Line 729: | Line 729: | ||
The water model includes an underground model which dictates the movement of water in the soil. The underground model includes the flow of water from the surface into the underground via infiltration, the flow of water from one underground location to another, and the exfiltration of water from the soil back onto the surface layer. | The water model includes an underground model which dictates the movement of water in the soil. The underground model includes the flow of water from the surface into the underground via infiltration, the flow of water from one underground location to another, and the exfiltration of water from the soil back onto the surface layer. | ||
The underground model can be explicitly activated or deactivated by setting the {{inlink|GROUND_WATER}} attribute of the water overlay to the appropriate value. | The underground model can be explicitly activated or deactivated by setting the {{inlink|GROUND_WATER}} attribute of the water overlay to the appropriate value. If the underground model is deactivated, no water can move from or to the underground in any form. | ||
The underground is bounded vertically by the {{inlink|Surface model|surface of the terrain}} at the top, and an assumed impenetrable layer at the bottom. The distance between the surface and the impenetrable layer, and thus the effective height of the underground, is equal to {{inlink|GROUND_BOTTOM_DISTANCE_M}}. In other words, the impenetrable underground layer is assumed to be a set distance below the surface. The distance is uniform across the entire project area, and follows the profile of the surface. | The underground is bounded vertically by the {{inlink|Surface model|surface of the terrain}} at the top, and an assumed impenetrable layer at the bottom. The distance between the surface and the impenetrable layer, and thus the effective height of the underground, is equal to {{inlink|GROUND_BOTTOM_DISTANCE_M}}. In other words, the impenetrable underground layer is assumed to be a set distance below the surface. The distance is uniform across the entire project area, and follows the profile of the surface. |
Revision as of 14:13, 22 January 2019
What are the Water Overlays
Configuration wizard
Step 1
Step 2
- ground water data
- Weirs
- Culverts
- Pumps
Step 3
Step 4
Step 5
Step 6
Model connections
Terrain height
Weather
Rain and simulation time
Linear configuration
Property | Unit | Description |
Rain for | minutes | How long rain should last at the start of the simulation. |
Total rainfall | mm | How much rain should fall in the specified period. |
Dry after rain (days, hours, minutes) | days, hours, minutes | How long the simulation continues after the rain has fallen. |
Custom configuration
Rain and simulation CSV specification | |||||||||
Data per line | Additional rainfall until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Rain should never be negative | ||||||||
First entry | Second entry | ||||||||
Time (s) | Rain (m) | ||||||||
Line 1 | Time when first period ends | Total rain during first period | |||||||
Line 2 | Time when second period ends | Total rain during second period |
Evaporation
Surface evaporation | mm/day | The speed at which water evaporates during the simulation |
Evaporation CSV specification | |||||||||
Data per line | Rate of evaporation until specified moment | ||||||||
Criteria | Time should always be greater than or equal to previous time Evaporation should never be negative | ||||||||
Time (s) | Evaporation (m) | ||||||||
Line 1 | Time when first period ends | Amount of evaporation during first period | |||||||
Line 2 | Time when second period ends | Amount of evaporation during second period |
Ground water GeoTIFF
Subsidence
Hydrological features
Water level area
Attribute | Unit | Description | Default (when attribute is not present) |
WATER_LEVEL | m + datum | The water level for all water terrains in this water level area | n/a |
Sewer area
SEWER_STORAGE | m | The maximum height the water can reach in this sewer. This value, multiplied by the surface area of the sewered constructions the sewer area intersects with, forms the total amount of water this sewer can store. | n/a |
SEWER_PUMP_SPEED | m3/s | The amount of water removed from the sewer by removing it from the hydrological model entirely. | 0 |
Breach
SURFACE_OVERRIDE | m + datum | The new terrain height at the location of the breach. | n/a |
INLET_Q | m3/sec | The maximum amount of water flowing into the model through this breach. A negative value means the breach functions as an outlet, and water is removed from the hydrological model. | 0 |
INLET_CAPACITY | m3 | The maximum, total amount of water which can flow in or out through this breach. Water flowing back in the other direction replenishes the capacity. | Infinite |
LOWER_THRESHOLD | m + datum | If a lower threshold is set, water will only flow into the model through this breach until the average water level on this breach is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion. | None |
