Line 61: | Line 61: | ||
===Manual configuration=== | ===Manual configuration=== | ||
{{Editor ribbon|header=Current situation|bar=Overlays|left panel=The overlay}} | |||
====Grid overlay settings==== | ====Grid overlay settings==== | ||
{{main|Grid overlay}} | {{main|Grid overlay}} | ||
Like all grid overlays, the water overlays have a number of configuration options related to their general method of calculation. | {{Editor ribbon|header=Current situation|bar=Overlays|left panel=The overlay|right panel=General tab}} | ||
Like all grid overlays, the water overlays have a number of configuration options related to their general method of calculation. Most notably, it is possible to configure the cell size on which the calculations occur. | |||
The grid cell size can be changed by selecting "Change Grid". The minimum and maximum grid cell size depend on the project size. A larger cell size will allow for faster calculations. A smaller cell size will produce more detailed results. | |||
====Result type==== | |||
{{Editor ribbon|header=Current situation|bar=Overlays|left panel=The overlay|right panel=General tab}} | |||
The calculation performed can produce a multitude of results. | |||
==Data== | ==Data== |
Revision as of 10:00, 6 February 2019
What are the Water Overlays
Configuration
Configuration wizard
Each of the water overlay variants has a configuration wizard which helps the user with configuring the overlay. The general structure of the wizard is the same for all variants, with the exception that for flooding overlays a breach area can be configured as well.
Step 1: Weather
Step 2: Water system
- Breach (flooding overlays only): A breach, a location where an (uncontrolled) inflow of water takes places, can be imported or connected to the hydrological model.
- Water areas: Water level areas, defined regions in which a specific water level is maintained, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single water level area for the entire project area.
- Ground water: Ground water, the height of the underground saturated by water, relative to datum. A GeoTIFF can be imported.
- Sewers: Sewer areas, the broad definitions for where what kind of sewert exist, can be imported or connected to the hydrological model. It is also possible to have the wizard generate sewer areas based on the neighborhoods in the project area.
- Inundation areas: Inundation areas, definitions of water on the surface, in the forum of inundated land, can be imported or connected to the hydrological model. It is also possible to have the wizard generate a single inundation area covering the entire project area.
- Weirs: Weirs, minor barriers in the water flow, can be imported or connected to the hydrological model.
- Culverts: Culverts, tunnels which form direct connections between two locations, can be imported or connected to the hydrological model.
- Pumps: Pumps, structures which move water from a lower to a higher location, can be imported or connected to the hydrological model.
- Inlets: Inlets, structures which add or remove water, can be imported or connected to the hydrological model.
- Sewer overflows: Sewer overflows, points where water from sewers can flow back onto the surface, can be imported or connected to the hydrological model.
- Surface terrain: For the surface terrains, attributes can be adjusted directly.
- Underground terrain: For the underground terrains, attributes can be adjusted directly as well.
- Constructions: For constructions, the wizard links to the function values editing screen, and will open it the "WATER" filter for the values to display.
