Line 645: Line 645:
! Default
! Default
|{{anchor|INLET_Q_constructions|INLET_Q}}
|{{anchor|INLET_Q|INLET_Q}}
|m3/sec
|m3/sec
|The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model.
|n/a
|n/a
|{{anchor|INLET_CAPACITY_constructions|INLET_CAPACITY}}
|{{anchor|INLET_CAPACITY|INLET_CAPACITY}}
|m3
|m3
|The maximum amount of water which can flow in or out through this construction. Water flowing back in the other direction replenishes the capacity.
|Infinite
|Infinite
|{{anchor|LOWER_THRESHOLD_constructions|LOWER_THRESHOLD}}
|{{anchor|LOWER_THRESHOLD|LOWER_THRESHOLD}}
|{{mdatum}}
|{{mdatum}}
|If a lower threshold is set, water will only flow into the model through this inlet until the water level at the point of this inlet is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion.
|None
|None
|{{anchor|UPPER_THRESHOLD_constructions|UPPER_THRESHOLD}}
|{{anchor|UPPER_THRESHOLD|UPPER_THRESHOLD}}
|{{mdatum}}
|{{mdatum}}
|If an upper threshold is set, water will only flow out the model through this outlet until the water level at the point of this inlet is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion.
Line 667: Line 667:
Also note that an inlet shares attribute names with the {{inlink|Breach|breach}}es, and that changing the attribute keys for inlets also affects the keys for breaches.
Also note that an inlet shares attribute names with the {{inlink|lcase=1|Breach}}es, and that changing the attribute keys for inlets also affects the keys for breaches.
===Miscellaneous hydrological properties of constructions===
Revision as of 10:35, 18 February 2019
What is the Water overlay
Water flow is affected by properties of the surface across which it flows, including the terrain height and the properties of the underlying terrain.
Variants
Use cases
This section is a stub.
How to use the Water overlay
Prerequisites
Configuration
Configuration wizard
Template:Editor ribbon
Step 1: Weather
Step 2: Water system
Sewers: Sewer areas, the broad definitions for where what kind of sewers exist, can be imported or connected to the hydrological model. It is also possible to have the wizard generate sewer areas based on the neighborhoods in the project area.
Step 4: Interaction
Step 5: Output overlays
Multiple result types are available. In the wizard multiple result types can be selected. One result type (indicated with the "First" checkbox) will be the main overlay's result type. The other selections will become result child overlays. Relevant attributes can be modified as well, if they are related to selected result types.
Step 6: Input overlays
To gain more insight into the data used by the model, you may opt to add one or more input overlays as well. These add Average Overlays configured for the geographical display of attribute values relevant for the calculation of the water model.
Manual configuration
Besides using the configuration wizard, it is also possible to configure a number of settings manually. A few settings can only be changed manually. Besides the data of geographical features, which have their own means of loading in depending on their type, all manual configuration options are listed here.
Grid cell size configuration
Main article: Grid overlay
Main section: Weather
Template:Editor ribbon The weather configuration, which dictates the duration of the simulation, the amount of rain and the evaporation rate, is modeled as a separate weather object which is connected to the water overlay. The weather object can be replaced with another, changing the main simulation and weather properties. The weather itself can be changed as well.
Ground water configuration
Main section: Ground water
Subsidence configuration
Main section: Subsidence
Active in simulation setting
Result type configuration
Main section: Result type
Note that via the configuration wizard multiple result types can be added in parallel in the form of result child overlays.
Legend configuration
Keys configuration
Main section: Keys
Attributes configuration
Main section: Attributes
Template:Editor ribbon The water model's calculations make use of a number of centralized parameters, which are configured as attributes of the overlay. Depending on the exact variants of the water overlay, some of the parameters will have different defaults to better suit the exact type of calculation. The parameters can be tweaked further to better fit specific use-cases, but in general the defaults are appropriate for most calculations.
