Line 1,214: Line 1,214:
====Culvert formula====
* [[Culvert_formula_(Water_Overlay)|Culvert formula]]
Flow through culverts is based on an open channel flow calculation.
: ''CH<sub>real</sub> = max( CH<sub>attr</sub> , T<sub>left</sub> , T<sub>right</sub> )''
The height of the water column at either end of the culvert, relative to the culvert, is calculated:
: ''WH<sub>left</sub> = max(0, WL<sub>left</sub>-CH<sub>real</sub>)''
: ''WH<sub>right</sub> = max(0, WL<sub>right</sub>-CH<sub>real</sub>)''
The loss coefficient for the culvert is calculated:
: U = sqrt( 1.0 / ( 1.0 + 2.0 * G * CN * CN * length /  (Rh ^ (4 / 3 ) ) )
The potential flow through the culvert is then calculated:
: ''C = U * A * sqrt( 2 * G * abs(WH<sub>left</sub> - WH<sub>right</sub>) )''
: ''Δw = ''Δt * C / cell''
Where:
* Δw = The water flow which takes place.
* Δt = Computational timestep.
* cell = Cell size.
* C = The potential rate of water flow through the culvert.
* U = Loss coefficient for  culverts.
* WH<sub>left</sub> = The height of the water column relative to the bottom of the culvert on the left side of the culvert.
* WH<sub>right</sub> = The height of the water column relative to the bottom of the culvert on the right side of the culvert.
* CH<sub>real</sub> = The {{inlink|CULVERT_THRESHOLD}} of the culvert, recalculated so the culvert is not below ground on either side.
* A = Flow area, based on the height of the water in the (circular) culvert.
* G = Acceleration factor of gravity
* CW = The {{inlink|CULVERT_DIAMETER}} attribute of the culvert. <!--Unused-->
* CH<sub>attr</sub> = The {{inlink|CULVERT_THRESHOLD}} attribute of the culvert.
* CN = The {{inlink|CULVERT_N}} attribute of the culvert.
* WL<sub>left</sub> = The water level on the left side of the culvert, relative to {{datum}}.
* WL<sub>right</sub> = The water level on the right side of the culvert, relative to {{datum}}.
* L = The length of the culvert, calculated as the distance between the culvert's endpoints.
* Rh = The hydrological radius in the culvert<ref name="hydradius" />.
====Weir formula====
Revision as of 13:12, 2 April 2019
What is the Water overlay
Water flow is affected by properties of the surface across which it flows, including the terrain height and the properties of the underlying terrain.
Variants
Use cases
This section is a stub.
How to use the Water overlay
Prerequisites
Configuration
Configuration wizard
Template:Editor ribbon
Step 1: Weather
Step 2: Water system
The water system is the most complex step of the configuration and contains a multitude of substeps to configure all geographical data. Its various components can be configured in the following order:
Breach (flooding overlays only): A breach, a location where an (uncontrolled) inflow of water takes places.
Water areas: Water level areas, defined regions in which a specific water level is maintained. It is also possible to have the wizard generate a single water level area for the entire project area.
Sewers: Sewer areas, the broad definitions for where what kind of sewers exist. It is also possible to have the wizard generate sewer areas based on the neighborhoods in the project area.
Inundation areas: Inundation areas, definitions of water on the surface, in the form of inundated land. It is also possible to have the wizard generate a single inundation area covering the entire project area.
Aquifer areas (groundwater overlays only): Aquifer areas, definitions for transmissivity or hydraulic conductivity of the underground layer.
Weirs: Weirs, minor barriers in the water flow.
Culverts: Culverts, tunnels which form direct connections between two locations.
Pumps: Pumps, structures which move water from a lower to a higher location.
Inlets: Inlets, structures which add or remove water.
Sewer overflows: Sewer overflows, points where water from sewers can flow back onto the surface.
All of the above components can be imported or connected to the hydrological model.
Step 4: Interaction
Step 5: Output overlays
Multiple result types are available. In the wizard multiple result types can be selected. One result type (indicated with the "First" checkbox) will be the main overlay's result type. The other selections will become result child overlays. Relevant attributes can be modified as well, if they are related to selected result types.
Step 6: Input overlays
To gain more insight into the data used by the model, you may opt to add one or more input overlays as well. These add Average Overlays configured for the geographical display of attribute values relevant for the calculation of the water model.