Step 4: Interaction
Step 5: Output overlays
Step 6: Input overlays
- Main article: Grid overlay
Result type
Data
Model connections
Terrain height
- Main article: Terrain height
Weather
Rain and simulation time
Linear configuration
Property | Unit | Description |
Rain for | minutes | How long rain should last at the start of the simulation. |
Total rainfall | mm | How much rain should fall in the specified period. |
Dry after rain (days, hours, minutes) | days, hours, minutes | How long the simulation continues after the rain has fallen. |
Custom configuration
Rain and simulation CSV specification | |||||||||
Data per line | Additional rainfall until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Rain should never be negative | ||||||||
First entry | Second entry | ||||||||
Time (s) | Rain (m) | ||||||||
Line 1 | Time when first period ends | Total rain during first period | |||||||
Line 2 | Time when second period ends | Total rain during second period |
Evaporation
Surface evaporation | mm/day | The speed at which water evaporates during the simulation |
Evaporation CSV specification | |||||||||
Data per line | Rate of evaporation until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Evaporation should never be negative | ||||||||
Time (s) | Evaporation (m) | ||||||||
Line 1 | Time when first period ends | Amount of evaporation during first period | |||||||
Line 2 | Time when second period ends | Amount of evaporation during second period |
Ground water
Subsidence
Hydrological features
Water level area
Attribute | Unit | Description | Default (when attribute is not present) |
WATER_LEVEL | m + datum | The water level for all water terrains in this water level area | n/a |
Sewer area
SEWER_STORAGE | m | The maximum height the water can reach in this sewer. This value, multiplied by the surface area of the sewered constructions the sewer area intersects with, forms the total amount of water this sewer can store. | n/a |
SEWER_PUMP_SPEED | m3/s | The amount of water removed from the sewer by removing it from the hydrological model entirely. | 0 |
Breach
The breach can grow over time, based on its initial width and the critical speed at which water may flow. If a BREACH_WIDTH is defined, the breach's polygon is intersected with a circle emanating from the centerpoint of the polygon. It is only in that intersection, dubbed the "active breach" that the terrain height is considered lowered to the BREACH_HEIGHT. The radius of the circle defining the intersection will expand when the water flowing in from the external water body exceeds the BREACH_SPEED. Water flowing in the hydrological model across the breach's surface without explicitly entering or leaving the hydrological model does not "count" for the critical speed. All cells in the active breach are considered directly adjacent to the external water body.
BREACH_HEIGHT | m + datum | The new terrain height at the location of the breach. | n/a |
BREACH_WIDTH | m | The radius of the breach as drawn on the polygon defining the breach, emanating from the center point. | 10000 |
BREACH_SPEED | m/s | The speed at which water should flow through the breach before the width begins to increase. | n/a |
EXTERNAL_SURFACE_LEVEL | m + datum | The height of the bottom of the external water body behind the breach. The lowest level the external water level can lower to. | 0 |
EXTERNAL_WATER_LEVEL | m + datum | The water level of the external water body behind the breach. The initial level the water level is set to. | 0 |
EXTERNAL_AREA | m² | The surface area of the external water body behind the breach. The larger the external water body, the more water can flow from it, and the smaller the effect of the inflow or outflow of water on the external water level. | n/a |
Inundation
INUNDATION_LEVEL | m + datum | The height of the water. | n/a |
Hydrological constructions
- Line-based constructions
Culvert
Attribute | Unit | Description | Default |
CULVERT_WIDTH | m | The diameter of the culvert. For throughput calculations, the culvert is assumed to have a spherical cross-section. | 1 |
CULVERT_HEIGHT | m + datum | The height of the culvert. (When set to a level lower than the terrain for either endpoint of it, the culvert's height is equal to the height of the (highest) terrain under either endpoint.) | 0 |
CULVERT_N | manning value | The manning value of the culvert's material, which influences the flow speed. | 0,014 |
Weir
WEIR_HEIGHT | m + datum | The height of the weir. | n/a |
WEIR_WIDTH | m | The width of the weir. | 5 |
WEIR_COEFFICIENT | coefficient | The flow coefficient related to the shape of the weir | 1,1 |
Pump
PUMP_SPEED | m3/s | The speed at which water is pumped from the lower end-point to the higher end-point. | n/a |
Sewer overflow
SEWER_OVERFLOW | m + datum | The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water level in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out. | n/a |
SEWER_OVERFLOW_SPEED | m3/s | The maximum speed at which water can flow out from the sewer through this overflow. | 10 |
Inlet
INLET_Q | m3/sec | The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model. | n/a |
INLET_CAPACITY | m3 | The maximum amount of water which can flow in or out through this construction. Water flowing back in the other direction replenishes the capacity. | Infinite |
LOWER_THRESHOLD | m + datum | If a lower threshold is set, water will only flow into the model through this inlet until the water level at the point of this inlet is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion. | None |
