| Line 290: | Line 290: | ||
====Input overlay==== | ====Input overlay==== | ||
{{main|Average Overlay}} | {{main|Average Overlay}} | ||
The water overlay's calculations rely on multiple geographical parameters, such as {{inlink|WATER_MANING|Manning value}}s and {{inlink| | The water overlay's calculations rely on multiple geographical parameters, such as {{inlink|WATER_MANING|Manning value}}s and {{inlink|WATER_EVAPORATION_FACTOR_surface|evaporation factors}} . To help with both understanding the outcome of the calculation as well as verifying the results, the {{inlink|Configuration wizard|configuration wizard}} offers the option to add input overlays to the project, which are {{Average Overlay}}s configured to display the input parameters geographically. | ||
Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired [[attribute]], and with an as small an averaging distance as possible. Optionally, a specific layer (such as [[construction]]s or [[terrain]]s) can be configured which the overlay should inspect. | Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired [[attribute]], and with an as small an averaging distance as possible. Optionally, a specific layer (such as [[construction]]s or [[terrain]]s) can be configured which the overlay should inspect. | ||
Revision as of 10:37, 14 February 2019
What is the Water overlay
Variants
- Rainfall Overlay, provides insight into the water stress caused by (excessive) rainfall.
- Flooding Overlay, provides insight into water stress caused by breaches in levees or other sources causing excessive water inflow.
- Groundwater Overlay, provides insight into long-term processes of water flow both on the surface and underground.
Use cases
- Main article: Use cases Water Overlay
How to use the Water overlay
Prerequisites
- Your project has been loaded in with a high-resolution DEM. This can be configured during the new project wizard.
- Your project is large enough to account for edge effects.
- When creating a new project in the new project wizard, consider using the AHN3 dataset rather than the default AHN2. Where coverage is available, the AHN3 dataset will be more accurate. Where coverage is not available, the default AHN2 should be used.
- Additionally, when creating a new project, consider whether you want to use the IMWA dataset for hydrological constructions. Although this dataset is not complete, some information about constructions which serve as culverts other relevant objects can be loaded in from this datasource. If more complete or accurate data is available to be loaded in into the project after it is created, it may be desirable to disregard this source so that hydrological constructions are not doubly included.
- Water flow can often be dictated by small features in an area, such as small openings between buildings, and thin levees. To have these small features included properly in the calculations, the grid cell size will need to be set to an appropriate size. The default setting offered by the Tygron Platform will often need to be adjusted to allow for smaller features to be recognized without having their presence averaged out with their surroundings.
- The water overlay performs a complete simulation, which is a series of complex calculations across multiple layers. Depending on the configuration of the overlay, the calculation time can range from seconds to hours. If the overlay is to be used in a setting where response times need to be short, it may be preferable to configure the overlay for greater speed rather than excessive precision.
Configuration
Step 1: Weather
Step 2: Water system
- Breach (flooding overlays only): A breach, a location where an (uncontrolled) inflow of water takes places, can be imported or connected to the hydrological model.
- Water areas: Water level areas, defined regions in which a specific water level is maintained, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single water level area for the entire project area.
- Ground water: Ground water, the height of the underground saturated by water, relative to datum. A GeoTIFF can be imported.
- Sewers: Sewer areas, the broad definitions for where what kind of sewert exist, can be imported or connected to the hydrological model. It is also possible to have the wizard generate sewer areas based on the neighborhoods in the project area.
- Inundation areas: Inundation areas, definitions of water on the surface, in the forum of inundated land, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single inundation area covering the entire project area.
- Weirs: Weirs, minor barriers in the water flow, can be imported or connected to the hydrological model.
- Culverts: Culverts, tunnels which form direct connections between two locations, can be imported or connected to the hydrological model.
- Pumps: Pumps, structures which move water from a lower to a higher location, can be imported or connected to the hydrological model.
- Inlets: Inlets, structures which add or remove water, can be imported or connected to the hydrological model.
- Sewer overflows: Sewer overflows, points where water from sewers can flow back onto the surface, can be imported or connected to the hydrological model.
- Surface terrain: For the surface terrains, attributes can be adjusted directly.
- Underground terrain: For the underground terrains, attributes can be adjusted directly as well.
- Constructions: For constructions, the wizard links to the function values editing screen, and will open it the "WATER" filter for the values to display.
Step 4: Interaction
Step 5: Output overlays
Step 6: Input overlays
To gain more insight into the data used by the model, you may opt to add one or more input overlays as well. These add Average Overlays configured for the geographical display of attribute values relevant for the calculation of the water model.