Manual configuration
Besides using the configuration wizard, it is also possible to configure a number of settings manually. A few settings can only be changed manually. Besides the data of geographical features, which have their own means of loading in depending on their type, all manual configuration options are listed here.
Grid cell size configuration
Main article: Grid overlay
Main section: Weather
Template:Editor ribbon The weather configuration, which dictates the duration of the simulation, the amount of rain and the evaporation rate, is modeled as a separate weather object which is connected to the water overlay. The weather object can be replaced with another, changing the main simulation and weather properties. The weather itself can be changed as well.
Ground water configuration
Main section: Ground water
Subsidence configuration
Main section: Subsidence
Active in simulation setting
Result type configuration
Main section: Result type
Note that via the configuration wizard multiple result types can be added in parallel in the form of result child overlays.
Legend configuration
Keys configuration
Main section: Keys
Attributes configuration
Main section: Attributes
Template:Editor ribbon The water model's calculations make use of a number of centralized parameters, which are configured as attributes of the overlay. Depending on the exact variants of the water overlay, some of the parameters will have different defaults to better suit the exact type of calculation. The parameters can be tweaked further to better fit specific use-cases, but in general the defaults are appropriate for most calculations.
Results
When the calculation completes, the results are stored as numerical values in a grid spanning the entire 3D world. The exact values and their meanings depend on the selected result type. Each timeframe and each result child overlays has it's own grid of data. There are multiple ways to interact with this data. In addition, there are a few additional outputs provided by the water overlay specifically to gain further insight, verification, and visualization of the results.
Geographical overview
Visualization
Depending on whether the option is selected, the hydrological system can be visualized when when the overlay is activated. Each water level area will be visualized by a blue floating sphere and a striped border along the surface of the terrain. Sewer areas are visualized by an orange floating sphere. If the sewer has a sewer overflow, the overflow is connected to the sewer's sphere via an orange line. Culverts, weirs, and pumps are visualized by green, orange, and red spheres respectively for their endpoints, connected by blue lines.
Hover panel
Detailed results
Timeframes
Note that the simulation time is divided into a TIMEFRAMES amount of periods, and at the end of each period a timeframe is recorded. This means the first timeframe is not a snapshot of the initial state of the simulation, but a snapshow of the state of the simulation after the first period of time has passed already.
TQL
Main article: TQL
Measuring tool
Main article: Measuring tool
While viewing the overlay, a general impression of the values can be seen at a glance. However, depending on the configuration of the overlay's legend the exact values may be difficult to view exactly. Using the measuring tool it's possible to retrieve the values of the overlay on exact locations. Additionally, cross-sections can be defined and easily have their values inspected.
Exporting Geotiff
Additional forms of output
A number of output forms don't fit in the analysis structure described above, but can provide additional information or insight into the calculation. These can provide different ways of looking at both the input and output of the simulation. They are offered as a means to further visualize but also verify the performed calculations.
Weather visualization
Saving overlay result
Water balance
Input Output
  • Breach
  • Inlet
  • Rain
  • Water surface
  • Inundated land
  • Breach out
  • Outlet
  • Land surface
  • Water surface
  • Building surface
  • Sewer storage
  • Evaporated
Debug info
Debug information as generated by a calculation of the Water Overlay.
After the calculation completes, some additional information is tallied and output for debugging purposes. This is intended for verification that the model has computed as expected, and may provide some basic information at a glance. It is not meant as a primary tool for in-depth analysis of the results.
The following information is displayed:
Debug info
  • Total rainfall
  • Simulation time (and amount of timeframes)
  • Map size
  • Amount of cells and amount of computational timesteps
  • Amount of special hydrological areas
  • Amount of flow over weirs
  • Amount of overflow from sewers
  • Total calculation time, and the amount of GPU's used to perform the calculation
  • Total volume of water processed
Input overlay
Main article: Average Overlay
The water overlay's calculations rely on multiple geographical parameters, such as manning values and evaporation factors. To help with both understanding the outcome of the calculation as well as verifying the results, the configuration wizard offers the option to add input overlays to the project, which are Average Overlays configured to display the input parameters geographically.
Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired attribute, and with an as small an averaging distance as possible. Optionally, a specific layer (such as constructions or terrains) can be configured which the overlay should inspect.