Results
When the calculation completes, the results are stored as numerical values in a grid spanning the entire 3D world. The exact values and their meanings depend on the selected result type. Each timeframe and each result child overlays has it's own grid of data. There are multiple ways to interact with this data. In addition, there are a few additional outputs provided by the water overlay specifically to gain further insight, verification, and visualization of the results.
Geographical overview
Visualization
Depending on whether the option is selected, the hydrological system can be visualized when when the overlay is activated. Each water level area will be visualized by a blue floating sphere and a striped border along the surface of the terrain. Sewer areas are visualized by an orange floating sphere. If the sewer has a sewer overflow, the overflow is connected to the sewer's sphere via an orange line. Culverts, weirs, and pumps are visualized by green, orange, and red spheres respectively for their endpoints, connected by blue lines.
Hover panel
Detailed results
Timeframes
Note that the simulation time is divided into a }TIMEFRAMES amount of periods, and at the end of each period a timeframe is recorded. This means the first timeframe is not a snapshot of the initial state of the simulation, but a snapshow of the state of the simulation after the first period of time has passed already.
TQL
Main article: TQL
Measuring tool
Main article: Measuring tool
While viewing the overlay, a general impression of the values can be seen at a glance. However, depending on the configuration of the overlay's legend the exact values may be difficult to view exactly. Using the measuring tool it's possible to retrieve the values of the overlay on exact locations. Additionally, cross-sections can be defined and easily have their values inspected.
Exporting Geotiff
Additional forms of output
A number of output forms don't fit in the analysis structure described above, but can provide additional information or insight into the calculation. These can provide different ways of looking at both the input and output of the simulation. They are offered as a means to further visualize but also verify the performed calculations.
Weather visualization
Saving overlay result
Water balance
Input Output
  • Breach
  • Inlet
  • Rain
  • Water surface
  • Inundated land
  • Breach out
  • Outlet
  • Land surface
  • Water surface
  • Building surface
  • Sewer storage
  • Evaporated
Debug info
Debug information as generated by a calculation of the Water Overlay.
After the calculation completes, some additional information is tallied and output for debugging purposes. This is intended for verification that the model has computed as expected, and may provide some basic information at a glance. It is not meant as a primary tool for in-depth analysis of the results.
The following information is displayed:
Debug info
  • Total rainfall
  • Simulation time (and amount of timeframes)
  • Map size
  • Amount of cells and amount of computational timesteps
  • Amount of special hydrological areas
  • Amount of flow over weirs
  • Amount of overflow from sewers
  • Total calculation time, and the amount of GPU's used to perform the calculation
  • Total volume of water processed
Input overlay
Main article: Average Overlay
The water overlay's calculations rely on multiple geographical parameters, such as manning values and evaporation factors. To help with both understanding the outcome of the calculation as well as verifying the results, the configuration wizard offers the option to add input overlays to the project, which are Average Overlays configured to display the input parameters geographically.
Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired attribute, and with an as small an averaging distance as possible. Optionally, a specific layer (such as constructions or terrains) can be configured which the overlay should inspect.
Model connections
The hydrological model can be linked to other models, which adds and defines more data for the simulation. Some models are automatically connected, and are required for the calculations to take place. Others are optional, and can apply additional detail to the calculations. When the optional models are absent, default behavior is defined.
Terrain height
Main article: Terrain height
Template:GeoTIFFSpec
Weather
Rain and simulation time
Linear configuration
Property Unit Description
Custom configuration
Evaporation rate
Ground water
Subsidence
Data
The calculations performed by the water overlay are influenced by many kinds of geographical information present in the project area. For any given location, terrain, constructions and other features can influence either the initial state of the simulation or how water flows in a given area.
Water level area
Sewer area
Breach
EXTERNAL_AREA m² The surface area of the external water body behind the breach. The larger the external water body, the more water can flow from it, and the smaller the effect of the inflow or outflow of water on the external water level. n/a
Inundation
Hydrological constructions
In general, hydrological constructions are loaded in as underground constructions.
