_EVAPORATION_FACTOR_surface|WATER_EVAPORATION_FACTOR}}
|factor
|Surface
|How fast this terrain can evaporate water from the underground. The {{inlink|weather}}'s evaporation speed is multiplied by this factor to determine the rate of evaporation.
Also note that the groundwater level reduction is inversely proportional to the {{inlink|WATER_STORAGE_PERCENTAGE}}, as the contribution of a given volume of water to the groundwater level increases as the capacity for water storage in the underground layer decreases.
====Infiltration and storage====
! Attribute
! Unit
! Terrain type
! Description
|{{anchor|GROUND_INFILTRATION_MD_surface|GROUND_INFILTRATION_MD}}
|m/day
|Surface
|{{anchor|GROUND_INFILTRATION_MD_underground|GROUND_INFILTRATION_MD}}
|m/day
|Underground
|The speed at which water can flow vertically from the underground unsaturated zone to the underground saturated zone, and horizontally through across the saturated zone.
|{{anchor|WATER_STORAGE_PERCENTAGE|WATER_STORAGE_PERCENTAGE}}
|percentage
|Underground
|The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer.
===Result types===
* {{Anchor|Start_resulttype}}'''Start''': The data is determined at the start of the simulation, and does not change afterwards.
* {{Anchor|Last_resulttype}}'''Last''': The data is the latest value determined at the timestep the data is recorded. The values can increase and decrease between different timesteps. This mode is primarily used for monitoring progression.
* {{Anchor|Maximum_resulttype}}'''Maximum''': The data is the highest value determined up until the timestep the data is recorded. The values can only increase or stay the same, but will never decrease. This mode is primarily used to gain insight into impact; the most severe situation any point had to endure.
* {{Anchor|Total_resulttype}}'''Total''': The result of a running tally, counting the relevant data up until the timestep the data is recorded. The value can only increase or stay the same, but will never decrease. This mode is primarily used to gain insight into quantities rather than duration.
! Result type
! Unit
! Display mode
! Description
|{{anchor|BASE_TYPES|BASE_TYPES}}
|Nominal value
|{{inlink|Start_resulttype|Start}}
|Categorization of the individual cells based on how they are processed by the water model, displaying which cells are considered to be specific features.<br>
0: Cell on the edge of the project area<br>
1: Water level area<br>
2: Land<br>
3: Sewer<br>
4: Breach<br>
5: Hydrological construction
|{{anchor|CHLORIDE|CHLORIDE}}
|x/m²
|{{inlink|Last_resulttype|Last}}
|The amount of chloride present. The value is the sum of the quantities on the surface, and the underground.
|{{anchor|DIRECTION|DIRECTION}}
|Degrees
|The direction in which water is flowing.
|{{anchor|EVAPORATED|EVAPORATED}}
|m (mm)&sup1;
|{{inlink|Total_resulttype|Total}}
|The amount of water that has evaporated. The value is the sum of the quantities evaporated from the surface and the underground.
|{{anchor|GPU OVERVIEW|GPU OVERVIEW}}
|nominal value
|{{inlink|Maximum_resulttype|Maximum}}
|Shows which GPU cluster calculated which part of the overlay.
|{{anchor|IMPACTED_BUILDINGS|IMPACTED_BUILDINGS}}
|nominal value
|Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in {{inlink|IMPACT_FLOOD_TRESHOLD_M}}.<br>
0: Construction is not impacted<br>
1...N: The {{inlink|Critical structures|(critical) construction}} is impacted, and has a critical [[function value]] set to this value.
|{{anchor|LAST SPEED|LAST SPEED}}
|m/s
|The speed of water flow in any given location.
|{{anchor|MAX SPEED|MAX SPEED}}
|m/s
|{{anchor|NITROGEN|NITROGEN}}
|x/m²
|The amount of nitrogen present. The value is the sum of the quantities on the surface, and the underground.
|{{anchor|PHOSPHORUS|PHOSPHORUS}}
|x/m²
|The amount of phosphorus present. The value is the sum of the quantities on the surface, and the underground.
|{{anchor|SEWER_LAST_VALUE|SEWER_LAST_VALUE}}
|m (mm)&sup1;
|The amount of water stored in the sewer.
|{{anchor|SEWER_MAX_VALUE|SEWER_MAX_VALUE}}
|m (mm)&sup1;
|{{anchor|SURFACE_DURATION|SURFACE_DURATION}}
|s (min)&sup1;
|The amount of time the water depth on the surface exceeds {{inlink|SHOW_DURATION_FLOOD_LEVEL_M}}.
|{{anchor|SURFACE_FLOW|SURFACE_FLOW}}
|m&sup3;/m&sup2;
|''Description wil be added'' <!--Total volume of water passed a grid-cell, scaled by the cell surface (grid cell-size^2)-->
|{{anchor|SURFACE_LAST_VALUE|SURFACE_LAST_VALUE}}
|m (mm)&sup1;
|The amount of water on the surface.
|{{anchor|SURFACE_MAX_VALUE|SURFACE_MAX_VALUE}}
|m (mm)&sup1;
|{{anchor|UNDERGROUND_FLOW|UNDERGROUND_FLOW}}
|m&sup3;/m&sup2;
|''Description wil be added'' <!--Amount of water which has infiltrated from the surface to the underground-->
|{{anchor|UNDERGROUND_LAST_STORAGE|UNDERGROUND_LAST_STORAGE}}
|m (mm)&sup1;
|The (effective) amount of water in the underground unsaturated zone.
|{{anchor|UNDERGROUND_LAST_VALUE|UNDERGROUND_LAST_VALUE}}
|m (mm)&sup1;
|The distance between the surface and the groundwater level.