UPPER_THRESHOLD | m + datum | If an upper threshold is set, water will only flow out the model through this breach until the average water level at the point of this breach is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion. | None |
Inundation
INUNDATION_LEVEL | m + datum | The height of the water. | n/a |
Hydrological constructions
- Line-based constructions
Culvert
Attribute | Unit | Description | Default |
CULVERT_WIDTH | m | The diameter of the culvert. For throughput calculations, the culvert is assumed to have a spherical cross-section. | 1 |
CULVERT_HEIGHT | m + datum | The height of the culvert. (When set to a level lower than the terrain for either endpoint of it, the culvert's height is equal to the height of the (highest) terrain under either endpoint.) | 0 |
CULVERT_N | manning value | The manning value of the culvert's material, which influences the flow speed. | 0,014 |
Weir
WEIR_HEIGHT | m + datum | The height of the weir. | n/a |
WEIR_WIDTH | m | The width of the weir. | 5 |
WEIR_COEFFICIENT | coefficient | The flow coefficient related to the shape of the weir | 1,1 |
Pump
PUMP_SPEED | m3/s | The speed at which water is pumped from the lower water level to the higher water level. | n/a |
Sewer overflow
SEWER_OVERFLOW | m + datum | The height of the bottom of the sewer, relative to the average terrain height of the connected sewer. Starting from this height, the water level in the sewer must exceed the height of the terrain at the location of the overflow in order for water to flow out. | n/a |
SEWER_OVERFLOW_SPEED | m3/s | The maximum speed at which water can flow out from the sewer through this overflow. | 10 |
Inlet
INLET_Q | m3/sec | The maximum amount of water flowing into the model through this inlet. A negative value means the construction functions as an outlet, and water is removed from the hydrological model. | n/a |
INLET_CAPACITY | m3 | The maximum amount of water which can flow in or out through this construction. Water flowing back in the other direction replenishes the capacity. | Infinite |
LOWER_THRESHOLD | m + datum | If a lower threshold is set, water will only flow into the model through this inlet until the water level at the point of this inlet is equal to or greater than the threshold. If the threshold is not set, the amount of water flowing in is not limited in this fashion. | None |
UPPER_THRESHOLD | m + datum | If an upper threshold is set, water will only flow out the model through this outlet until the water level at the point of this inlet is equal to or lower than the threshold. If the threshold is not set, the amount of water flowing out is not limited in this fashion. | None |
Sewered constructions
Attribute | Unit | Function value | Description |
SEWERED | boolean | Connected to sewer | Whether this construction is connected to the sewer. |
Water storage constructions
WATER_STORAGE | m³/m² | Water storage (m³/m²) | How much water this construction can store. |
Porous constructions
GROUND_INFILTRATION_MD | m/day | Ground infiltration per day (m) | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
Crops and foliage
ROOT_DEPTH_M | m | Depth of plant roots (m) | The depth of the roots of this construction, relative to the terrain height at the location of this construction. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Water evaporation | How fast this construction can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Critical structures
CRITICAL_INFRASTRUCTURE | nominal integer | Critical infrastructure | Whether this construction is deemed a critical construction. 0 means the construction is never deemed impacted. |
Chemical emitters/decomposer
CHLORIDE | x/m² | The amount of chloride created per second per m² in this location. | 0 |
NITROGEN | x/m² | The amount of nitrogen created per second per m² in this location. | 0 |
PHOSPHORUS | x/m² | The amount of phosphorus created per second per m² in this location. | 0 |
Water
Attribute | Unit | Terrain type | Description |
WATER | boolean | Surface | Whether the specified terrain is a water terrain. |
Evaporation
ROOT_DEPTH_M | m | Surface | The depth of the roots of this surface terrain, relative to the surface. Water can be drawn from the underground and evaporated if the roots can reach it. |
WATER_EVAPORATION_FACTOR | factor | Surface | How fast this terrain can evaporate water from the underground. The weather's evaporation speed is multiplied by this factor to determine the rate of evaporation. |
Infiltration and storage
GROUND_INFILTRATION_MD | m/day | Surface | The speed at which water can flow vertically from the surface to the underground unsaturated zone. |
GROUND_INFILTRATION_MD | m/day | Underground | The speed at which water can flow vertically from the underground unsaturated zone to the underground saturated zone, and horizontally through across the saturated zone. |