Manual configuration
Grid cell size configuration
- Main article: Grid overlay
- Main section: Calculation preference formula
- Main section: Weather
Ground water configuration
- Main section: Ground water
Subsidence configuration
- Main section: Subsidence
- Main section: System visualization
Active in simulation setting
Result type configuration
- Main section: Result type
Legend configuration
Keys configuration
- Main section: Data
Attributes configuration
- Main section: Attributes
Results
When the calculation completes, the results are stored as numerical values in a grid spanning the entire 3D world. The exact values and their meanings depend on the selected result type. Each timeframe and each result child overlay has it's own grid of data. There are multiple ways to interact with this data. In addition, there are a few additional outputs provided by the water overlay specifically to gain further insight, verification, and visualization of the results.
Geographical overview
Visualization
Depending on whether the option is selected, the hydrological system can be visualized when when the overlay is activated. Each water level area will be visualized by a blue floating sphere and a striped border along the terrain surface. Sewers are visualized by an orange floating sphere. If the sewer has a sewer overflow, the overflow is connected to the sewer's sphere via an orange line. Culverts, weirs, and pumps are visualized by green, orange, and red spheres respectively for their endpoints, connected by blue lines.
Hover panel
- The ground height, which is the terrain height relative to datum.
- The output value of the overlay, which is dependent on the selected result type.
- The hydrological properties of the terrain (if applicable), such as manning value and infiltration speed.
- The hydrological properties of features (if applicable), such as water level, inundation level, and altered terrain height.
- The hydrological properties of constructions (if applicable), such as building storage, and sewer storage of sewered buildings.
Detailed results
Timeframes
TQL
- Main article: TQL
Measuring tool
- Main article: Measuring tool
While viewing the overlay in the 3D client, a general impression of the values can be seen at a glance. However, depending on the configuration of the overlay's legend the exact values may be difficult to view exactly. Using the measuring tool it's possible to retrieve the values of the overlay on exact locations. Additionally, cross-sections can be defined and easily have their values inspected.
Exporting Geotiff
Additional forms of output
Weather visualization
Saving overlay result
Water balance
| Input | Output |
Debug info
After the calculation completes, some additional information is tallied and output for debugging purposes. This is intended for verification that the model has computed as expected, and may provide some basic information at a glance. It is not meant as a primary tool for in-depth analysis of the results.
The following information is displayed:
| Debug info |
Input overlay
- Main article: Average Overlay
The water overlay's calculations rely on multiple geographical parameters, such as Manning values and evaporation factors . To help with both understanding the outcome of the calculation as well as verifying the results, the configuration wizard offers the option to add input overlays to the project, which are Template:Average Overlays configured to display the input parameters geographically.
Overlays such as these can also be created manually, by creating an Average Overlay and configuring it such that it functions on the desired attribute, and with an as small an averaging distance as possible. Optionally, a specific layer (such as constructions or terrains) can be configured which the overlay should inspect.
Model connections
Terrain height
- Main article: Terrain height
Weather
Rain and simulation time
Linear configuration
Custom configuration
Template:CSVSpec
Evaporation rate
Template:CSVSpec
Ground water
Subsidence
- Main article: Subsidence (Overlay)
Data
Water level area
Sewer area
Breach
| BREACH_HEIGHT | m + datum | The new terrain height at the location of the breach. | n/a |
| BREACH_WIDTH | m | The radius of the breach as drawn on the polygon defining the breach, emanating from the center point. | 10000 |
| BREACH_SPEED | m/s | The speed at which water should flow through the breach before the width begins to increase. | n/a |
| EXTERNAL_SURFACE_LEVEL | m + datum | The height of the bottom of the external water body behind the breach. The lowest level the external water level can lower to. | 0 |
| EXTERNAL_WATER_LEVEL | m + datum | The water level of the external water body behind the breach. The initial level the water level is set to. | 0 |
| EXTERNAL_AREA | m² | The surface area of the external water body behind the breach. The larger the external water body, the more water can flow from it, and the smaller the effect of the inflow or outflow of water on the external water level. | n/a |
Inundation
Hydrological constructions
- Line-based constructions
Culvert
Weir
Pump
| PUMP_SPEED | m3/s | The speed at which water is pumped from the lower end-point to the higher end-point. | n/a |
Sewer overflow
Inlet
Sewered constructions
Water storage constructions
Porous constructions
Crops and foliage
Critical structures
Chemical emitters/decomposers
Water
Evaporation
Infiltration and storage
| WATER_STORAGE_PERCENTAGE | fraction | Underground | The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer. |
Settings
Result type
| GPU OVERVIEW | nominal integer | Maximum | Shows which GPU cluster calculated which part of the overlay. |
| IMPACTED_BUILDINGS | nominal integer | Maximum | Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_TRESHOLD_M. 0: Construction is not impacted |
| UNDERGROUND_LAST_STORAGE | m (mm)¹ | Last | The (effective) amount of water in the underground unsaturated zone. |
| UNDERGROUND_LAST_VALUE | m (mm)¹ | Last | The distance between the surface and the groundwater level. |
| UNDERGROUND_MAX_STORAGE | m (mm)¹ | Maximum | The (effective) amount of water in the underground unsaturated zone. |
| UNDERGROUND_MAX_VALUE | m (mm)¹ | Maximum | The distance between the surface and the groundwater level. |
Result child overlays
Keys
The water model calculations rely on a number of calculation-wide parameters. These parameters are available as attributes of the water overlay and can be modified as such.