|{{anchor|UNDERGROUND_MAX_STORAGE|UNDERGROUND_MAX_STORAGE}}
|m (mm)&sup1;
|{{anchor|UNDERGROUND_MAX_VALUE|UNDERGROUND_MAX_VALUE}}
|m (mm)&sup1;
|{{anchor|UNDERGROUND WATERTABLE|UNDERGROUND WATERTABLE}}
|{{mdatum}}
|The groundwater level, relative to [[datum]].
|{{anchor|WATER_STRESS|WATER_STRESS}}
|m (mm)&sup1;
|The amount of water on the surface, similar to {{inlink|SURFACE_MAX_VALUE}}. However, for water terrains, the water level must rise by at least {{inlink|ALLOWED_WATER_INCREASE_M}}. Otherwise, the value in those locations is 0.
&sup1; the units between () are as displayed in the 3D client. If exported to GeoTiff the SI-convention is used: meters (m) and seconds (s).
====Result child overlays====
Result child overlays do not recalculate if either they or their parent is set to [[Grid_overlay#active|inactive]].
If a calculation overlay is removed, all result child overlays which are children of that overlay are removed as well. Separate overlays set as child overlays (such as [[Input overlays|input overlays]]) of the overlay will not be removed.
It is only possible to add result child overlays via the {{inlink|Configuration wizard|configuration wizard}}.
==Calculations==
===Models===
====Surface model====
The water model's primary function is the simulation of the flow of water on the surface of the terrain. The surface model includes the flow of water across the surface of the terrain, including over {{inlink|Water|water terrains}}, including the flow through {{inlink|Hydrological constructions|hydrological constructions}} and water that is created or removed by hydrological constructions.
The surface is defined by the {{inlink|Terrain height|terrain height}} in the project. The terrain height is further influenced by the height of constructions present in the project (bounded by {{inlink|DESIGN_FLOOD_ELEVATION_M}}) and by the {{inlink|SURFACE_OVERRIDE}} of {{inlink|breach}}es.
The surface water level is initialized based on hydrological features present in the project. For all {{inlink|Water|water terrains}}, water is placed on the surface of the world. The amount of water placed is such that the resulting water level in that location is equal to the {{inlink|WATER_LEVEL}} attribute of the {{inlink|Water level area}} in that location. If there is no water level area in that location, the water level is assumed to be so low that no water is created. Besides the water level areas, {{inlink|Inundation}} is added to the model. Water is placed in all locations where inundation is defined (regardless of the terrain type in that location, in contrast to the water level areas), such that the resulting height of the water inundating the land is equal to the inundation area's {{inlink|INUNDATION_LEVEL}} attribute.
In addition to water flowing between geographically adjacent cells, water can also flow through {{inlink|Hydrological constructions|hydrological constructions}}. When a {{inlink|Line-based_constructions|line-based hydrological construction}} exists in the project area, the 2 cells indicated by the endpoints of the line are considered adjacent as well. Flow between those cells is not dictated by the same parameters as the regular surface flow. Instead, water can flow between the 2 indicated cells based on the construction's underlying formula.
Water can also be added to or removed from the water model by {{inlink|Point-based_constructions|point-based hydrological constructions}}. Based on the construction's underlying formula water can be added or removed to the cell indicated by the construction. Only that single cell will receive or lose the calculated amount of water.
Water can also be removed from the surface by {{inlink|Miscellaneous hydrological properties of constructions|other properties}} of constructions, based on the construction's polygons (either moving it to another part of the hydrological model, or removing it completely from the hydorlogical model). When water is removed from the surface via a polygon-based construction, the removal of water is calculated per individual cell.
====Underground model====
The underground model can be explicitly activated or deactivated by setting the {{inlink|GROUND_WATER}} attribute of the water overlay to the appropriate value. If the underground model is deactivated, no water can move from or to the underground in any form, including {{inlink|Underground_evaporation_model|underground evaporation}}.
The underground is bounded vertically by the {{inlink|Surface model|surface of the terrain}} at the top, and an assumed impenetrable layer at the bottom. The distance between the surface and the impenetrable layer, and thus the effective height of the underground, is equal to {{inlink|GROUND_BOTTOM_DISTANCE_M}}. In other words, the impenetrable underground layer is assumed to be a set distance below the surface. The distance is uniform across the entire project area, and follows the profile of the surface.
The groundwater level, and thus the height of the saturated zone, is determined both by the amount of water in the saturated zone, and the underground terrain's {{inlink|WATER_STORAGE_PERCENTAGE|WATER_STORAGE_PERCENTAGE}}. The lower the water storage percentage of the soil, the greater the volume of soil that is saturated by the same amount of water, and thus the higher the the groundwater level will become.
The underground water level is initialized with the values of the {{inlink|Ground water GeoTIFF}} connected to the water model. If no ground water data is connected, the ground water level relative to {{datum}} is equal to the surface water level relative to {{datum}}, as defined by the {{inlink|WATER_LEVEL}} attribute of the {{inlink|Water level area}} in that location.
When water infiltrates from the surface, it infiltrates at a speed dictated by the surface terrain's {{inlink|GROUND_INFILTRATION_MD_surface|GROUND_INFILTRATION_MD}} attribute, or (if present) by the construction's {{inlink|GROUND_INFILTRATION_MD_constructions|GROUND_INFILTRATION_MD}}, whichever value is lower. If a highly porous constructions is present above a non-porous surface terrain, or the other way around, the lower infiltration value of either will cause the water to infiltrate slower despite the porous properties of the other.