  • Line-based constructions
  • Point-based constructions
Culvert
A culvert is a line-based constructions.
Weir
A weir is a line-based constructions.
Pump
A pump is a line-based constructions.
Sewer overflow
A sewer overflow is a point-based constructions. It must intersect with a sewer area, but does not need to intersect with a an actual sewer.
SEWER_OVERFLOW m + datum The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water height in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out. n/a
Inlet
An inlet is a point-based constructions.
Sewered constructions
Water storage constructions
Porous constructions
Crops and foliage
Constructions representing crops and foliage can draw water from the underground, allowing it to evaporate. This behaves in the same way as terrain which is configured as plants.
Critical structures
Chemical emitters/decomposers
Structures which are defined to create a negative amount of chemicals function as a scrubber or decomposer, removing the specified quantity of chemicals from the hydrological model.
Manning value (construction)
Construction height
Though not an explicit attribute or function value in and of itself, the height of constructions is taken into account when computing the flow of water above ground. Constructions are computed to have at most a height of DESIGN_FLOOD_ELEVATION_M. Lower constructions retain their own construction height. Taller constructions have their height capped at the attribute's value.
Terrains in a project have a number of hydrological properties which can influence the flow of water in a project. Because there is always both surface and underground terrain defined for the entirety of the project area, all cells are affected by all properties of terrains, unless a construction is present with overwriting values.
Water
Water terrains are processed by the water model in a specific manner before the simulation is started. For each water terrain in the 3D world, the bottom of the water body is treated as a land surface in the same fashion as dry land. Water is then placed on it on the surface layer, up to the level defined by the overlapping water level area's WATER_LEVEL attribute. Terrains not marked as water terrain are not initiated with water.
Plants
Terrains can be configured with plant-related attributes, similar to crops and foliage constructions, allowing it to draw water from the underground and evaporate it.
Also note that the groundwater level reduction is inversely proportional to the WATER_STORAGE_PERCENTAGE, as the contribution of a given volume of water to the groundwater level increases when the capacity for water storage in the underground layer decreases.
Infiltration and storage
WATER_STORAGE_PERCENTAGE fraction Underground The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer.
Manning value (terrain)
Settings
The water overlay features a number of overall settings which can be configured for the hydrological calculations and its results. These settings do not have a geographical or temporal element to them, and are fixed values relevant for the complete simulation.
Result type
1: Water area
2: Land
3: Sewer
4: Water object
5: Breach Area
6: Active Breach
IMPACTED_BUILDINGS nominal integer Maximum Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_THRESHOLD_M.
1...N: The (critical) construction is impacted, and has a critical function values set to this value.
SUBSTANCE_A x/m² Last The amount of substance A present. The value is the sum of the quantities on the surface, and the underground.
SUBSTANCE_B x/m² Last The amount of substance B present. The value is the sum of the quantities on the surface, and the underground.
SUBSTANCE_C x/m² Last The amount of substance C present. The value is the sum of the quantities on the surface, and the underground.
SUBSTANCE_D x/m² Last The amount of substance D present. The value is the sum of the quantities on the surface, and the underground.
SURFACE_ELEVATION Description wil be added
WATER_STRESS m (mm)¹ Maximum The amount of water on the surface, similar to SURFACE_MAX_VALUE. However, for water terrains, the water level must rise by at least ALLOWED_WATER_INCREASE_M. Otherwise, the reported value in those locations is 0.
Result child overlays
If a calculation overlay is removed, all result child overlays which are children of that overlay are removed as well. Separate overlays set as child overlays (such as input overlay) of the overlay will not be removed.
It is only possible to add result child overlays via the configuration wizard, in the output overlays step.
Keys
The water model calculations rely on a number of calculation-wide parameters. These parameters are available as attributes of the water overlay and can be modified as such.
QUAD_CELL boolean This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated.
SUPERGRID boolean This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated.
TIMEFRAMES integer The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed.