| MIN_SLOPE | ratio | The minimum slope required to account for the effect of gravity on the speed of the water. If the slope of the terrain is less than the minimum slope, the effect of gravity on the speed of the water is assumed to be 0. The ratio is the height over distance. |
| QUAD_CELL | boolean | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. |
| SUPERGRID | boolean | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. |
| TIMEFRAMES | integer | The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed. |
Calculations
Models
Surface model
Underground model
Rain model
Evaporation model
Surface evaporation model
Underground evaporation model
Sewer model
Storage model
Chemical flow model
Model border
Timestep formula
- Δt = Δx /umax
Where:
- Δt = computational timestep
- Δx = grid cell size
Surface water level formula
- WLsurface = Wsurface + Hsurface
Where:
- WLsurface = The water level, relative to datum.
- Wsurface = The amount of water (the water column) on the surface.
- Hsurface = The terrain height in the cell, relative to datum.
Surface flow formula
2D Saint Venant
- friction
- bed slope
- water pressure
Groundwater level formula
- WHunderground = Wsat / WSP
- WLunderground = WHunderground + Hsurface - GBDM
Where:
- WLunderground = The groundwater level, relative to datum.
- WHunderground = The height (column) of the saturated zone.
- Wsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
- GBDM = The GROUND_BOTTOM_DISTANCE_M(effectively available height in the underground model).
Surface infiltration formula
Infiltration capacities:
- Cwater = Wsurface
- Ctop = max( Icon, Isurf )
- Isurf = 0 if a construction is present
- Icon = 0 if no construction is present
Actual infiltration:
- Δw = min( Cwater , Δt * Ctop)
Where:
- Cwater = The amount of infiltration that can take place based on the amount of water on the surface.
- Ctop = The amount of evaporation that can take place based on the infiltration values present.
- Hunsat = Hsurface - WLunderground
- S = Wunsat/Hunsat
- Cinf = min( Hunsat , Δt * Iund )
- Δw = Cinf * S
Where:
- Hunsat = The height of the unsaturated zone.
- S = Ratio of water to height in the unsaturated zone.
- Cinf = The height in the unsaturated zone which can be subject to infiltration to the saturated zone.
- Wunset = The amount of water in the unsaturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
Underground flow formula
- Cd = Δt * Iund * width * A * ( (WLsource - WLtarget) / distance )
- Cd = Δt * Iund * A * (Wsource - Wtarget) / cell
- Cwsp = (WLsource - WLtarget) * (WSPsource / (WSPsource + WSPtarget) )
- Δw = max( 0 , min( Cd , Cwsp ) )
Where:
- Δw = The underground flow which takes place.
- cell = Cell size.
- Cd = The capacity for water flow possible based on the relative water heights.
- Cwsp = The capacity for water flow possible based on the relative water storage percentages.
- WLsource = The amount of water in the saturated zone of the source cell. The height of the water column if the equivalent amount of water was placed on the surface.
- WLtarget = The amount of water in the saturated zone of the target cell. The height of the water column if the equivalent amount of water was placed on the surface.
- A = Contact area of the underground cells
- Iund = The GROUND_INFILTRATION_MD of the underground terrain type of the origin cell.
- WSPsource = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the origin cell.
- WSPtarget = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the target cell.
Culvert formula
- CHreal = max( CHattr Tright , Tright )
- WHleft = max(0, WLleft-CHreal)
- WHright = max(0, WLright-CHreal)
- Cfull = U * A * sqrt( 2 * G * abs(WHleft - WHright) )
- Cpartial = 0.9 * A * sqrt( 2 * G * abs(WHleft - WHright) )
- Cculvert = Cfull
- Cculvert = min( Cfull , Cpartial ) if 0.5 < (WHleft/WHright) < 2
- Δw = Δt * Cculvert / cell
Where:
- Δw = The water flow which takes place.
- cell = Cell size.
- Cculvert = The potential rate of water flow through the culvert.
- Cfull = The potential rate of water flow through the culvert, if the culvert is mostly filled.
- Cpartial = The potential rate of water flow through the culvert, if the culvert is partially filled.
- WHleft = The height of the water column relative to the bottom of the culvert on the left side of the culvert.
- WHright = The height of the water column relative to the bottom of the culvert on the right side of the culvert.
- CHreal = The CULVERT_HEIGHT of the culvert, recalculated so the culvert is not below ground on either side.