UPPER_THRESHOLD | m + datum | If an upper threshold is set, water will only flow out the model through this outlet until the water level at the point of this inlet is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion. | None |
Sewered constructions
Attribute | Unit | Function value | Description |
SEWERED | boolean | Connected to sewer | Whether this construction is connected to the sewer. |
Water storage constructions
WATER_STORAGE | m³/m² | Water storage (m³/m²) | How much water this construction can store. |
Porous constructions
GROUND_INFILTRATION_MD | m/day | Ground infiltration per day (m) | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
Crops and foliage
ROOT_DEPTH_M | m | Depth of plant roots (m) | The depth of the roots of this construction, relative to the terrain height at the location of this construction. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Water evaporation | How fast this construction can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Critical structures
CRITICAL_INFRASTRUCTURE | nominal integer | Critical infrastructure | Whether this construction is deemed a critical construction. 0 means the construction is never deemed impacted. |
Chemical emitters/decomposers
CHLORIDE | x/m² | The amount of chloride created per second per m² in this location. | 0 |
NITROGEN | x/m² | The amount of nitrogen created per second per m² in this location. | 0 |
PHOSPHORUS | x/m² | The amount of phosphorus created per second per m² in this location. | 0 |
Water
Attribute | Unit | Terrain type | Description |
WATER | boolean | Surface | Whether the specified terrain is a water terrain. |
Evaporation
ROOT_DEPTH_M | m | Surface | The depth of the roots of this surface terrain, relative to the surface. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Surface | How fast this terrain can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Infiltration and storage
GROUND_INFILTRATION_MD | m/day | Surface | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
GROUND_INFILTRATION_MD | m/day | Underground | The speed at which water can flow vertically from the underground unsaturated zone to the underground saturated zone, and horizontally through across the saturated zone. |
WATER_STORAGE_PERCENTAGE | percentage | Underground | The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer. |
Result types
Result type | Unit | Display mode | Description |
BASE_TYPES | Nominal value | Start | Categorization of the individual cells based on how they are processed by the water model, displaying which cells are considered to be specific features. 0: Cell on the edge of the project area |
CHLORIDE | x/m² | Last | The amount of chloride present. The value is the sum of the quantities on the surface, and the underground. |
DIRECTION | Degrees | Last | The direction in which water is flowing. |
EVAPORATED | m (mm)¹ | Total | The amount of water that has evaporated. The value is the sum of the quantities evaporated from the surface and the underground. |
GPU OVERVIEW | nominal integer | Maximum | Shows which GPU cluster calculated which part of the overlay. |
IMPACTED_BUILDINGS | nominal integer | Maximum | Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_TRESHOLD_M. 0: Construction is not impacted |
LAST SPEED | m/s | Last | The speed of water flow in any given location. |
MAX SPEED | m/s | Maximum | The speed of water flow in any given location. |
NITROGEN | x/m² | Last | The amount of nitrogen present. The value is the sum of the quantities on the surface, and the underground. |
PHOSPHORUS | x/m² | Last | The amount of phosphorus present. The value is the sum of the quantities on the surface, and the underground. |
SEWER_LAST_VALUE | m (mm)¹ | Last | The amount of water stored in the sewer. |
SEWER_MAX_VALUE | m (mm)¹ | Maximum | The amount of water stored in the sewer. |
SURFACE_DURATION | s (min)¹ | Total | The amount of time the water depth on the surface exceeds SHOW_DURATION_FLOOD_LEVEL_M. |
SURFACE_FLOW | m³/m² | Description wil be added | |
SURFACE_LAST_VALUE | m (mm)¹ | Last | The amount of water on the surface. |
SURFACE_MAX_VALUE | m (mm)¹ | Maximum | The amount of water on the surface. |
UNDERGROUND_FLOW | m³/m² | Description wil be added | |
UNDERGROUND_LAST_STORAGE | m (mm)¹ | Last | The (effective) amount of water in the underground unsaturated zone. |
UNDERGROUND_LAST_VALUE | m (mm)¹ | Last | The distance between the surface and the groundwater level. |
UNDERGROUND_MAX_STORAGE | m (mm)¹ | Maximum | The (effective) amount of water in the underground unsaturated zone. |
UNDERGROUND_MAX_VALUE | m (mm)¹ | Maximum | The distance between the surface and the groundwater level. |
UNDERGROUND WATERTABLE | m + datum | Last | The groundwater level, relative to datum. |
WATER_STRESS | m (mm)¹ | Maximum | The amount of water on the surface, similar to SURFACE_MAX_VALUE. However, for water terrains, the water level must rise by at least ALLOWED_WATER_INCREASE_M. Otherwise, the value in those locations is 0. |
Result child overlays
Calculations
Models
Surface model
Underground model
Rain model
Evaporation model
Surface evaporation model
Underground evaporation model
Sewer model
Storage model
Chemical flow model
Model border
Timestep formula
- Δt = Δx /umax
Where:
- Δt = computational timestep
- Δx = grid cell size
Surface water level formula
- WLsurface = Wsurface + Hsurface
Where:
- WLsurface = The water level, relative to datum.