Model connections
The hydrological model can be linked to other models, which adds and defines more data for the simulation. Some models are automatically connected, and are required for the calculations to take place. Others are optional, and can apply additional detail to the calculations. When the optional models are absent, default behavior is defined.
Terrain height
Main article: Terrain height
Template:GeoTIFFSpec
Weather
Rain and simulation time
Linear configuration
Property Unit Description
Custom configuration
Rain should never be negative
First entry Second entry
Time (s) Rain (m)
Evaporation rate
Evaporation CSV specification
Time (s) Evaporation (m)
Ground water
Subsidence
Data
The calculations performed by the water overlay are influenced by many kinds of geographical information present in the project area. For any given location, terrain, constructions and other features can influence either the initial state of the simulation or how water flows in a given area.
Water level area
Sewer area
Breach
The breach can grow over time, based on its initial width and the critical speed at which water may flow. If a BREACH_WIDTH is defined, the breach's polygon is intersected with a circle emanating from the centerpoint of the polygon. It is only in that intersection, dubbed the "active breach", that water will flow in from the simulated external water body.. The radius of the circle defining the intersection will expand when the water flowing in from the external water body exceeds the BREACH_SPEED. Water flowing in the hydrological model across the breach's surface without explicitly entering or leaving the hydrological model through the breach and its simulated water body does not "count" for the critical speed. All cells in the active breach are considered directly adjacent to the external water body.
The entire breach area is considered lowered to the height defined by its BREACH_HEIGHT attribute, even if the active breach does not extend across the entirety of the breach area.
Water flowing through or across a breach will flow in the direction defined by the BREACH_ANGLE attribute, regardless of whether the water flowed onto the breach from elsewhere in the water model, or from the simulated external water body. If no BREACH_ANGLE is defined, water can flow in any direction.
BREACH_ANGLE geo angle (0-360°) The angle at which water can flow from the breach. n/a
Inundation
Aquifer
The aquifer is an additional definition for the underground, allowing for underground horizontal flow different from the underground terrain's GROUND_INFILTRATION_MD.
AQUIFER_KD m²/day The hydraulic conductivity of the aquifer, which dictates the speed at which water can flow horizontally through the underground. n/a
AQUIFER_HEIGHT m n/a
Note that the aquifer only functions if its hydraulic conductivity is greater than 0. If it is 0 or less the aquifer is disregarded, and the GROUND_INFILTRATION_MD of the underground terrain is used.
Hydrological constructions
In general, hydrological constructions are loaded in as underground constructions.
  • Line-based constructions
  • Point-based constructions
Culvert
Culverts are assumed to have a spherical cross-section.
A culvert is a line-based constructions.
CULVERT_DIAMETER m The diameter of the culvert. For throughput calculations, the culvert is assumed to have a spherical cross-section. 1
CULVERT_THRESHOLD m + datum The height of the culvert. (When set to a level lower than the terrain for either endpoint of it, the culvert's height is equal to the height of the (highest) terrain under either endpoint.) 0
Weir
A weir is a line-based constructions.
WEIR_COEFFICIENT coefficient The flow coefficient related to the shape of the weir. 1,1
Pump
A pump is a line-based constructions.
Sewer overflow
A sewer overflow is a point-based constructions. It must intersect with a sewer area, but does not need to intersect with an actual sewer.
SEWER_OVERFLOW m + datum The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water height in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out. n/a
Inlet
An inlet is a point-based constructions.
INLET_Q m3/sec The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model. Infinite
Sewered constructions
Water storage constructions
Porous constructions
Crops and foliage
Constructions representing crops and foliage can draw water from the underground, allowing it to evaporate. This behaves in the same way as terrain which is configured as plants.
Critical structures
Chemical emitters/decomposers
Chemicals have generic definitions, in terms of name and magnitude, to allow for the modeling of arbitrary substances.
Structures which are defined to create a negative amount of chemicals function as a scrubber or decomposer, removing the specified quantity of chemicals from the hydrological model.
SUBSTANCE_A x/m² The amount of substance A created per second per m² in this location. 0
SUBSTANCE_B x/m² The amount of substance B created per second per m² in this location. 0
SUBSTANCE_C x/m² The amount of substance C created per second per m² in this location. 0
SUBSTANCE_D x/m² The amount of substance d created per second per m² in this location. 0
Manning value (construction)
Constructions have an inherent "roughness", which influences how fast water can flow across the surface. This is known as the Manning coefficient or Manning value.