Surface water infiltrates into the underground unsaturated layer. Water in the unsaturated layer is assumed to be spread equally across the entire unsaturated volume. Water then flows from the unsaturated zone into the saturated zone at the speed dictated by the underground terrain's {{inlink|GROUND_INFILTRATION_MD_underground|GROUND_INFILTRATION_MD}}. For a given timestep, the distance the water travels is determined. The amount of water that flows from the unsaturated zone to the saturated zone is equal to the amount of water in a section of the unsaturated zone the height of which is equal to that distance. After water has been added to the saturated zone, the groundwater level (and thus the height of the saturated zone) is redetermined. The water in the unsaturated zone is redistributed uniformly across the (remaining) unsaturated zone.
Water stored in the underground saturated zone can flow horizontally from one underground cell to another, if the groundwater level relative to {{datum}} is higher than the neighboring cell's ground water level, relative to {{datum}}. The amount of water which can flow from one cell to another is dictated by the underground terrain's {{inlink|GROUND_INFILTRATION_MD_underground|GROUND_INFILTRATION_MD}}.
Water stored in the underground saturated zone can also exfiltrate out of the underground and back onto the surface, if the groundwater level relative to {{datum}} exceeds the neighboring cell's surface water level relative to {{datum}}. The amount of water which can flow from the underground of one cell onto the surface of an adjacent cell is dictated by the underground terrain's {{inlink|GROUND_INFILTRATION_MD_underground|GROUND_INFILTRATION_MD}}.
====Rain model====
Rain can be implicitly activated and deactivated by defining an appropriate period of {{inlink|Rain and simulation time|rainfall}}. If a period with no rainfall is defined, that period is simulated but no rain is simulated.
Currently, during a period in the simulation where {{inlink|Rain and simulation time|rainfall}} is defined, water is uniformly added to the {{inlink|Surface model|surface}} of all cells in the project area. During any single defined period of rain, the amount of rain is consistent over time. At the end of the defined period of rain, exactly the defined amount of rain will have fallen on each cell.
====Evaporation model====
All forms of evaporation can be implicitly activated and deactivated by setting the {{inlink|Weather|weather}}'s {{inlink|Evaporation|evaporation rate}}. If the evaporation factor is set to 0, no evaporation will take place in any form.
=====Surface evaporation model=====
Water can evaporate from the {{inlink|Surface_model|surface}}, based on the {{inlink|Weather|weather}}'s {{inlink|Evaporation|evaporation factor}} and the overlay's {{inlink|SURFACE_WATER_EVAPORATION_FACTOR}}. These values compute to a net rate of evaporation which is applied to the surface of all cells. Only water on the surface of cells is affected by this evaporation.
=====Underground evaporation model=====
Water can evaporate from the {{inlink|Underground_model|underground}} if the cell has either a {{inlink|Crops and foliage|construction which allows for underground evaporation}}, or a {{inlink|Evaporation terrain|surface terrain type}} which allows for underground evaporation and is unobstructed by a construction. In other words: if a construction is present the construction's properties are used, otherwise the terrain's properties are used.
Underground evaporation can be implicitly activated or deactivated by setting the relevant properties of all terrain types and constructions to appropriate evaporation values. If the relevant properties are set to 0, no underground evaporation will take place. Underground evaporation is also explicitly deactivated when the {{inlink|Underground_model|underground_model}} is deactivated.
The rate of evaporation is determined by the {{inlink|Weather|weather}}'s {{inlink|Evaporation|evaporation factor}}, and either the construction's {{inlink|WATER_EVAPORATION_FACTOR_constructions|WATER_EVAPORATION_FACTOR}} or the surface terrain's {{inlink|WATER_EVAPORATION_FACTOR_surface|WATER_EVAPORATION_FACTOR}}.
Evaporation can only take place if the roots of the terrain or construction can reach underground water. The depth the roots can reach is defined by either the construction's {{inlink|ROOT_DEPTH_M_constructions|ROOT_DEPTH_M}} or the surface terrain's {{inlink|ROOT_DEPTH_M_surface|ROOT_DEPTH_M}}.
====Sewer model====
Sewers can be implicitly activated and deactivated by adding or removing {{inlink|Sewer area|sewer area}}s. If no sewer areas exist, no sewers are available in the water model and no water can flow to and from there.
Sewer areas define the areas in which sewers exist. The capacity of those sewers is based on the sewer area's {{inlink|SEWER_STORAGE}} attribute. The actual locations where the sewer exists is the intersection between the sewer areas and the {{inlink|Sewered constructions|sewered constructions}} in the project area. The total surface area of the actual sewer is equal to that intersection.
If there is water on the {{inlink|Surface model|surface}}, in a cell with a sewered construction, and there is a sewer present in the same location, the water flows directly into the sewer. Water can flow in until the sewer is filled to capacity. Water can only flow into a sewer a via sewered construction. It is not possible for water to flow from a sewer back to the surface via a sewered construction, unless that construction is is explicitly a sewer overflow.
Water can flow from a sewer overflow back onto the surface via a {{inlink|Sewer overflow|sewer overflow}}. A sewer overflow removes water from the sewer and places it on the surface of the cell where the overflow is located. The speed at which this water flows is determined by the {{inlink|SEWER_OVERFLOW_SPEED}}.
To overflow from the sewer to the surface, two criteria need to be met. Firstly, the amount of water in the sewer relative to the sewer's total capacity must exceed the {{inlink|SEWER_OVERFLOW_THRESHOLD}}. Secondly, the water level in the sewer must exceed the terrain height at the location of the sewer overflow.
Water can be removed from a sewer based on the sewer area's {{inlink|SEWER_PUMP_SPEED}}. Water removed from the sewer in this way is removed entirely from the hydrological model.