Calculations
The water overlay performs a large number of calculations to form a complete hydrological simulation. Depending on the desired viewpoint, both the overarching concepts as well as the implemented formulas can be reviewed for detailed insight into how the water overlay works.
Models
Surface model
The surface is defined by the terrain height in the project. The terrain height is further influenced by the height of constructions present in the project (bounded by DESIGN_FLOOD_ELEVATION_M) and by the BREACH_HEIGHT of breaches.
The surface water level is initialized based on hydrological features present in the project. For all water terrains, water is placed on the surface of the world. The amount of water placed is such that the resulting water level in that location is equal to the WATER_LEVEL attribute of the water level area in that location. If there is no water level area in that location, the water level is assumed to be so low that no water is created. Besides the water level areas, Inundation is added to the model. Water is placed in all locations where inundation is defined (regardless of the terrain type in that location, in contrast to the water level areas), such that the resulting height of the water inundating the land is equal to the inundation area's INUNDATION_LEVEL attribute.
Underground model
The underground water level is initialized with the values of the ground water GeoTIFF connected to the water model. If no ground water data is connected, the ground water level relative to datum is equal to the surface water level relative to datum, as defined by the WATER_LEVEL attribute of the water level area in that location.
When water infiltrates from the surface, it infiltrates at a speed dictated by the surface terrain's GROUND_INFILTRATION_MD attribute, the underground terrain's GROUND_INFILTRATION_MD attribute, or (if present) by the construction's GROUND_INFILTRATION_MD, whichever value is lowest. The least porous material present will always serve as a bottleneck for the water to flow through, even if the other layers allow for a high rate of infiltration.
Rain model
Rain can be implicitly activated and deactivated by defining an appropriate period of rainfall in the weather. If a period with no rainfall is defined, that period is simulated but no rain is simulated.
Evaporation model
Surface evaporation model
Underground evaporation model
Underground evaporation can be implicitly activated or deactivated by setting the relevant properties of all terrain types and constructions to appropriate evaporation values. If the relevant properties are set to 0, no underground evaporation will take place. Underground evaporation is also explicitly deactivated when the underground model is deactivated.
The rate of evaporation is determined by the weather's evaporation rate, and either the construction's WATER_EVAPORATION_FACTOR or the surface terrain's WATER_EVAPORATION_FACTOR.
Sewer model
Storage model
Water on the surface can be stored in water storage constructions.
Chemical flow model
Chemicals are added to the hydrological model and removed from the hydrological model by chemical emitters and decomposers. The chemicals created are then placed on the surface of the cells where they are created. Chemicals can also be removed by chemical constructions, if their attributes are configured appropriately. When chemicals enter the cell which contains a chemical decomposer, the chemicals are removed from the hydrological model.
When water moves from a cell which also contains chemicals, the chemicals are carried along with the water. The chemicals are uniformly distributed between the water which remains in the cell, which flows to other cells, and which infiltrates. Water which flows into the sewer explicitly cannot carry chemicals along with it.
Model border
The precise calculations which govern the water overlay's simulation are many and varied, and based as much as possible on available expert knowledge.
Timestep formula
Δt = Δx /umax
Where:
  • Δt = computational timestep
  • Δx = grid cell size
Surface water level formula
Where:
Surface flow formula
2D Saint Venant
  • friction
  • bed slope
  • water pressure
Groundwater level formula
WHunderground = Wsat / WSP
Where:
Surface infiltration formula
Infiltration capacities:
Cwater = Wsurface
Ctop = max( Icon, Isurf )
Actual infiltration:
Δw = min( Cwater , Δt * Ctop)
Where:
S = Wunsat/Hunsat
Δw = Cinf * S
Where:
Underground flow formula
Where:
  • cell = Cell size.