WATER_STORAGE_PERCENTAGE | percentage | Underground | The percentage of the underground volume which can be filled with water. A lower percentage means the underground will be able to store less water, and the saturated zone will rise higher with the same amount of water in the underground layer. |
Result types
Result type | Unit | Display mode | Description |
BASE_TYPES | Nominal value | Start | Categorization of the individual cells based on how they are processed by the water model, displaying which cells are considered to be specific features. 0: Cell on the edge of the project area |
CHLORIDE | x/m² | Last | The amount of chloride present. The value is the sum of the quantities on the surface, and the underground. |
DIRECTION | Degrees | Last | The direction in which water is flowing. |
EVAPORATED | m (mm)¹ | Total | The amount of water that has evaporated. The value is the sum of the quantities evaporated from the surface and the underground. |
GPU OVERVIEW | nominal value | Maximum | Shows which GPU cluster calculated which part of the overlay. |
IMPACTED_BUILDINGS | nominal value | Maximum | Constructions impacted by excess water. Constructions are considered impacted when the construction itself or an adjacent cell contains more water on the surface than configured in IMPACT_FLOOD_TRESHOLD_M. 0: Construction is not impacted |
LAST SPEED | m/s | Last | The speed of water flow in any given location. |
MAX SPEED | m/s | Maximum | The speed of water flow in any given location. |
NITROGEN | x/m² | Last | The amount of nitrogen present. The value is the sum of the quantities on the surface, and the underground. |
PHOSPHORUS | x/m² | Last | The amount of phosphorus present. The value is the sum of the quantities on the surface, and the underground. |
SEWER_LAST_VALUE | m (mm)¹ | Last | The amount of water stored in the sewer. |
SEWER_MAX_VALUE | m (mm)¹ | Maximum | The amount of water stored in the sewer. |
SURFACE_DURATION | s (min)¹ | Total | The amount of time the water depth on the surface exceeds SHOW_DURATION_FLOOD_LEVEL_M. |
SURFACE_FLOW | m³/m² | Description wil be added | |
SURFACE_LAST_VALUE | m (mm)¹ | Last | The amount of water on the surface. |
SURFACE_MAX_VALUE | m (mm)¹ | Maximum | The amount of water on the surface. |
UNDERGROUND_FLOW | m³/m² | Description wil be added | |
UNDERGROUND_LAST_STORAGE | m (mm)¹ | Last | The (effective) amount of water in the underground unsaturated zone at the end of the last calculated timestep. |
UNDERGROUND_LAST_VALUE | m (mm)¹ | Last | The amount by which the groundwater table has risen above the initial groundwater level at the last calculated timestep. |
UNDERGROUND_MAX_STORAGE | m (mm)¹ | Maximum | The maximum (effective) amount of water in the underground unsaturated zone across all calculated timesteps. |
UNDERGROUND_MAX_VALUE | m (mm)¹ | Maximum | The maximum amount by which the groundwater table has risen above the initial groundwater of all the calculated timesteps. |
UNDERGROUND WATERTABLE | m + datum | Last | The groundwater level, relative to datum. |
WATER_STRESS | m (mm)¹ | Maximum | The amount of water on the surface, similar to SURFACE_MAX_VALUE. However, for water terrains, the water level must rise by at least ALLOWED_WATER_INCREASE_M. Otherwise, the value in those locations is 0. |
Result child overlays
Calculations
Models
Surface model
Underground model
The underground model can be explicitly activated or deactivated by setting the GROUND_WATER attribute of the water overlay to the appropriate value. If the underground model is deactivated, no water can move from or to the underground in any form.
Surface water infiltrates into the underground unsaturated layer. Water in the unsaturated layer is assumed to be spread equally across the entire unsaturated volume. Water then flows from the unsaturated zone into the saturated zone at the speed dictated by the underground terrain's GROUND_INFILTRATION_MD. For a given timestep, the distance the water travels is determined. The amount of water that flows from the unsaturated zone to the saturated zone is equal to the amount of water in a section of the unsaturated zone the height of which is equal to that distance. After water has been added to the saturated zone, the groundwater level (and thus the height of the saturated zone) is redetermined. The water in the unsaturated zone is redistributed uniformly across the unsaturated zone.
Sewer model
Evaporation model
Chemical flow model
Line construction model
Point construction model
Polygon construction model
Model border
Timestep formula
Δt = Δx /umax
- Δt = computational timestep
- Δx = grid cell size
Surface water level formula
Surface flow formula
2D Saint Venant
- friction
- bed slope
- water pressure
Groundwater level formula
Surface infiltration formula
Surface infiltration capacity is calculated per cell.
I = min(Icon, Isurf)
- I = The cell's infiltration capacity (m/day)
Δw = (Δt * Iund * Wunsat) / (GBDM - (Wsat/WSP))
- Wsat = The amount of water stored in the saturated zone.
- Wunsat = The amount of water stored in the saturated zone.
- GBDM = GROUND_BOTTOM_DISTANCE_M.
- WSP = WATER_STORAGE_PERCENTAGE.