====Storage model====
Water on the {{inlink|Surface model|surface model}} can be stored in {{inlink|Water storage constructions|water storage constructions}}.
When water flows onto a cell with a {{inlink|Water storage constructions|construction capable of storing water}}, that water will be stored in the construction until the construction's water storage capacity has been reached. Water cannot leave that storage, either through flow back into the hydrological model or by being removed from it altogether. When the storage is filled, no additional water cannot flow into that storage for the remainder of the simulation.
====Chemical flow model====
Chemicals are tracked as an exact amount on a given location. The exact unit and magnitude is not defined in the {{software}}, as the calculations for chemicals function the same for all magnitudes.
Chemicals are added to the hydrological model and removed from the hydrological model by {{inlink|Chemical emitters/decomposers|chemical constructions}}. The chemicals created are then placed on the {{inlink|Surface model|surface}} of the cells where they are created. Chemicals can also be removed by chemical constructions, if their attributes are configured appropriately. When chemicals enter the cell which contains a chemical decomposer, the chemicals are removed from the hydrological model.
====Model border====
===Formulas===
====Timestep formula====
An adaptive timestep is implemented according to Kurganov and Petrova (2007)<ref name="Kurganov1" />. At every timestep, the courant-number is kept smaller than 0.25 for every active computation cell.
[[File:Inundation_overlay_03.PNG|400px]]
* the timestep is choosen so that all computation cells follow one of the following criteria.
* if a cells waterdepth is below the flooding threshold, 5 * 10<sup>-3</sup> (m) there is no flow assumed between that cell and it neigboring cell.
* if the cells waterdepth is above above the flooding threshold, the maximum timestep is assumed to be 100 * the waterdepth at the cell.
* if the waterdepth increases, the timestep is assumed to be not larger than the formula above.
If the numerical flux decreases, larger timesteps are allowed than set by Kurganov and Petrova<ref name="Kurganov1" />, depending on the {{inlink|Calculation_preference_formula|configured calculation}}.
====Calculation preference formula====
: ''Δt  = Δx /u<sub>max</sub>''
Where:
* Δt = computational timestep
* Δx = grid cell size
* u<sub>max</sub> = max velocity, assumed 2.5 (SPEED), 5 (AVERAGE) and 10 (ACCURACY) m/s respectively
====Surface water level formula====
: ''WL<sub>surface</sub> = W<sub>surface</sub> + H<sub>surface</sub>''
Where:
* WL<sub>surface</sub> = The water level, relative to {{datum}}.
* W<sub>surface</sub> = The amount of water (the water column) on the surface.
* H<sub>surface</sub> = The terrain height in the cell, relative to {{datum}}.
====Surface flow formula====
=====2D Saint Venant=====
[[File:Inundation_overlay_01.PNG|350px]]
* friction
* bed slope
* water pressure
* convection (changes in bathemetry over space)
* inertia (increase or decrease of velocity over time)
=====Numerical scheme for the 2D Saint Venant equations=====
[[File:Inundation overlay 04 HWP(1).PNG|thumb|250px|Source: Horváth et al. (2014)<ref name="Horvath"/>]]
[[File:Inundation overlay 04 HWP(2).PNG|thumb|250px|Source: Horváth et al. (2014)<ref name="Horvath"/>]]
The explicit second-order semi-discrete central-upwind scheme for the 2D Saint Venant Equations is implemented. A reconstruction of cell bottom, water level and velocity at the interfaces between computational cells as proposed by Lax and Wendroff (Rezzolla, 2011)<ref name="Rezolla"/>. The {{software}}'s [[water model]] relies on the scheme described in Kurganov and Petrova (2007)<ref name="Kurganov2"/>. The reconstruction method is taken from Bolderman et all (2014) and ensures numerical stability at the wetting and drying front of a flood wave<ref name="Bollerman" />.
A clear explanation on the numerical approach can be found at Horváth et al. (2014)<ref name="Horvath"/>, but in general it follows these steps:
# The elevation value of the cell (denoted as B in included figures) is equal to the elevation value at the center of the cell. At the same time, it is equal to the average value of the elevation values at the cell interface midpoints.
# The slopes of the conserved variables (denoted as U in included figures), continuity and momentum in x and y direction, are reconstructed.
# Values of conserved variables at the cell interface midpoints are compared with the left-sided and right sided values at cell centers.
# At partially dry cells, the slope is modified to both avoid negative depths and numerical instability.
# (Numerical) fluxes are computed at each cell interface to determine the values of the conserved variable at the cell centers for the next time-step.
{{clear}}
====Groundwater level formula====
: ''WH<sub>underground</sub> = W<sub>sat</sub> / WSP''
: ''WL<sub>underground</sub> = WH<sub>underground</sub> + H<sub>surface</sub> - GBDM''
Where:
* WL<sub>underground</sub> = The groundwater level, relative to {{datum}}.
* WH<sub>underground</sub> = The height (column) of the saturated zone.
* W<sub>sat</sub> = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
* GBDM = The {{inlink|GROUND_BOTTOM_DISTANCE_M}}(effectively available height in the underground model).
* WSP = The {{inlink|WATER_STORAGE_PERCENTAGE}} of the underground terrain type.
====Surface infiltration formula====
Infiltration capacities:
: ''C<sub>water</sub> = W<sub>surface</sub>''
: ''C<sub>top</sub>'' = max( I<sub>con</sub>, I<sub>surf</sub> )
:: I<sub>surf</sub> = 0 if a construction is present
:: I<sub>con</sub> = 0 if no construction is present
Actual infiltration:
: ''Δw =  min( C<sub>water</sub> , Δt * C<sub>top</sub>)''
Where:
* Δw = The surface infiltration which takes place.