- Wsurface = The amount of water (the water column) on the surface.
- Hsurface = The terrain height in the cell, relative to datum.
Surface flow formula
2D Saint Venant
- friction
- bed slope
- water pressure
Groundwater level formula
- WHunderground = Wsat / WSP
- WLunderground = WHunderground + Hsurface - GBDM
Where:
- WLunderground = The groundwater level, relative to datum.
- WHunderground = The height (column) of the saturated zone.
- Wsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
- GBDM = The GROUND_BOTTOM_DISTANCE_M(effectively available height in the underground model).
Surface infiltration formula
Infiltration capacities:
- Cwater = Wsurface
- Ctop = max( Icon, Isurf )
- Isurf = 0 if a construction is present
- Icon = 0 if no construction is present
Actual infiltration:
- Δw = min( Cwater , Δt * Ctop)
Where:
- Cwater = The amount of infiltration that can take place based on the amount of water on the surface.
- Ctop = The amount of evaporation that can take place based on the infiltration values present.
- Hunsat = Hsurface - WLunderground
- S = Wunsat/Hunsat
- Cinf = min( Hunsat , Δt * Iund )
- Δw = Cinf * S
Where:
- Hunsat = The height of the unsaturated zone.
- S = Ratio of water to height in the unsaturated zone.
- Cinf = The height in the unsaturated zone which can be subject to infiltration to the saturated zone.
- Wunset = The amount of water in the unsaturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
Underground flow formula
- Cd = Δt * Iund * width * A * ( (WLsource - WLtarget) / distance )
- Cd = Δt * Iund * A * (Wsource - Wtarget) / cell
- Cwsp = (WLsource - WLtarget) * (WSPsource / (WSPsource + WSPtarget) )
- Δw = max( 0 , min( Cd , Cwsp ) )
Where:
- Δw = The underground flow which takes place.
- cell = Cell size.
- Cd = The capacity for water flow possible based on the relative water heights.
- Cwsp = The capacity for water flow possible based on the relative water storage percentages.
- WLsource = The amount of water in the saturated zone of the source cell. The height of the water column if the equivalent amount of water was placed on the surface.
- WLtarget = The amount of water in the saturated zone of the target cell. The height of the water column if the equivalent amount of water was placed on the surface.
- A = Contact area of the underground cells
- Iund = The GROUND_INFILTRATION_MD of the underground terrain type of the origin cell.
- WSPsource = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the origin cell.
- WSPtarget = The WATER_STORAGE_PERCENTAGE of the underground terrain type of the target cell.
Culvert formula
Weir formula
Pump formula
- Δw = min( Wlower , Δt * PS )
Where:
- Δw = The amount water water pumped from the lower to the higher endpoint.
- Wlower = The water amount of water (the water column) at the lower end point.
- Hlower = The terrain height at the lower end point, relative to datum.
- PS = The PUMP_SPEED of the pump.