WATER_MANNING s/(m1/3) Surface The Gauckler–Manning coefficient of the construction.
Note that if no construction is present in any location, the WATER_MANNING value of the surface terrain present is used instead.
Construction height
Though not an explicit attribute or function value in and of itself, the height of constructions is taken into account when computing the flow of water above ground. Constructions are computed to have at most a height of DESIGN_FLOOD_ELEVATION_M. Lower constructions retain their own construction height. Taller constructions have their height capped at the attribute's value.
Terrains in a project have a number of hydrological properties which can influence the flow of water in a project. Because there is always both surface and underground terrain defined for the entirety of the project area, all cells are affected by all properties of terrains, unless a construction is present with overwriting values.
Water
Water terrains are processed by the water model in a specific manner before the simulation is started. For each water terrain in the 3D world, the bottom of the water body is treated as a land surface in the same fashion as dry land. Water is then placed on it on the surface layer, up to the level defined by the overlapping water level area's WATER_LEVEL attribute. Terrains not marked as water terrain are not initiated with water.
Plants
Terrains can be configured with plant-related attributes, similar to crops and foliage constructions, allowing it to draw water from the underground and evaporate it.
Also note that the groundwater level reduction is inversely proportional to the WATER_STORAGE_PERCENTAGE, as the contribution of a given volume of water to the groundwater level increases when the capacity for water storage in the underground layer decreases.
Infiltration and storage
Underground flow, or horizontal infiltration, are dependent on the infiltration properties of the underground, unless an aquifer exists the same location.
WATER_STORAGE_PERCENTAGE fraction Underground The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer.
Manning value (terrain)
Terrains have an inherent "roughness", which influences how fast water can flow across the surface. This is known as the Manning coefficient or Manning value.
WATER_MANNING s/(m1/3) Surface The Gauckler–Manning coefficient of the terrain.
Note that if a construction is present in the same location, that construction's WATER_MANNING value is used instead.
Settings
The water overlay features a number of overall settings which can be configured for the hydrological calculations and its results. These settings do not have a geographical or temporal element to them, and are fixed values relevant for the complete simulation.
Result type
1: Water area
2: Land
3: Sewer
4: Water object
5: Breach Area
6: Active Breach
DEBUG_UV
DEBUG_WALLS
GPU_OVERVIEW nominal integer Maximum Shows which GPU cluster calculated which part of the overlay.
GROUND_LAST_STORAGE m (mm)¹ Last The (effective) amount of water in the underground unsaturated zone.
GROUND_LAST_VALUE m (mm)¹ Last The distance between the surface and the groundwater level.
GROUND_MAX_STORAGE m (mm)¹ Maximum The (effective) amount of water in the underground unsaturated zone.
GROUND_MAX_VALUE m (mm)¹ Maximum The distance between the surface and the groundwater level.
GROUND WATERTABLE m + datum Last The groundwater level, relative to datum.
IMPACTED_BUILDINGS nominal integer Maximum Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_THRESHOLD_M.
1...N: The (critical) construction is impacted, and has a critical function values set to this value.
SUBSTANCE_A x/m² Last The amount of substance A present. The value is the sum of the quantities on the surface, and in the underground.
SUBSTANCE_B x/m² Last The amount of substance B present. The value is the sum of the quantities on the surface, and in the underground.
SUBSTANCE_C x/m² Last The amount of substance C present. The value is the sum of the quantities on the surface, and in the underground.
SUBSTANCE_D x/m² Last The amount of substance D present. The value is the sum of the quantities on the surface, and in the underground.
SURFACE_DIRECTION geo angle (0-360°) Last The direction in which water is flowing across the surface.
SURFACE_ELEVATION m + datum Start The rasterized version of the terrain height for use in the water overlay's calculations.
SURFACE_FLOW m³/m² Last The amount of water which has flowed through a given location.
SURFACE_LAST SPEED m/s Last The (horizontal) speed of water flow in any given location.
SURFACE_MAX SPEED m/s Maximum The (horizontal) speed of water flow in any given location.
WATER_STRESS m (mm)¹ Maximum The amount of water on the surface, similar to SURFACE_MAX_VALUE. However, for water terrains, the water level must rise by at least ALLOWED_WATER_INCREASE_M. Otherwise, the reported value in those locations is 0.
Result child overlays
If a calculation overlay is removed, all result child overlays which are children of that overlay are removed as well. Separate overlays set as child overlays (such as input overlay) of the overlay will not be removed.