* Δt = Computational timestep.
* C<sub>water</sub> = The amount of infiltration that can take place based on the amount of water on the surface.
* C<sub>top</sub> = The amount of evaporation that can take place based on the infiltration values present.
* I<sub>con</sub> = The {{inlink|GROUND_INFILTRATION_MD_constructions|GROUND_INFILTRATION_MD}} of a construction on a specific cell (if present).
* I<sub>surf</sub> = The {{inlink|GROUND_INFILTRATION_MD_surface|GROUND_INFILTRATION_MD}} of the surface terrain type. This value should be interpreted as the vertical conductivity (Kv) of the sub-soil.
====Underground infiltration formula====
: ''H<sub>unsat</sub> = H<sub>surface</sub> - WL<sub>underground</sub>''
: ''S = W<sub>unsat</sub>/H<sub>unsat</sub>''
: ''C<sub>inf</sub> = min( H<sub>unsat</sub> , Δt * I<sub>und</sub> )''
: ''Δw = C<sub>inf</sub> * S''
Where:
* Δw = The underground infiltration which takes place.
* H<sub>unsat</sub> = The height of the unsaturated zone.
* S = Ratio of water to height in the unsaturated zone.
* C<sub>inf</sub> = The height in the unsaturated zone which can be subject to infiltration to the saturated zone.
* W<sub>unset</sub> = The amount of water in the unsaturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
* I<sub>und</sub> = The {{inlink|GROUND_INFILTRATION_MD_underground|GROUND_INFILTRATION_MD}} of the underground terrain type.
====Underground flow formula====
====Culvert formula====
<!--Culvert flow is calculated based on the 2 end-point cells.-->
====Weir formula====
====Pump formula====
: ''Δw = min( W<sub>lower</sub> , Δt * PS )''
Where:
* Δw = The amount water water pumped from the lower to the higher endpoint.
* W<sub>lower</sub> = The water amount of water (the water column) at the lower end point.
* H<sub>lower</sub> = The terrain height at the lower end point, relative to {{datum}}.
* PS = The {{inlink|PUMP_SPEED}} of the pump.
====Overflow formula====
Overflow can take place when:
: ''H<sub>sewer</sub> + SO - H<sub>overflow</sub> &gt; 0''
Actual overflow:
: ''Δw = min( 0 , WH<sub>sewer</sub> * Σ<sub>sewer</sub> , Δt * SOS )''
* Δw = The amount of sewer overflow which takes place.
* Σ<sub>sewer</sub> = The surface area of the sewer.
* WH<sub>sewer</sub> = The water height sewer.
* H<sub>sewer</sub> = The average height of the terrain where the sewer is present, relative to {{datum}}.
* H<sub>overflow</sub> = The height of the terrain at the centerpoint of the sewer overflow, relative to {{datum}}.
* SO = The {{inlink|SEWER_OVERFLOW}} attribute of the sewer overflow.
* SOS = The {{inlink|SEWER_OVERFLOW_SPEED}} attribute of the sewer overflow.
====Inlet formula====
When calculating '''inlets''', first the capacities are calculated.
If a T<sub>lower</sub> is defined:
: ''C<sub>inthres</sub> = max( 0 , T<sub>lower</sub> - WL<sub>surface</sub> )''
If a I<sub>Q</sub> is defined:
: ''C<sub>speed</sub> = Δt * I<sub>Q</sub>''
If a C<sub>total</sub> is defined:
: ''C<sub>incap</sub> = C<sub>used</sub> - C<sub>total</sub>''
: ''Δw = max( 0 , C<sub>inthres</sub> , C<sub>speed</sub> , C<sub>incap</sub> ) / cell''
: If any of the terms are undefined, they are not included.
When calculating '''outlets''', first the capacities are calculated.
: ''C<sub>outthres</sub> = min( 0 , T<sub>upper</sub> - WL<sub>surface</sub> )''
: ''C<sub>outcap</sub> = -C<sub>total</sub> - C<sub>used</sub>''
: ''Δw = min( 0 , C<sub>outthres</sub> , C<sub>speed</sub> , C<sub>outcap</sub> ) / cell''
: ''C<sub>used</sub> (new) = C<sub>used</sub> (old) + (Δw * cell)''
Where:
* Δw = The amount of water flow which takes place.
* cell = Cell size.
* C<sub>speed</sub> = The amount of water inflow (or outflow when negative) possible based on the inlet's {{inlink|INLET_Q}} attribute.
* C<sub>incap</sub> = The amount of water inflow possible based on the total {{inlink|INLET_CAPACITY|capacity}} of the inlet.
* C<sub>outcap</sub> = The amount of water outflow possible based on the total {{inlink|INLET_CAPACITY|capacity}} of the outlet.
* C<sub>inthres</sub> = The amount of water inflow desired based on the inlet's {{inlink|LOWER_THRESHOLD}} attribute.
* C<sub>outthres</sub> = The amount of water outflow desired based on the outlet's {{inlink|UPPER_THRESHOLD}} attribute.
* WL<sub>surface</sub> The water level on the surface, relative to {{datum}}.
* C<sub>total</sub> = The {{inlink|INLET_CAPACITY}} attribute of the inlet.
* I<sub>Q</sub> = The {{inlink|INLET_Q}} attribute of the inlet.
* T<sub>lower</sub> = The {{inlink|LOWER_THRESHOLD}} attribute of the inlet.
* T<sub>upper</sub> = The {{inlink|UPPER_THRESHOLD}} attribute of the inlet.