Underground flow formula
Culvert formula
Weir formula
Pump formula
Overflow formula
Inlet formula
Surface evaporation formula
Calculation time impact
General Tab
Calculation Preference
Δt = Δx /umax
Grid cell size
Refresh Grid
Export Grid File
Save Overlay result
Show Water Balance
Warnings
Debug Info
- Water areas:
Keys tab
Water Level | m + datum | initial water level, relative to datum, for all water cells in a water area |
Outlet | m3/s | water abstraction for all water cells in a water area |
Outlet level | m + datum | initial water level, relative to datum, for all water cells in an outlet area (breach for example) |
Outlet capacity | m3 | maximum amount of water that can be used for the outlet |
Sewer Storage | m | available storage in sewers at the start of simulation in a sewer area |
Sewer Pump Speed | m3/s | sewer water abstraction for all cells in a sewer area |
Breach Floor | m + datum | Modified terrain height, to simulate a breach in a levee. |
Inundation level | m + datum | Initial water height, to simulate water present at the start of the simulation. |
Weir Height | m + datum | weir crest level |
Weir Output | m3/s | The amount of water that flows through a weir/culvert |
Weir Coefficient | linear weir coefficient for accounting discharge & contraction losses | |
Culvert Speed | m3/s | the discharge capacity of a culvert |
Pump Speed | m3/s | the capacity of a pump |
Sewer Overflow Height | m + datum | the height of a crest of a sewer overflow |
Sewer Overflow Speed | m3/s | the discharge capacity of a sewer overflow |
Chloride | x/m2 | Amount* of chloride which is created per second, per m² of construction with this attribute. |
Nitrogen | x/m2 | Amount* of nitrogen which is created per second, per m² of construction with this attribute. |
Phosphorus | x/m2 | Amount* of phosphorus which is created per second, per m² of construction with this attribute. |
Attributes tab
ALLOWED_WATER_INCREASE_M | m | The amount by which the water level on a water terrain must increase before it is considered stressed by water. This is used to compute the WATER_STRESS result type. |
DESIGN_FLOOD_ELEVATION_M | m | Constructions in the 3D world are assumed to have at most this height compared to the surface of the terrain. Greater values can create a more accurate model but will impact performance. |
GROUND_BOTTOM_DISTANCE_M | m | Assumed distance under the terrain surface where the soil becomes impenetrable for water. The groundwater level cannot go below this depth, relative to the surface. The maximum amount of water that can be stored underground is equal to this attribute multiplied by the local terrain's WATER_STORAGE_PERCENTAGE. |
GROUND_WATER | boolean | Whether underground water flow is simulated during the calculation. If this is deactivated, surface infiltration, underground infiltration, and underground evaporation do not occur. Water flowing in- and out of the sewer are still simulated when sewers are present. |
IMPACT_FLOOD_THRESHOLD_M | m | The amount of water a construction must experience before it is considered impacted by water. Water must reach this height either on one of the cells the construction is on, or on one of the cells adjacent to it. This is used to compute the IMPACTED BUILDINGS result type. |
MAX_SPEED_MS | m/s | Maximum speed at which water is allowed to flow. This effects the preservation of impulse in water, and as a result the length of computational timesteps. Impulse is more accurately preserved as the maximum speed increases, but will reduce the time per step of the calculation, increasing the total time for the calculation to complete. |
MIN_SLOPE | ratio | The minimum slope required to account for the effect of gravity on the speed of the water. If the slope of the terrain is less than the minimum slope, the effect of gravity on the speed of the water is assumed to be 0. The ratio is the height over distance. |
SEWER_OVERFLOW_THRESHOLD | fraction | How much of a sewer's storage must be filled with water before the sewer's overflows are allowed to overflow water. |
SHOW_DURATION_FLOOD_LEVEL_M | m | The amount of water which must be present in a specific location before the duration of surface water can be recorded. This is used to compute the SURFACE_DURATION result type. |
SUPERGRID | This attribute name is reserved for future functionality. Currently, this marks an experimental feature which is currently under development and may result in unexpected behavior when activated. | |
SURFACE_WATER_EVAPORATION_FACTOR | factor | The factor by which the weather's evaporation factor is multiplied to compute the amount of evaporation which takes place on the surface. |
TIMEFRAMES | amount | The number of intermediate results recorded during the calculation. Each timeframe becomes a snapshot of data which can be viewed and analysed. The total simulation time is divided by this value, and at each interval of that period of time a snapshot of the results so far is made. Note that the first timeframe does not contain the starting conditions of the simulation, but the state of the simulation after the first period of time has passed. |