It is only possible to add result child overlays via the configuration wizard, in the output overlays step.
Keys
The water model makes use of data present in geographical features in the 3D world. This data is used as input for the various calculations which together model the water flow. The water model recognizes what attributes of geographical features form the parameters required for the calculation through key definitions. Each key is the name of an attribute which the water model should use to determine a specific parameter.
Keys are set to default attribute names, which apply to hydrological features, hydrological constructions, and hydrological properties of terrain. Keys can be changed so that imported data can be interpreted without renaming attributes, or to allow different configurations to come forth from the same dataset.
The water model calculations rely on a number of calculation-wide parameters. These parameters are available as attributes of the water overlay and can be modified as such.
GRAVITY m/s² Used constant for gravitational acceleration
LIMIT_RAIN boolean Whether rainfall locations should be limited to water level areas (1) or everywhere (0).
MAX_WATER_DEPTH_M m
QUAD_CELL boolean This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated.
TIMEFRAMES integer The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed.
WALL_ANGLE
Calculations
The water overlay performs a large number of calculations to form a complete hydrological simulation. Depending on the desired viewpoint, both the overarching concepts as well as the implemented formulas can be reviewed for detailed insight into how the water overlay works.
Models
The precise calculations which govern the water overlay's simulation are many and varied, and based as much as possible on available expert knowledge.
Model related Formula's:
Hydraulic structure related Formula's:
Weir formula
Flow across weirs is calculated differently for free flow and submerged flow.
The height of the water at each end of the weir, relative to the weir, is calculated:
WHsource = max(0, max( WLleft, WLright ) - WHweir)
WHdest = max(0, min( WLleft, WLright ) - WHweir)
For free flow, capacity is calculated directly:
Cfree = DWF * WC * WW * ( WHsource - WHdest )3/2
For submerged flow, a culvert-like calculation is used:
Csubmerged = U * A * sqrt( 2 * G * (WHsource - WHdest) )
WHrelative = WHdest : WHsource
C = min( Csubmerged , Cfree) if WHrelative > 0,5
C = Cfree otherwise
Δw = Δt * C / cell
Where:
  • cell = Cell size.
  • C = The potential rate of water flow across the weir.
  • WHrelative = The ratio of water heights on either side of the culvert.
  • Cfree = The potential rate of water flow across the weir, based on a free flow calculation.
  • Csubmerged = The potential rate of water flow across the weir, based on a submerged calculation.
  • WHsource = The height of the water column relative to the top of the weir, on the side with the highest water level.
  • WHdest = The height of the water column relative to the top of the weir, on the side with the lowest water level.
  • U = Loss coefficient for submerged weirs (0,9).
  • A = Flow area, based on the highest water column height relative to the top of the weir, and the weir width, defined by the WEIR_WIDTH attribute of the weir
  • DWF = Dutch weir factor, set to 1.7
  • WC = The WEIR_COEFFICIENT attribute of the weir.
  • WHweir = The WEIR_HEIGHT attribute of the weir.
  • WLleft = The water level on the left side of the weir, relative to datum.
  • WLright = The water level on the right side of the weir, relative to datum.
Breach growth formula
Breaches can grow when water flows from the virtual external water source into the hydrological model[1].
First, the difference in height of the water on either side of the breach is calculated.
H = abs( max(0, EL - BH) - max(0, WL - BH) )
Using the height difference, the breach width increase is calculated.
ΔB = 1.3 * ((G^0.5 * H^1.5) / Uc) * log10 (1 + (0.04 * G / Uc) * Δt / 3600)
The current breach width is then equal to the last calculated breach width, plus the calculated additional breach width.
Bnew = Bold + ΔB
Where:
  • B = The total calculated breach width, initially equal to BW.
  • ΔB = The calculated width increase of the breach.
  • H = The difference between the height of the water columns on either side of the breach.
  • MF = Material factor, set to 1.3 (average for sand and clay levees)
  • BH = The BREACH_HEIGHT attribute of the breach.
  • BW = The BREACH_WIDTH attribute of the breach.
  • BS = The BREACH_SPEED attribute of the breach.
  • EL = Current external water level.
Breach flow formula
Main section: Weir formula
Flow through breaches is calculated based on the weir formula, including the consideration between free flow and submerged flow situations. However, the following also applies.