====Surface evaporation formula====
: ''Δw = min( WL<sub>surface</sub> , Δt * E<sub>weather</sub> * E<sub>overlay</sub> )''
* Δw = The amount of evaporation which takes place.
* E<sub>weather</sub> = The {{inlink|Evaporation|evaporation rate}} of the weather.
* E<sub>overlay</sub> = The {{inlink|SURFACE_WATER_EVAPORATION_FACTOR}}.
====Underground evaporation formula====
Evaporation capacities:
: ''C<sub>sat</sub> = max( 0 , min( RD , GBDM ) - H<sub>unsat</sub> ) * WSP''
: ''C<sub>unsat</sub> = max( 0 , min( RD , H<sub>unsat</sub> ) ) * ( W<sub>unsat</sub> / H<sub>unsat</sub> )''
: ''Δw<sub>unsat</sub> = min( C<sub>unsat</sub> , Δt * E<sub>weather</sub> * E<sub>top</sub> )''
: ''Δw<sub>sat</sub> = min( C<sub>sat</sub> , (Δt * E<sub>weather</sub> * E<sub>top</sub>) - Δw<sub>unsat</sub> )''
: ''Δw = Δw<sub>unsat</sub> + Δw<sub>sat</sub>''
Where:
* Δw = The total amount of evaporation which takes place.
* Δw<sub>unsat</sub> = The amount of evaporation which takes place from the unsaturated zone.
* Δw<sub>sat</sub> = The amount of evaporation which takes place from the saturated zone.
* C<sub>sat</sub> = The amount of evaporation that can take place from the saturated zone.
* C<sub>unsat</sub> = The amount of evaporation that can take place from the unsaturated zone.
* H<sub>unsat</sub> = The height (column) of the unsaturated zone.
* W<sub>unsat</sub> = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
* RD = The {{inlink|ROOT_DEPTH_M_constructions|ROOT_DEPTH_M}} of the construction if present, the {{inlink|ROOT_DEPTH_M_surface|ROOT_DEPTH_M}} of the surface terrain otherwise.
* GBDM = The {{inlink|GROUND_BOTTOM_DISTANCE_M}} (effectively available height in the underground model).
* E<sub>top</sub> = The {{inlink|WATER_EVAPORATION_FACTOR_constructions|WATER_EVAPORATION_FACTOR}} of the construction if present, the {{inlink|WATER_EVAPORATION_FACTOR_surface|WATER_EVAPORATION_FACTOR}} of the surface terrain otherwise.
==Calculation time impact==
==General Tab==
[[File:General_tab.JPG|250px|right|The geberal tab of the Water Overlays.]]
===Calculation Preference===
* u<sub>max</sub> = max velocity, assumed 2.5 (SPEED), 5 (AVERAGE) and 10 (ACCURACY) m3/s respectively
===Grid cell size===
The {{software}} computes flow equations over a rectangular cartesian grid, the grid cell size can be set by clicking on Change Grid.
After the grid cell size is changed, the Overlay is immediately being recalculated.
Note: if you choose a smaller grid cell size, both the amount of time steps (see Calculation Preference) and amount of computational cells increase.
===Refresh Grid===
By Refreshing the grid, the Overlay is recalculated. This may take some time, depending on the grid cell size, the size of your project and the calcualtion preference.
Below some use cases when to use Refresh Grid:
* when you have changed a setting in the Configuration Wizard, but not clicked on the Finish button of the wizard.
* when you change the Result type or calculcation preference in the General tab
* when you change the legend in the Legend tab
* when you change the keys in the Keys tab
* when you change the attrbutes of the Overlay in the Attributes tab
===Export Grid File===
You can export the current result type as either a GeoTiff (binary file/bitmap image can be opened in a GIS or in an image viewer) or ASCII (text file, can also be opened in a GIS but is also readable in a text editor) file.
Also, it is possible to export the difference result type of the current and maquette situation.
===Save Overlay result===
===Show Water Balance===
The Water Balance panel shows the in- and outflow of water in m3. The Water Balance panel is also visible when clicking on the Debug info (see below).
The water balance is made up of the following components (depending on what is in the project):
* Land surface: amount of water on the land surface after simulation (m3)
* Water surface: amount of water stored on water cells after simulation (m3)
* Building storage: amount of water stored in building storage (m3)
* Sewer storage: amount of water stored in sewers after simulation (m3)
* Underground storage: amount of water stored in the sub-soil after simulation (m3)
* Evaporated: amount of water evaporated after simulation (m3)
* Outlet: amount of water extracted from the model during the simulation via outlets of water areas or sewer pumps (m3).
===Warnings===
===Debug Info===
* Rain: the amount of rainfall (mm) in the duration of the rainfall event (hours)
* Total Simulation: the simulation period (hours)
* Cells: The dimensions of the simulation: the amount of computational cells and the amount of time steps (cycles)
* Water areas:
* Weir flow: the amount of water flown over weirs during simulation (m3)
* Sewer overflow: the amount of water flown over sewer overflows during simulation (m3)
* GPU time: the computation time on GPU (seconds)
* Volume: total volume of the in- and outflow of water in the model.
==Keys tab==
==Variants==
A Water Module will be initialized by adding one of the following Overlays to a project. Each variant has a number of parameters tuned to best fit specific use-cases. This means that each of these overlays is based on the same theory and calculation method, however they are customized to conveniently provide insight in different aspects of the Water Module.
