Bottom flow pankow benchmark (Water Module): Difference between revisions
Line 42: Line 42:
We use the following setup. The grid size used is 53 by 5, with a configurable cell size of <math>dx</math> in meters. There are two waterways, left and right, both with a stable water level of 3 meters.
One inlet is placed on the cells x = 1 and y = 1 to 3 and another is placed on the cells x = 52 and y - 1 to 3, with the following setup to ensure a stable water level:
One inlet is placed on the cells x = 1 and y = 1 to 3 and another is placed on the cells x = 52 and y = 1 to 3, with the following setup to ensure a stable water level:
:[[Inlet_upper_threshold_(Water_Overlay)|UPPER_THRESHOLD]] set to 3 m.
:[[Inlet_lower_threshold_(Water_Overlay)|LOWER_THRESHOLD]] set to 3 m.
Latest revision as of 13:38, 8 October 2026
This benchmark demonstrates a situation where a parcel of land is situated between two waterways with a stable water level. In combination with ground water flowing from deeper ground layers through the bottom boundary, a characteristic curve will form over time, as shown in the image below. This scenario and its accompanying formulas are described in the 1968 water balance research by Pankow and Rijtema [1]. This benchmark ignores the additional water flow resistance of the waterway. Secondly, rain could also be taken into account, but we set that to 0 to exclusively benchmark the bottom flow mechanics. The continuous rainfall case is already tested in phreatic groundwater levels benchmark.
A parcel of land situated between two waterways with ground bottom flow and optional continuous rainfall[2]
Due to ground bottom flow and two stable water levels left and right, a specific ground water table curve will form. Part of the water flowed in from the bottom will flow left and part of the it will flow right. Note that the time at which this balance occurs is dependent on the starting situation.
The following formula, taken from [1], describes the curve of ground water levels when the ground water flow to the left and right have become stable:
A=(h1−h2)coshx1KD⋅cx222KD⋅2KD⋅cx22⋅(cosh(x2KD⋅c)−1)−x122KD⋅2KD⋅cx12⋅(cosh(x1KD⋅c)−1)=(h1−h2)coshx1KD⋅cc⋅(cosh(x2KD⋅c)−1)−c⋅(cosh(x1KD⋅c)−1)
A=N+hd−h1c
Simplified without rain N:
h1=hd−(h1−h2)coshx1KD⋅c(cosh(x2KD⋅c)−1)−(cosh(x1KD⋅c)−1)
To test the correctness of the ground bottom flow, the formula can test the following condition with the accepted error margin ϵ:
|hd−(h1−h2)coshx1KD⋅c(cosh(x2KD⋅c)−1)−(cosh(x1KD⋅c)−1)−h1|<ϵ
x1: distance (m) of the point of measurement compared to the middle of the parcel.
x2: distance (m) of the second point of measurement, which is always situated 3 meters from the edge of the waterway.
h1: measured ground water level (m) at x1
h2: measured ground water level (m) at x2
hd: bottom head pressure
KD: measured horizontal transmissivity of the ground layer (m2/day)
N: additional ground water due to rainfall (m/day).
ϵ: accepted error margin
Setup
We use the following setup. The grid size used is 53 by 5, with a configurable cell size of dx in meters. There are two waterways, left and right, both with a stable water level of 3 meters.
UPPER_THRESHOLD set to 3 m.
LOWER_THRESHOLD set to 3 m.
Inlet Q set to 0, such that is unlimited.
The terrain height is set to: {0,if x<4 or x>481.5,if x=4 or x=483.5,if x=5 or x=475,otherwise
Depending on the specific test case, the Bottom head pressure hp is set to:
{hp,if x>5 and x<47none,otherwise
Similarly, the Bottom resistance (in days) is set to:
{c,if x>5 and x<47none,otherwise
An aquifer can be added to configure the horizontal infiltration speed. An important thing to note here, is that the KD value used in the report [1] is derived from changes in water head over time, and does not mention the storage capacity of the soil. Therefore, in order to configure the Aquifer KD value in the Tygron Platform, the KD value has to be multiplied with the storage percentage.
The water level is configured to 3 m for all cells, resulting in an initial water level above and below ground of 3 meters.
The simulation time is set to n days, with rain set to 0 mm. To configure this, the rain set is set to [3600⋅24⋅n,0].
Results
Test case 1
cell size: 10 m;
KD: 17 m²/day;
Water storage fraction: 0.10;
Aquifer KD configured to 1.7 m²/day in the Tygron Platform;
Bottom resistance c: 20 days
Bottom head pressure hd: 4.1
Simulation days n: 128 days
Test case 2
cell size: 10 m;
KD: 22 m²/day;
Water storage fraction: 0.25;
Aquifer KD configured to 5.5 m²/day in the Tygron Platform;
Bottom resistance c: 40 days
Test case 3
cell size: 10 m;
KD: 22 m²/day;
Bottom head pressure hd: 3.8
Test case 4
cell size: 10 m;
KD: 22 m²/day;
Bottom resistance c: 10 days
Bottom head pressure hd: 4.8
Test case 5
cell size: 10 m;
KD: 17 m²/day;
Bottom head pressure hd: 4.1 (but leads to hd=4.077 for the comparisons with the middle value)
Simulation days n: 64 days
Test case 6
cell size: 10 m;
KD: 22 m²/day;
Water storage fraction: 0.33;
Aquifer KD configured to 7.26 m²/day in the Tygron Platform;
Bottom head pressure hd: 4.5 (but leads to hd=4.499 for the comparisons with the middle value)
Test case 7
cell size: 10 m;
KD: 220 m²/day;
Aquifer KD configured to 55 m²/day in the Tygron Platform;
Test case 8
cell size: 10 m;
KD: 220 m²/day;
Test case 9
cell size: 5 m;
KD: 22 m²/day;
Aquifer KD configured to 2.2 m²/day in the Tygron Platform;
Test case 10
cell size: 2 m;
KD: 22 m²/day;
  • A higher KD value can lead to a lower stable ground water level than the head pressure.
  1. ↑ 1.0 1.1 1.2 De resultaten van het waterbalansonderzoek in 1968 voor de objecten met een constant slootpeil in Hoenkoop. Nota 567. ∙ J. Pankow en P.E. Rijtema, 1970 ∙ Instituut voor Cultuurtechniek en Waterhuishouding, Wageningen.
  2. ↑ Schatten van kwel ∙ Found at: Grondwaterformules.nl/index.php/formules/ontwatering/kwel-berekenen-pankow ∙ (last visited: 2025-10-17)