For the virtual side of the breach, the water level used is defined by the external water level of the breach. The terrain height used for the virtual side of the breach is equal to the external surface level, limiting how far the external water level can be lowered.
Each timestep, the external water level is changed based on the amount of water flowing in or out.
ELnew = ELold - ( (Δw * cell) / EA )
Where:
  • Δw = The water flow which takes place (out of the virtual external water source)
  • cell = Cell size
Pump formula
Δw = min( WHlower , Δt * PS )
Where:
  • WHlower = The height of the water column at the lower end of the pump, relative to the terrain.
Overflow formula
The amount that can overflow relies on both the sewer overflow itself as well as the sewer overflow threshold:
Cthreshold = max( 0 , WHsewer - SS * SOT )
Cheight = max( 0, Tsewer + SO + WHsewer - Toverflow )
C = min ( Cthreshold, Cheight )
Actual overflow is then calculated:
Δw = min( 0 , C * Σsewer , Δt * SOS )
  • C = The amount of water that can overflow out of the sewer
  • Cthreshold = The amount of water that could overflow, based on the sewer overflow threshold.
  • Cheight = The amount of water that could overflow, based on the properties of the sewer overflow.
  • WHsewer = The height of the water column in the sewer.
  • Tsewer = The average height of the terrain where the sewer is present, relative to datum.
  • Toverflow = The height of the terrain at the centerpoint of the sewer overflow, relative to datum.
  • SS = The SEWER_STORAGE attribute of the sewer area.
  • SOT = The SEWER_OVERFLOW_THRESHOLD.
Inlet formula
If a Tlower is defined:
If a IQ is defined:
Cspeed = Δt * IQ
If a Ctotal is defined:
Cincap = Cused - Ctotal
If a IQ is defined:
Cspeed = Δt * IQ
Coutcap = -Ctotal - Cused
Where:
  • cell = Cell size.
Surface evaporation formula
Evaporation capacities:
Δw = Δwunsat + Δwsat
Where:
Computational structure
This section is a stub.
The formulas and concepts come together in a single computational structure which is repeated a large number of times until the total simulation duration has been reached.
Order of operations
During the calculation, multiple facets have to be calculated. In each timestep, each aspect of the calculation has to be performed. Although as timesteps become smaller exact order of operation becomes less important, the order of operations can lead to specific behavioral details in some edge cases.
  • Rain
  • Building storage
  • Sewer inflow
  • Surface evaporation
  • Underground infiltration
  • Surface infiltration
  • Exfiltration
  • Hydrological constructions (culverts, weirs, pumps, in- and outlets, outlets)
  • Hydrological areas (sewer overflow, breach in- and outflow)
  • Chemical movement, based on the water flow and infiltration which has occurred
Calculation time impacts
Warnings
When the water overlay is used and calculations take place, there are some problems or points of attention the calculation can run into. Where possible, the water overlay will show appropriate warnings when running into any issues.
Configuration wizard warnings
While configuring the water overlay using the configuration wizard, each type of data loaded in or found in the project must meet certain requirements to be functional. For example, configured water levels may deviate greatly from the mean terrain height in the project, or certain hydrological constructions may not be shaped appropriately or intersect with required features. In these cases, the configuration wizard will show the warnings in the steps related to the specific type of data.
Inaccurate terrain
When the project is created, the advanced options allow for selecting a high-resolution height map to be loaded in. The default, low resolution height map can introduce artifacts in the calculation due to inaccuracy. This issue can currently only be resolved by reloading the project area.
Calculation halted
If the overlay is recalculated, but the (re)calculation is halted, the water overlay will not contain meaningful results. A warning will be displayed indicating that the calculation did not complete.
Large cell size
The water overlay performs its calculations based on a discretization of the project area. This means both that areas of water are considered a single block, and that obstacles and hydrological properties are averaged out over the extent of a cell. To best approach a realistic, continuous water flow and a realistic model of obstacles and values, it is sufficient to reduce the size of the cells the calculation uses.
Limited cycles
  1. Verheij, H.J. ∙ Aanpassen van het bresgroeimodel in HIS-OM: Bureaustudie ∙ found at: http://resolver.tudelft.nl/uuid:aedc8109-da43-4a03-90c3-44f706037774 ∙ (last visited 2019-03-08)
Cite error: <ref> tag with name "hydradius" defined in <references> is not used in prior text.