{| class="wikitable"
! Attribute
|[[File:Overlay_rainfall.png]]
! Unit
|[[Rainfall_(Overlay)|Rainfall Overlay]]
! Description
|provides insight into the water stress and impact caused by (excessive) rainfall
|Water Level
|m + datum
|initial water level, relative to datum, for all water cells in a water area
|Outlet
|m3/s
|water abstraction for all water cells in a water area
|Outlet level
|m + datum
|initial water level, relative to datum, for all water cells in an outlet area (breach for example)
|Outlet capacity
|[[File:Overlay_flooding.png]]
|m3
|[[Flooding_(Overlay)|Flooding Overlay]]
|maximum amount of water that can be used for the outlet
|provides insight into water stress and impact caused by breaches in levees or other sources causing excessive water inflow
|Sewer Storage
||[[File:Overlay_groundwater.png]]
|m
|[[Groundwater_(Overlay)|Groundwater Overlay]]
|available storage in sewers at the start of simulation in a sewer area
|provides insight into long-term processes of water flow both on the surface and underground
|Sewer Pump Speed
|m3/s
|sewer water abstraction for all cells in a sewer area
|Breach Floor
|{{mdatum}}
|Modified terrain height, to simulate a breach in a levee.
|Inundation level
|{{mdatum}}
|Initial water height, to simulate water present at the start of the simulation.
<!--==Input Data and Settings==
The calculations performed by the Water Overlay are influenced by many kinds of geographical information present in the project area. For any given location, [[terrain]], [[construction]]s and other features can influence either the initial state of the simulation or how water flows in a given area.
Furthermore, the Water Overlay features a number of overall settings which can be configured for the hydrological calculations and its results. These settings do not have a geographical or temporal element to them, and are fixed values relevant for the simulation as a whole.
! Attribute
! Unit
! Description
|Weir Height
|m + datum
|weir crest level
|Weir Output
|m3/s
|The amount of water that flows through a weir/culvert
|Weir Coefficient
|linear weir coefficient for accounting discharge & contraction losses
|Culvert Speed
|m3/s
|the discharge capacity of a culvert
|Pump Speed
|m3/s
|the capacity of a pump
|Sewer Overflow Height
|m + datum
|the height of a crest of a sewer overflow
|Sewer Overflow Speed
|m3/s
|the discharge capacity of a sewer overflow
|Chloride
|x/m2
|Amount* of chloride which is created per second, per m² of construction with this attribute.
|Nitrogen
|x/m2
|Amount* of nitrogen which is created per second, per m² of construction with this attribute.
|Phosphorus
|x/m2
|Amount* of phosphorus which is created per second, per m² of construction with this attribute.
<nowiki>*</nowiki> The unit of the substances is left incomplete, as the project creator is free to set their own unit for quantities of substances.
==Attributes tab==
;[[Hydrologic_features_(Water_Overlay)|Hydrological features]]
This tab shows the attributes of result types that can be adjusted. These attributes can also be adjusted in the configuration wizard in step 5 in the General tab. It is therefore generally not needed to change the attributes here. However, below an overview of the Overlay Attributes. <!--
:The water system can be enhanced with a number of hydrological features, which can be loaded in as [[area]]s. These hydrological features form special properties or modifications on the hydrological system. See [[Hydrologic_features_(Water_Overlay)|Hydological features]] for a list of supported features.
;[[Hydraulic structures (Water Overlay)|Hydraulic structures]]
:See [[Hydraulic structures (Water Overlay)|Hydraulic structures]] for the list of supported structures.
;[[Additional_hydrological_attributes_of_buildings_(Water Overlay)|Hydrological attributes of buildings]]
:Besides the [[building]]s which directly influence the hydrologic model as a [[Hydraulic structures (Water Overlay)|hydraulic structure]], each building may also have attributes which can contribute to the hydrological model in some way. These attributes are stored and used on a grid cell level. This is different from the hydraulic structure attributes, which are stored and used on an object level. For a full list, see [[Additional_hydrological_attributes_of_buildings_(Water Overlay)|Additional hydrological attributes of buildings]].
;[[Terrain_attributes_(Water_Overlay)| Hydrological attributes of terrain]]
:[[Terrain]]s in a project have a number of hydrological attributes which can influence the flow of water in a project. Because there is always both surface and underground terrain defined for the entirety of the project area, all cells are affected by all attributes of terrains, unless a building is present with overwriting values. For a full list, see [[Terrain_attributes_(Water_Overlay)| Terrain attributes for the water overlay]].
;[[Model_attributes_(Water_Overlay)|Model settings]]
:For a full list, see: [[Model_attributes_(Water_Overlay)|Water Model attributes]]
The water model calculation's rely on a number of calculation-wide parameters. These parameters are available as attributes of the water overlay and can be modified as such.
==Troubleshoot, warnings and recommendations==
When the Water Overlay is used and calculations take place, there are some problems or points of attention the calculation can run into. Where possible, the Water Overlay will show appropriate warnings when running into any issues.
See [[Warning_and_recommendations_(Water_Overlay)|Troubleshoot, warnings and recommendations]];
==Results==
! Attribute
With a Water Overlay, a user can generate multiple [[Results_(Water_Overlay)|results]] for a single water simulation. For further information about these outcomes, see also [[Results_(Water_Overlay)|results]] and [[Result type (Water Overlay)|result types]].