- Ufull = Loss coefficient for fully submerged culverts (0.8 to 1.0).
- Upartial = Loss coefficient for partially submerged culverts (0.9).
- A = Flow area, based on the highest water level.
- G = Acceleration factor of gravity
- CW = The CULVERT_WIDTH attribute of the culvert.
- CHattr = The CULVERT_HEIGHT attribute of the culvert.
Weir formula
Pump formula
- Δw = min( Wlower , Δt * PS )
Where:
- Δw = The amount water water pumped from the lower to the higher endpoint.
- Wlower = The water amount of water (the water column) at the lower end point.
- Hlower = The terrain height at the lower end point, relative to datum.
- PS = The PUMP_SPEED of the pump.
Overflow formula
Overflow can take place when:
- Hsewer + SO - Hoverflow > 0
Actual overflow:
- Δw = min( 0 , WHsewer * Σsewer , Δt * SOS )
- Δw = The amount of sewer overflow which takes place.
- Σsewer = The surface area of the sewer.
- WHsewer = The water height sewer.
- Hsewer = The average height of the terrain where the sewer is present, relative to datum.
- Hoverflow = The height of the terrain at the centerpoint of the sewer overflow, relative to datum.
- SO = The SEWER_OVERFLOW attribute of the sewer overflow.
- SOS = The SEWER_OVERFLOW_SPEED attribute of the sewer overflow.
Inlet formula
If a Tlower is defined:
- Cinthres = max( 0 , Tlower - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
If a Ctotal is defined:
- Cincap = Cused - Ctotal
- Δw = max( 0 , min( Cinthres , Cspeed , Cincap ) ) / cell
- If any of the terms are undefined, they are not included.
- Coutthres = min( 0 , Tupper - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
- Coutcap = -Ctotal - Cused
- Δw = min( 0 , max( Coutthres , Cspeed , Coutcap) ) / cell
- Cused (new) = Cused (old) + (Δw * cell)
Where:
- Δw = The amount of water flow which takes place.
- cell = Cell size.
- Cspeed = The amount of water inflow (or outflow when negative) possible based on the inlet's INLET_Q attribute.
- Cincap = The amount of water inflow possible based on the total capacity of the inlet.
- Coutcap = The amount of water outflow possible based on the total capacity of the outlet.
- Cinthres = The amount of water inflow desired based on the inlet's LOWER_THRESHOLD attribute.
- Coutthres = The amount of water outflow desired based on the outlet's UPPER_THRESHOLD attribute.
- WLsurface The water level on the surface, relative to datum.
- Ctotal = The INLET_CAPACITY attribute of the inlet.
- IQ = The INLET_Q attribute of the inlet.
- Tlower = The LOWER_THRESHOLD attribute of the inlet.
- Tupper = The UPPER_THRESHOLD attribute of the inlet.
Surface evaporation formula
- Δw = min( WLsurface , Δt * Eweather * Eoverlay )
Evaporation capacities:
- Csat = max( 0 , min( RD , GBDM ) - Hunsat ) * WSP
- Cunsat = max( 0 , min( RD , Hunsat ) ) * ( Wunsat / Hunsat )
- Δwunsat = min( Cunsat , Δt * Eweather * Etop )
- Δwsat = min( Csat , (Δt * Eweather * Etop) - Δwunsat )
- Δw = Δwunsat + Δwsat
Where:
- Δw = The total amount of evaporation which takes place.
- Δwunsat = The amount of evaporation which takes place from the unsaturated zone.
- Δwsat = The amount of evaporation which takes place from the saturated zone.
- Cunsat = The amount of evaporation that can take place from the unsaturated zone.
- Hunsat = The height (column) of the unsaturated zone.
- Wunsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
- RD = The ROOT_DEPTH_M of the construction if present, the ROOT_DEPTH_M of the surface terrain otherwise.
Computational structure
Order of operations
- Horizontal surface flow and horizontal underground flow
- Rain
- Building storage
- Sewer inflow
- Surface evaporation
- Groundwater evaporation (saturated zone)
- Groundwater evaporation (unsaturated zone)
- Underground infiltration
- Surface infiltration
- Exfiltration
Calculation time impacts
General Tab
Calculation Preference
Δt = Δx /umax
Grid cell size
Refresh Grid
Export Grid File
Save Overlay result
Show Water Balance
Warnings
Debug Info
- Water areas:
- ↑ Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods, book 6, chap. A55 ∙ p 31 ∙ found at: https://doi.org/10.3133/tm6A55 (last visited 2019-02-04)
- ↑ Hydraulic Radius Equations Formulas Calculator ∙ found at: https://www.ajdesigner.com/phphydraulicradius/hydraulic_radius_equation_pipe.php ∙ (last visited 2019-02-11)