Culvert formula
CHreal = max( CHattr Tright , Tright )
WHleft = max(0, WLleft-CHreal)
WHright = max(0, WLright-CHreal)
Cfull = U * A * sqrt( 2 * G * abs(WHleft - WHright) )
Cpartial = 0.9 * A * sqrt( 2 * G * abs(WHleft - WHright) )
Cculvert = Cfull
Cculvert = min( Cfull , Cpartial ) if 0.5 < (WHleft/WHright) < 2
Δw = Δt * Cculvert / cell
Where:
  • cell = Cell size.
  • Cculvert = The potential rate of water flow through the culvert.
  • Cfull = The potential rate of water flow through the culvert, if the culvert is mostly filled.
  • Cpartial = The potential rate of water flow through the culvert, if the culvert is partially filled.
  • WHleft = The height of the water column relative to the bottom of the culvert on the left side of the culvert.
  • WHright = The height of the water column relative to the bottom of the culvert on the right side of the culvert.
  • CHreal = The CULVERT_HEIGHT of the culvert, recalculated so the culvert is not below ground on either side.
  • Ufull = Loss coefficient for fully submerged culverts (0.8 to 1.0).
  • Upartial = Loss coefficient for partially submerged culverts (0.9).
  • A = Flow area, based on the highest water level.
  • CW = The CULVERT_WIDTH attribute of the culvert.
  • CHattr = The CULVERT_HEIGHT attribute of the culvert.
Weir formula
Pump formula
Δw = min( Wlower , Δt * PS )
Where:
Overflow formula
Overflow can take place when:
Hsewer + SO - Hoverflow > 0
Actual overflow:
Inlet formula
If a Tlower is defined:
If a IQ is defined:
Cspeed = Δt * IQ
If a Ctotal is defined:
Cincap = Cused - Ctotal
If a IQ is defined:
Cspeed = Δt * IQ
Coutcap = -Ctotal - Cused
Where:
  • cell = Cell size.
Surface evaporation formula
Evaporation capacities:
Δw = Δwunsat + Δwsat
Where:
Computational structure
The formulas and concepts come together in a single computational structure which is repeated a large number of times until the total simulation duration has been reached.
Order of operations
  • Rain
  • Building storage
  • Sewer inflow
  • Surface evaporation
  • Underground infiltration
  • Surface infiltration
  • Exfiltration
Calculation time impacts
  1. ↑ 1.0 1.1 Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivy Preserving Central-Upwind Scheme for the Saint-Venant System ∙ p 15 ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)
  2. ↑ 2.0 2.1 2.2 Zsolt Horváth, Jürgen Waser, Rui A. P. Perdigão, Artem Konev and Günter Blöschl (2014) ∙ A two-dimensional numerical scheme of dry/wet fronts for the Saint-Venant system of shallow water equations ∙ found at: http://citeseerx.ist.psu.edu/viewdoc/download?doi=10.1.1.700.7977&rep=rep1&type=pdf ∙ http://visdom.at/media/pdf/publications/Poster.pdf ∙ (last visited 2018-06-29)
  3. ↑ Rezzolla L (2011) ∙ Numerical Methods for the Solution of Partial Differential Equations ∙ found at: http://www.scirp.org/(S(lz5mqp453edsnp55rrgjct55))/reference/ReferencesPapers.aspx?ReferenceID=1886006 (last visited 2018-06-29)
  4. ↑ Kurganov A, Petrova G (2007) ∙ A Second-Order Well-Balanced Positivy Preserving Central-Upwind Scheme for the Saint-Venant System ∙ found at: http://www.math.tamu.edu/~gpetrova/KPSV.pdf (last visited 2018-06-29)
  5. ↑ Bollermann A, Chen G, Kurganov A and Noelle S (2014) ∙ A Well-Balanced Reconstruction For Wetting/Drying Fronts ∙ found at: https://www.researchgate.net/publication/269417532_A_Well-balanced_Reconstruction_for_Wetting_Drying_Fronts (last visited 2018-06-29)
  6. ↑ Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods, book 6, chap. A55 ∙ p 31 ∙ found at: https://doi.org/10.3133/tm6A55 (last visited 2019-02-04)
  7. ↑ Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)