! Unit
! Description
|{{anchor|ALLOWED_WATER_INCREASE_M|ALLOWED_WATER_INCREASE_M}}
|m
|The amount by which the water level on a water terrain must increase before it is considered stressed by water. This is used to compute the {{inlink|WATER_STRESS}} result type.
|{{anchor|DESIGN_FLOOD_ELEVATION_M|DESIGN_FLOOD_ELEVATION_M}}
|m
|Constructions in the 3D world are assumed to have at most this height compared to the surface of the terrain. Greater values can create a more accurate model but will impact performance.
|{{anchor|GROUND_BOTTOM_DISTANCE_M|GROUND_BOTTOM_DISTANCE_M}}
|m
|Assumed distance under the terrain surface where the soil becomes impenetrable for water. The groundwater level cannot go below this depth, relative to the surface. The maximum amount of water that can be stored underground is equal to this attribute multiplied by the local terrain's {{inlink|WATER_STORAGE_PERCENTAGE}}.
|{{anchor|GROUND_WATER|GROUND_WATER}}
|boolean
|Whether underground water flow is simulated during the calculation. If this is deactivated, {{inlink|Surface infiltration model|surface infiltration}}, {{inlink|Underground infiltration model|underground infiltration}}, and {{inlink|Evaporation model|underground evaporation}} do not occur. Water flowing {{inlink|Sewer model|in- and out of the sewer}} are still simulated when sewers are present.
|{{anchor|IMPACT_FLOOD_THRESHOLD_M|IMPACT_FLOOD_THRESHOLD_M}}
|m
|The amount of water a construction must experience before it is considered impacted by water. Water must reach this height either on one of the cells the construction is on, or on one of the cells adjacent to it. This is used to compute the {{inlink|IMPACTED BUILDINGS}} result type.
|{{anchor|MAX_SPEED_MS|MAX_SPEED_MS}}
|m/s
|Maximum speed at which water is allowed to flow. This effects the preservation of impulse in water, and as a result the length of {{inlink|Computational timestep calculation|computational timesteps}}. Impulse is more accurately preserved as the maximum speed increases, but will reduce the time per step of the calculation, increasing the total time for the calculation to complete.
|{{anchor|MIN_SLOPE|MIN_SLOPE}}
|ratio
|The minimum slope required to account for the effect of gravity on the speed of the water. If the slope of the terrain is less than the minimum slope, the effect of gravity on the speed of the water is assumed to be 0. The ratio is the height over distance.
|{{anchor|SEWER_OVERFLOW_THRESHOLD|SEWER_OVERFLOW_THRESHOLD}}
|fraction
|How much of a sewer's storage must be filled with water before the {{inlink|Sewer overflow|sewer's overflows}} are allowed to overflow water.
|{{anchor|SHOW_DURATION_FLOOD_LEVEL_M|SHOW_DURATION_FLOOD_LEVEL_M}}
|m
|The amount of water which must be present in a specific location before the duration of surface water can be recorded. This is used to compute the {{inlink|SURFACE_DURATION}} result type.
|{{anchor|SUPERGRID|SUPERGRID}}
|This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated.
|{{anchor|SURFACE_WATER_EVAPORATION_FACTOR|SURFACE_WATER_EVAPORATION_FACTOR}}
|factor
|The factor by which the {{inlink|weather}}'s evaporation factor is multiplied to compute the amount of {{inlink|Evaporation model|evaporation}} which takes place on the surface.
|{{anchor|TIMEFRAMES|TIMEFRAMES}}
|amount
|The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed.
==References==
==How-to's==
<references>
<ref name="Kurganov1">Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivy Preserving Central-Upwind Scheme for the Saint-Venant System ∙ p 15 ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)</ref>
* [[How to manually configure a Water Overlay|Configure a Water Overlay]]
* [[How to add Subsidence (Water Overlay)|Combine with Subsidence Overlay]]
* [[Water Model Limits]] (some basic rules)
<ref name="Horvath">Zsolt Horváth, Jürgen Waser, Rui A. P. Perdigão, Artem Konev and Günter Blöschl (2014) ∙ A two-dimensional numerical scheme of dry/wet fronts for the Saint-Venant system of shallow water equations ∙ found at: http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.700.7977&rep=rep1&type=pdf ∙ http://visdom.at/media/pdf/publications/Poster.pdf ∙ (last visited 2018-06-29)</ref>
===Features and components===
* [[Hydrological features (Water Overlay)|Hydrological features]]
* [[Hydraulic structures (Water Overlay)|Hydraulic structures]]
* [[How to_manually_configure_a_Water_Overlay|Manual configuration Options]]
* [[Simulation data (Water Overlay)|Simulation data]]
<ref name="Rezolla">Rezzolla  L (2011) ∙ Numerical Methods for the Solution of Partial Differential Equations ∙ found at: http://www.scirp.org/(S(lz5mqp453edsnp55rrgjct55))/reference/ReferencesPapers.aspx?ReferenceID=1886006 (last visited 2018-06-29)</ref>
===Attributes===
* [[Model attributes (Water Overlay)|Water Module Attributes]]
* [[Hydrological attributes of buildings (Water Overlay)|Hydrological Attributes of Buildings]]
* [[Hydrological attributes of terrains (Water Overlay)|Hydrological Attributes of Terrains]]
<ref name="Kurganov2">Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivy Preserving Central-Upwind Scheme for the Saint-Venant System ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)</ref>
{{WaterOverlay output nav}}
{{Overlay nav}}
<ref name="Bollerman">Bollermann A, Chen G, Kurganov A and Noelle S (2014) ∙ A Well-Balanced Reconstruction For Wetting/Drying Fronts ∙ found at: https://www.researchgate.net/publication/269417532_A_Well-balanced_Reconstruction_for_Wetting_Drying_Fronts (last visited 2018-06-29)</ref>
[[Category:Water Module]][[Category:Overlays with result types]]
</references>
Latest revision as of 13:40, 17 January 2023
Variants
Results
With a Water Overlay, a user can generate multiple results for a single water simulation. For further information about these outcomes, see also results and result types.