Overflow formula
Overflow can take place when:
- Hsewer + SO - Hoverflow > 0
Actual overflow:
- Δw = min( 0 , WHsewer * Σsewer , Δt * SOS )
- Δw = The amount of sewer overflow which takes place.
- Σsewer = The surface area of the sewer.
- WHsewer = The water height sewer.
- Hsewer = The average height of the terrain where the sewer is present, relative to datum.
- Hoverflow = The height of the terrain at the centerpoint of the sewer overflow, relative to datum.
- SO = The SEWER_OVERFLOW attribute of the sewer overflow.
- SOS = The SEWER_OVERFLOW_SPEED attribute of the sewer overflow.
Inlet formula
If a Tlower is defined:
- Cinthres = max( 0 , Tlower - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
If a Ctotal is defined:
- Cincap = Cused - Ctotal
- Δw = max( 0 , min( Cinthres , Cspeed , Cincap ) ) / cell
- If any of the terms are undefined, they are not included.
- Coutthres = min( 0 , Tupper - WLsurface )
If a IQ is defined:
- Cspeed = Δt * IQ
- Coutcap = -Ctotal - Cused
- Δw = min( 0 , max( Coutthres , Cspeed , Coutcap) ) / cell
- Cused (new) = Cused (old) + (Δw * cell)
Where:
- Δw = The amount of water flow which takes place.
- cell = Cell size.
- Cspeed = The amount of water inflow (or outflow when negative) possible based on the inlet's INLET_Q attribute.
- Cincap = The amount of water inflow possible based on the total capacity of the inlet.
- Coutcap = The amount of water outflow possible based on the total capacity of the outlet.
- Cinthres = The amount of water inflow desired based on the inlet's LOWER_THRESHOLD attribute.
- Coutthres = The amount of water outflow desired based on the outlet's UPPER_THRESHOLD attribute.
- WLsurface The water level on the surface, relative to datum.
- Ctotal = The INLET_CAPACITY attribute of the inlet.
- IQ = The INLET_Q attribute of the inlet.
- Tlower = The LOWER_THRESHOLD attribute of the inlet.
- Tupper = The UPPER_THRESHOLD attribute of the inlet.
Surface evaporation formula
- Δw = min( WLsurface , Δt * Eweather * Eoverlay )
Evaporation capacities:
- Csat = max( 0 , min( RD , GBDM ) - Hunsat ) * WSP
- Cunsat = max( 0 , min( RD , Hunsat ) ) * ( Wunsat / Hunsat )
- Δwunsat = min( Cunsat , Δt * Eweather * Etop )
- Δwsat = min( Csat , (Δt * Eweather * Etop) - Δwunsat )
- Δw = Δwunsat + Δwsat
Where:
- Δw = The total amount of evaporation which takes place.
- Δwunsat = The amount of evaporation which takes place from the unsaturated zone.
- Δwsat = The amount of evaporation which takes place from the saturated zone.
- Cunsat = The amount of evaporation that can take place from the unsaturated zone.
- Hunsat = The height (column) of the unsaturated zone.
- Wunsat = The amount of water in the saturated zone. The height of the water column if the equivalent amount of water was placed on the surface.
- RD = The ROOT_DEPTH_M of the construction if present, the ROOT_DEPTH_M of the surface terrain otherwise.
Computational structure
Order of operations
- Horizontal surface flow and horizontal underground flow
- Rain
- Building storage
- Sewer inflow
- Surface evaporation
- Groundwater evaporation (saturated zone)
- Groundwater evaporation (unsaturated zone)
- Underground infiltration
- Surface infiltration
- Exfiltration
Calculation time impacts
General Tab
Calculation Preference
Δt = Δx /umax
Grid cell size
Refresh Grid
Export Grid File
Save Overlay result
Show Water Balance
Warnings
Debug Info
- Water areas:
Keys tab
Water Level | m + datum | initial water level, relative to datum, for all water cells in a water area |
Outlet | m3/s | water abstraction for all water cells in a water area |
Outlet level | m + datum | initial water level, relative to datum, for all water cells in an outlet area (breach for example) |
Outlet capacity | m3 | maximum amount of water that can be used for the outlet |
Sewer Storage | m | available storage in sewers at the start of simulation in a sewer area |
Sewer Pump Speed | m3/s | sewer water abstraction for all cells in a sewer area |
Breach Floor | m + datum | Modified terrain height, to simulate a breach in a levee. |
Inundation level | m + datum | Initial water height, to simulate water present at the start of the simulation. |
Weir Height | m + datum | weir crest level |
Weir Output | m3/s | The amount of water that flows through a weir/culvert |
Weir Coefficient | linear weir coefficient for accounting discharge & contraction losses | |
Culvert Speed | m3/s | the discharge capacity of a culvert |
Pump Speed | m3/s | the capacity of a pump |
Sewer Overflow Height | m + datum | the height of a crest of a sewer overflow |
Sewer Overflow Speed | m3/s | the discharge capacity of a sewer overflow |
Chloride | x/m2 | Amount* of chloride which is created per second, per m² of construction with this attribute. |
Nitrogen | x/m2 | Amount* of nitrogen which is created per second, per m² of construction with this attribute. |
Phosphorus | x/m2 | Amount* of phosphorus which is created per second, per m² of construction with this attribute. |
Attributes tab
ALLOWED_WATER_INCREASE_M | m | The amount by which the water level on a water terrain must increase before it is considered stressed by water. This is used to compute the WATER_STRESS result type. |
DESIGN_FLOOD_ELEVATION_M | m | Constructions in the 3D world are assumed to have at most this height compared to the surface of the terrain. Greater values can create a more accurate model but will impact performance. |
GROUND_BOTTOM_DISTANCE_M | m | Assumed distance under the terrain surface where the soil becomes impenetrable for water. The groundwater level cannot go below this depth, relative to the surface. The maximum amount of water that can be stored underground is equal to this attribute multiplied by the local terrain's WATER_STORAGE_PERCENTAGE. |
GROUND_WATER | boolean | Whether underground water flow is simulated during the calculation. If this is deactivated, surface infiltration, underground infiltration, and underground evaporation do not occur. Water flowing in- and out of the sewer are still simulated when sewers are present. |
IMPACT_FLOOD_THRESHOLD_M | m | The amount of water a construction must experience before it is considered impacted by water. Water must reach this height either on one of the cells the construction is on, or on one of the cells adjacent to it. This is used to compute the IMPACTED BUILDINGS result type. |
MAX_SPEED_MS | m/s | Maximum speed at which water is allowed to flow. This effects the preservation of impulse in water, and as a result the length of computational timesteps. Impulse is more accurately preserved as the maximum speed increases, but will reduce the time per step of the calculation, increasing the total time for the calculation to complete. |
MIN_SLOPE | ratio | The minimum slope required to account for the effect of gravity on the speed of the water. If the slope of the terrain is less than the minimum slope, the effect of gravity on the speed of the water is assumed to be 0. The ratio is the height over distance. |
SEWER_OVERFLOW_THRESHOLD | fraction | How much of a sewer's storage must be filled with water before the sewer's overflows are allowed to overflow water. |
SHOW_DURATION_FLOOD_LEVEL_M | m | The amount of water which must be present in a specific location before the duration of surface water can be recorded. This is used to compute the SURFACE_DURATION result type. |
SUPERGRID | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. | |
SURFACE_WATER_EVAPORATION_FACTOR | factor | The factor by which the weather's evaporation factor is multiplied to compute the amount of evaporation which takes place on the surface. |
TIMEFRAMES | amount | The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed. |
- ↑ Langevin, C.D., Hughes, J.D., Banta, E.R., Niswonger, R.G., Panday, Sorab, and Provost, A.M. (2017) ∙ Documentation for the MODFLOW 6 Groundwater Flow Model: U.S. Geological Survey Techniques and Methods, book 6, chap. A55 ∙ p 31 ∙ found at: https://doi.org/10.3133/tm6A55 (last visited 2019-02-04)